[RE-wrenches] How much Li battery?

Mark Frye markf at berkeleysolar.com
Tue May 26 12:46:26 EDT 2020


Humm...suppose I wanted for myself some lead calcium flooded batteries, 
about 100 AH at 48 V, anyone have an idea of a good vendor?

On 5/26/2020 3:12 AM, drake.chamberlin at redwoodalliance.org wrote:
>
> I would use Concorde VRLA batteries. They can take a very fast charge. 
> In certain conditions they can charge at C X 5 instead of C/5.
>
>
>
> ---
>
>
> On 2020-05-25 18:13, Jay wrote:
>
>> You might check out discover batteries.
>> I'm a big fan of companies they make their equipment, they do, one of 
>> the very few in the lithium world.
>> And while the original question specifically asked about Lithium, 
>> what you're requiring is perfectly suited for VRLA float service 
>> batteries.
>> Long life, much lower cost.
>> Jay
>> Peltz power.
>>
>>> On May 25, 2020, at 2:37 PM, Dave Angelini Offgrid Solar 
>>> <offgridsolar at sti.net> wrote:
>>>
>>> Jay knows about these and I won't name them just because I use 
>>> them.  They are the perfect size for most offgrid and scalable.
>>>
>>> I have a client in Texas who left them for 14 months off, and maybe 
>>> they lost 1%. The best part of them for me, is all a client has to 
>>> do is enter the date in the system control panel and all of the rest 
>>> is done. True plug and play. Built by a company that has made 
>>> locomotive batteries for decades. I asked them Jay on linkedin.  He 
>>> said do what you want with Soc. Don't worry about any of that. Just 
>>> know that we have you covered. Below is from their latest webinar.
>>>
>>> For a solar installation to pass final inspection, the batteries 
>>> must have been tested and approved to UL 1973. Not just the cell but 
>>> the battery. So, before making a final selection, verify that the 
>>> battery selection you make has you covered. These LiFePO_4 
>>>  batteries meet this certification, so you can be confident that 
>>> your customers batteries are safe and pass inspection. Our 
>>> commitment to safety, reliability and certification also delivers 
>>> the following.
>>>
>>>   * Safe and Maintenance Free
>>>   * Sophisticated High Current BMS
>>>   * Field Serviceable BMS
>>>   * IP 55 Rated
>>>   * IEC 62133 Safety
>>>   * UL 1973 Safety Certified
>>>   * UN 38.3 Transport Certified
>>>
>>>
>>>   
>>> *Dave Angelini Offgrid Solar "we go where powerlines don't" 
>>> http://members.sti.net/offgridsolar/ e-mail offgridsolar at sti.net 
>>> <mailto:offgridsolar at sti.net> text 209 813 0060*
>>>
>>> On Sun, 24 May 2020 21:05:06 -0700, Jerry Shafer 
>>> <jerrysgarage01 at gmail.com> wrote:
>>>
>>>     It may take a little bit as it wrapped up just over 2 years ago,
>>>     most of the research stayed at the lab. I do recall V2 did not
>>>     survive the cycling test, it was unable to restart from 99% dod.
>>>     There is no substitute for a multi-level battery management
>>>     structure when it comes to Li tech. I have priced simplify dirt
>>>     to keys and it cost more then Blue did and required more space.
>>>     There was another one that came in near the end and was built in
>>>     what appeared to be a 66" tall chemical storage cabinet just to
>>>     make it fire rated, maybe it's just me but batteries that can
>>>     catch fire may not be the best choice but hey I'm funny like
>>>     that. Anyone installing any batteries needs to read the very
>>>     fine print that talks about "what to do in case of" and that can
>>>     be a deciding factor right there.
>>>     Way back when all FLA's had to be in a pan to catch the acid
>>>     before it did damage, that was 20 years ago by now it should be
>>>     safer not more dangerous.
>>>
>>>     On Sun, May 24, 2020, 8:36 PM jay <jay.peltz at gmail.com
>>>     <mailto:jay.peltz at gmail.com>> wrote:
>>>
>>>         HI Jerry,
>>>         Most impressive.
>>>         Would you be willing to tell us which ones didn't meet this
>>>         test, if not publicly, then off list?
