I believe that Magnum can handle an
imbalance of up to 85%. I haven't found this in the inverter manual, but
believe that I got it from tech support.
Allan On 5/25/2020 4:03 PM, Jay
wrote:
Hi Mark
This was a big advantage of the older FX inverters was the
use of the balancing transformer. The new FXR can't use it.
I can't find
but I had to call OB to get some info on how much you could out of balance
a Radian inverter. It was like 60% ,could have been a bit higher but wasn't
90-100% for sure.
Schneider xw is 75%
I don't know about magnum.
And yea
gotta try and figure out the load balance.
Jay
Peltz Power.
--