[RE-wrenches] Split Phase Load Rating

Sindelar Solar Allan at sindelarsolar.com
Mon May 25 21:26:07 EDT 2020


I believe that Magnum can handle an imbalance of up to 85%. I haven't 
found this in the inverter manual, but believe that I got it from tech 
support.

Allan

On 5/25/2020 4:03 PM, Jay wrote:
> Hi Mark
> This was a big advantage of the older FX inverters was the use of the balancing transformer. The new FXR can’t use it.
> I can’t find but I had to call OB to get some info on how much you could out of balance a Radian inverter. It was like 60% ,could have been a bit higher but wasn’t 90-100% for sure.
> Schneider xw is 75%
> I don’t know about magnum.
> And yea gotta try and figure out the load balance.
> Jay
> Peltz Power.
-- 

*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*