>>>         thanks
>>>         jay
>>>
>>>
>>>             On May 24, 2020, at 3:23 PM, Jerry Shafer
>>>             <jerrysgarage01 at gmail.com
>>>             <mailto:jerrysgarage01 at gmail.com>> wrote:
>>>
>>>             Wrenches
>>>             Again not all batteries are the same, Chemistry,
>>>             recharge rate or intelligence of the BMS, l have
>>>             personally tested Blue planet batteries, l have let them
>>>             sit at 100% SOC for 10 weeks, ran them at 30% SOC for 6
>>>             months, l have performed 100% to 0% cycling up to 4
>>>             times a day. This is the same tests l ran on a variety
>>>             of Li tech batteries and BluePlanet is the only one that
>>>             survived this testing. It's ore then spec sheets and
>>>             cost, it comes down to success or failure, personally l
>>>             like success and being able to pass or fail batteries
>>>             without having my customers pay the price is a good
>>>             thing. Blue Planet has 8000 cycles life and a 15 year
>>>             warranty at 70% compare that to anything out there but
>>>             again that's just me.
>>>
>>>             On Sun, May 24, 2020, 1:32 PM Darryl Thayer
>>>             <darylsolar1 at gmail.com <mailto:darylsolar1 at gmail.com>>
>>>             wrote:
>>>
>>>                 I have spoken with a li battery
>>>                 researcher. Do not charge over 85% of battery full
>>>                 charge voltage and they will last over 25 years. 
>>>                  But go above or below bottom and trouble
>>>
>>>                 On Sun, May 24, 2020, 10:27 AM Jay
>>>                 <jay.peltz at gmail.com <mailto:jay.peltz at gmail.com>>
>>>                 wrote:
>>>
>>>                     One question I have for those more versed than
>>>                     me in lithium is, I'm under the impression that
>>>                     having a lithium battery in float for years
>>>                     isn't good for it. Or at the very least it has
>>>                     to be cycled with some regularity.
>>>                     I'd like to hear data on that
>>>                     Thx
>>>                     Jay
>>>                     Peltz power.
>>>
>>>                         On May 23, 2020, at 10:08 PM, Ray
>>>                         <ray at solarray.com <mailto:ray at solarray.com>>
>>>                         wrote:
>>>
>>>                         I suggest starting with a very simple look
>>>                         at the continuous output rating of the
>>>                         battery and match that to the inverter
>>>                         continuous rating. This ends up with quite a
>>>                         bit more battery than you might think at
>>>                         first. However, if the customer paid the big
>>>                         bucks for a battery backup system, they
>>>                         should at least get enough battery to
>>>                         operate the inverter at its rated power.
>>>                         Anything less, I would consider poor design.
>>>                         The same goes for lead acid batteries, they
>>>                         just don't work well, even on grid, when the
>>>                         battery is undersized. Even lead acid
>>>                         batteries have maximum current output
>>>                         ratings that should at least be matched to
>>>                         the inverter rating.
>>>
>>>                         If you WERE going to under size the battery,
>>>                         then you should keep it safe by reducing the
>>>                         size of the inverter battery breaker as
>>>                         well.   I know this "micro battery for GTB"
>>>                         is becoming a trend, but it doesn't mean its
>>>                         right.
>>>
>>>                         Ray Walters
>>>                         Remote Solar
>>>                         303 505-8760
>>>
>>>                         On 5/23/20 5:48 PM, Mick Abraham wrote:
>>>
>>>                             Greetings, All~ Mark Frye had asked: 
>>>                             "...with a 4000w Outback Radian, AC
>>>                             coupled with 2000w of PV, what is the
>>>                             smallest Li battery I would want for
>>>                             stable operation?"
>>>                             Mick's reply: In the lithium arena, one
>>>                             often finds the ratings in
>>>                             kilowatt-hours rather than in amp-hours.
>>>                             This is an easy conversion for us energy
>>>                             nerds to make, so below I'm mainly using
>>>                             watts & watt-hours with occasional
>>>                             conversions to amp-hours.
>>>                             I suggest that you start with the spec
>>>                             sheet (of whichever brand lithium
>>>                             battery is on your radar), & see what
>>>                             the manufacturer says about "allowable
>>>                             rate of recharge". You may find that C/2
>>>                             is an acceptable rate with several
>>>                             manufacturers, Mark--much faster than
>>>                             what we're accustomed to with typical
>>>                             lead-acid batteries. Let's assume:
>>>                             * ...that your AC coupled PV array
>>>                             crests around 1800 watts to the battery
>>>                             when there are no loads
>>>                             * ...that the battery is below 100%
>>>                             state of charge, and
>>>                             * ...that the solar conditions are optimal.
>>>                             Let's further assume that
>>>                             those conditions represent your
>>>                             battery's highest energy rate in either
>>>                             direction.
