[RE-wrenches] How much Li battery?

Jerry Shafer jerrysgarage01 at gmail.com
Mon May 25 00:05:06 EDT 2020


It may take a little bit as it wrapped up just over 2 years ago, most of
the research stayed at the lab. I do recall V2 did not survive the cycling
test, it was unable to restart from 99% dod. There is no substitute for a
multi-level battery management structure when it comes to Li tech. I have
priced simplify dirt to keys and it cost more then Blue did and required
more space. There was another one that came in near the end and was built
in what appeared to be a 66" tall chemical storage cabinet just to make it
fire rated, maybe it's just me but batteries that can catch fire may not be
the best choice but hey I'm funny like that. Anyone installing any
batteries needs to read the very fine print that talks about "what to do in
case of" and that can be a deciding factor right there.
Way back when all FLA's had to be in a pan to catch the acid before it did
damage, that was 20 years ago by now it should be safer not more dangerous.

On Sun, May 24, 2020, 8:36 PM jay <jay.peltz at gmail.com> wrote:

> HI Jerry,
>
> Most impressive.
>
> Would you be willing to tell us which ones didn’t meet this test, if not
> publicly, then off list?
>
> thanks
>
> jay
>
>
>
> On May 24, 2020, at 3:23 PM, Jerry Shafer <jerrysgarage01 at gmail.com>
> wrote:
>
> Wrenches
> Again not all batteries are the same, Chemistry, recharge rate or
> intelligence of the BMS, l have personally tested Blue planet batteries, l
> have let them sit at 100% SOC for 10 weeks, ran them at 30% SOC for 6
> months, l have performed 100% to 0% cycling up to 4 times a day. This is
> the same tests l ran on a variety of Li tech batteries and BluePlanet is
> the only one that survived this testing. It's ore then spec sheets and
> cost, it comes down to success or failure, personally l like success and
> being able to pass or fail batteries without having my customers pay the
> price is a good thing. Blue Planet has 8000 cycles life and a 15 year
> warranty at 70% compare that to anything out there but again that's just me.
>
> On Sun, May 24, 2020, 1:32 PM Darryl Thayer <darylsolar1 at gmail.com> wrote:
>
>> I have spoken with a li battery
>> researcher. Do not charge over 85% of battery full charge voltage and
>> they will last over 25 years.   But go above or below bottom and trouble
>>
>> On Sun, May 24, 2020, 10:27 AM Jay <jay.peltz at gmail.com> wrote:
>>
>>> One question I have for those more versed than me in lithium is, I’m
>>> under the impression that having a lithium battery in float for years isn’t
>>> good for it. Or at the very least it has to be cycled with some regularity.
>>>
>>> I’d like to hear data on that
>>>
>>> Thx
>>> Jay
>>>
>>> Peltz power.
>>>
>>>
>>>
>>>
>>>
>>> On May 23, 2020, at 10:08 PM, Ray <ray at solarray.com> wrote:
>>>
>>> 
>>>
>>> I suggest starting with a very simple look at the continuous output
>>> rating of the battery and match that to the inverter continuous rating.
>>> This ends up with quite a bit more battery than you might think at first.
>>> However, if the customer paid the big bucks for a battery backup system,
>>> they should at least get enough battery to operate the inverter at its
>>> rated power.  Anything less, I would consider poor design.  The same goes
>>> for lead acid batteries, they just don't work well, even on grid, when the
>>> battery is undersized.  Even lead acid batteries have maximum current
>>> output ratings that should at least be matched to the inverter rating.
>>>
>>> If you WERE going to under size the battery, then you should keep it
>>> safe by reducing the size of the inverter battery breaker as well.   I know
>>> this "micro battery for GTB" is becoming a trend, but it doesn't mean its
>>> right.
>>>
>>> Ray Walters
>>> Remote Solar
>>> 303 505-8760
>>>
>>> On 5/23/20 5:48 PM, Mick Abraham wrote:
>>>
>>> Greetings, All~ Mark Frye had asked:  "...with a 4000w Outback Radian,
>>> AC coupled with 2000w of PV, what is the smallest Li battery I would want
>>> for stable operation?"
>>>
>>> Mick's reply: In the lithium arena, one often finds the ratings in
>>> kilowatt-hours rather than in amp-hours. This is an easy conversion for us
>>> energy nerds to make, so below I'm mainly using watts & watt-hours with
>>> occasional conversions to amp-hours.
>>>
>>> I suggest that you start with the spec sheet (of whichever brand lithium
>>> battery is on your radar), & see what the manufacturer says about
>>> "allowable rate of recharge". You may find that C/2 is an acceptable rate
>>> with several manufacturers, Mark--much faster than what we're accustomed to
>>> with typical lead-acid batteries. Let's assume:
>>>
>>> * ...that your AC coupled PV array crests around 1800 watts to the
>>> battery when there are no loads
>>> * ...that the battery is below 100% state of charge, and
>>> * ...that the solar conditions are optimal.
>>>
>>> Let's further assume that those conditions represent your battery's
>>> highest energy rate in either direction.
>>>
>>> 1800w X two hours = 3,600 watt-hours dividing by 48v nominal = 75
>>> amp-hours in the above hypothetical situation.
>>>
>>> ++++++++++++++++++++++++++++++
>>>
>>> The rate at which a battery can receive energy is (usually) also the
>>> rate at which it can comfortably deplete, so let's briefly look at the flip
>>> side: Assuming the battery mfr. wants the watt-hours to be no less than two
>>> times the maximum wattage, a 3600 watt-hour (C/2) battery should not be
>>> depleted faster than 1800 watts. Your 4kW Radian, Mark, could exceed that
>>> if the loads demand it--& maybe your loads don't. Motor starting surges
>>> should probably be part of the thinking & it wouldn't hurt to ask the
>>> mfr.'s opinion about short term surges which briefly deplete the battery
>>> faster than the hypothetical two hour rate.
>>>
>>> By approaching this question based on the battery manufacturer do's &
>>> don'ts, one improves the chance of getting warranty coverage should it
>>> later be needed. "What the large print giveth, the fine print taketh away."
>>>
>>> The Wrench List is the Bomb!
>>>
>>> Mick Abraham, Proprietor
>>> www.abrahamsolar.com
>>>
>>> Landline: 970-731-4675
>>> Cell phone or for text messaging: 970-946-6584
>>>>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200524/8e040480/attachment.htm>


More information about the RE-Wrenches mailing list