>>>                             1800w X two hours = 3,600 watt-hours
>>>                             dividing by 48v nominal = 75 amp-hours
>>>                             in the above hypothetical situation.
>>>                             ++++++++++++++++++++++++++++++
>>>                             The rate at which a battery can receive
>>>                             energy is (usually) also the rate at
>>>                             which it can comfortably deplete, so
>>>                             let's briefly look at the flip side:
>>>                             Assuming the battery mfr. wants the
>>>                             watt-hours to be no less than two times
>>>                             the maximum wattage, a 3600 watt-hour
>>>                             (C/2) battery should not be depleted
>>>                             faster than 1800 watts. Your 4kW Radian,
>>>                             Mark, could exceed that if the loads
>>>                             demand it--& maybe your loads don't.
>>>                             Motor starting surges should probably be
>>>                             part of the thinking & it wouldn't hurt
>>>                             to ask the mfr.'s opinion about short
>>>                             term surges which briefly deplete the
>>>                             battery faster than the hypothetical two
>>>                             hour rate.
>>>                             By approaching this question based on
>>>                             the battery manufacturer do's & don'ts,
>>>                             one improves the chance of getting
>>>                             warranty coverage should it later be
>>>                             needed. "What the large print giveth,
>>>                             the fine print taketh away."
>>>                             The Wrench List is the Bomb!
>>>
>>>                             Mick Abraham, Proprietor
>>>                             www.abrahamsolar.com
>>>                             <http://www.abrahamsolar.com/>
>>>
>>>                             Landline: 970-731-4675
>>>                             Cell phone or for text messaging:
>>>                             970-946-6584
>>>>>>
>>>                             _______________________________________________
>>>                             List sponsored by Redwood Alliance
>>>
>>>                             List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>                             Change listserver email address & settings:
>>>                             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>                             List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>                             List rules & etiquette:
>>>                             www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>                             Check out or update participant bios:
>>>                             www.members.re-wrenches.org  <http://www.members.re-wrenches.org/>
>>>
>>>                         _______________________________________________
>>>                         List sponsored by Redwood Alliance
>>>
>>>                         List Address:
>>>                         RE-wrenches at lists.re-wrenches.org
>>>                         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>                         Change listserver email address & settings:
>>>                         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>                         List-Archive:
>>>                         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>                         List rules & etiquette:
>>>                         www.re-wrenches.org/etiquette.htm
>>>                         <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>                         Check out or update participant bios:
>>>                         www.members.re-wrenches.org
>>>                         <http://www.members.re-wrenches.org/>
>>>
>>>                     _______________________________________________
>>>                     List sponsored by Redwood Alliance
>>>
>>>                     List Address: RE-wrenches at lists.re-wrenches.org
>>>                     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>                     Change listserver email address & settings:
>>>                     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>                     List-Archive:
>>>                     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>                     List rules & etiquette:
>>>                     www.re-wrenches.org/etiquette.htm
>>>                     <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>                     Check out or update participant bios:
>>>                     www.members.re-wrenches.org
>>>                     <http://www.members.re-wrenches.org/>
>>>
>>>                 _______________________________________________
>>>                 List sponsored by Redwood Alliance
>>>
>>>                 List Address: RE-wrenches at lists.re-wrenches.org
>>>                 <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>                 Change listserver email address & settings:
>>>                 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>                 List-Archive:
>>>                 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>                 List rules & etiquette:
>>>                 www.re-wrenches.org/etiquette.htm
>>>                 <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>                 Check out or update participant bios:
>>>                 www.members.re-wrenches.org
>>>                 <http://www.members.re-wrenches.org/>
>>>
>>>             _______________________________________________
>>>             List sponsored by Redwood Alliance
>>>
>>>             List Address: RE-wrenches at lists.re-wrenches.org
>>>             <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>             Change listserver email address & settings:
>>>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>             List-Archive:
>>>             http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>             List rules & etiquette:
>>>             www.re-wrenches.org/etiquette.htm
>>>             <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>             Check out or update participant bios:
>>>             www.members.re-wrenches.org
>>>             <http://www.members.re-wrenches.org>
>>>
>>>         _______________________________________________
>>>         List sponsored by Redwood Alliance
>>>
>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>         Change listserver email address & settings:
>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>         List-Archive:
>>>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>         List rules & etiquette:
>>>         www.re-wrenches.org/etiquette.htm
>>>         <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>         Check out or update participant bios:
>>>         www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org 
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200526/e981b72b/attachment.htm>


More information about the RE-Wrenches mailing list