<div dir="auto">It may take a little bit as it wrapped up just over 2 years ago, most of the research stayed at the lab. I do recall V2 did not survive the cycling test, it was unable to restart from 99% dod. There is no substitute for a multi-level battery management structure when it comes to Li tech. I have priced simplify dirt to keys and it cost more then Blue did and required more space. There was another one that came in near the end and was built in what appeared to be a 66&quot; tall chemical storage cabinet just to make it fire rated, maybe it&#39;s just me but batteries that can catch fire may not be the best choice but hey I&#39;m funny like that. Anyone installing any batteries needs to read the very fine print that talks about &quot;what to do in case of&quot; and that can be a deciding factor right there.<div dir="auto">Way back when all FLA&#39;s had to be in a pan to catch the acid before it did damage, that was 20 years ago by now it should be safer not more dangerous.</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sun, May 24, 2020, 8:36 PM jay &lt;<a href="mailto:jay.peltz@gmail.com">jay.peltz@gmail.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div style="word-wrap:break-word;line-break:after-white-space">HI Jerry,<div><br></div><div>Most impressive.</div><div><br></div><div>Would you be willing to tell us which ones didn\u2019t meet this test, if not publicly, then off list?</div><div><br></div><div>thanks</div><div><br></div><div>jay</div><div><br></div><div><br><div><br><blockquote type="cite"><div>On May 24, 2020, at 3:23 PM, Jerry Shafer &lt;<a href="mailto:jerrysgarage01@gmail.com" target="_blank" rel="noreferrer">jerrysgarage01@gmail.com</a>&gt; wrote:</div><br><div><div dir="auto">Wrenches<div dir="auto">Again not all batteries are the same, Chemistry, recharge rate or intelligence of the BMS, l have personally tested Blue planet batteries, l have let them sit at 100% SOC for 10 weeks, ran them at 30% SOC for 6 months, l have performed 100% to 0% cycling up to 4 times a day. This is the same tests l ran on a variety of Li tech batteries and BluePlanet is the only one that survived this testing. It&#39;s ore then spec sheets and cost, it comes down to success or failure, personally l like success and being able to pass or fail batteries without having my customers pay the price is a good thing. Blue Planet has 8000 cycles life and a 15 year warranty at 70% compare that to anything out there but again that&#39;s just me.</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sun, May 24, 2020, 1:32 PM Darryl Thayer &lt;<a href="mailto:darylsolar1@gmail.com" target="_blank" rel="noreferrer">darylsolar1@gmail.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="auto">I have spoken with a li battery<div dir="auto">researcher. Do not charge over 85% of battery full charge voltage and they will last over 25 years.   But go above or below bottom and trouble</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sun, May 24, 2020, 10:27 AM Jay &lt;<a href="mailto:jay.peltz@gmail.com" rel="noreferrer noreferrer" target="_blank">jay.peltz@gmail.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="auto"><div dir="ltr">One question I have for those more versed than me in lithium is, I\u2019m under the impression that having a lithium battery in float for years isn\u2019t good for it. Or at the very least it has to be cycled with some regularity. </div><div dir="ltr"><br></div><div dir="ltr">I\u2019d like to hear data on that</div><div dir="ltr"><br></div><div dir="ltr">Thx</div><div dir="ltr">Jay</div><div dir="ltr"><br></div><div dir="ltr">Peltz power. </div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br><blockquote type="cite">On May 23, 2020, at 10:08 PM, Ray &lt;<a href="mailto:ray@solarray.com" rel="noreferrer noreferrer noreferrer" target="_blank">ray@solarray.com</a>&gt; wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff
  
    
  
  
    <p>I suggest starting with a very simple look at the continuous
      output rating of the battery and match that to the inverter
      continuous rating. This ends up with quite a bit more battery than
      you might think at first.  However, if the customer paid the big
      bucks for a battery backup system, they should at least get enough
      battery to operate the inverter at its rated power.  Anything
      less, I would consider poor design.  The same goes for lead acid
      batteries, they just don&#39;t work well, even on grid, when the
      battery is undersized.  Even lead acid batteries have maximum
      current output ratings that should at least be matched to the
      inverter rating.   <br>
    </p><p>If you WERE going to under size the battery, then you should keep
      it safe by reducing the size of the inverter battery breaker as
      well.   I know this &quot;micro battery for GTB&quot; is becoming a trend,
      but it doesn&#39;t mean its right. <br>
    </p>
    <pre cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div>On 5/23/20 5:48 PM, Mick Abraham wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="ltr">Greetings, All~ Mark Frye had asked:  &quot;...with a
        4000w Outback Radian, AC coupled with 2000w of PV, what is the
        smallest Li battery I would want for stable operation?&quot;  
        <div><br>
        </div>
        <div>Mick&#39;s reply: In the lithium arena, one often finds the
          ratings in kilowatt-hours rather than in amp-hours. This is an
          easy conversion for us energy nerds to make, so below I&#39;m
          mainly using watts &amp; watt-hours with occasional
          conversions to amp-hours.</div>
        <div><br>
        </div>
        <div>I suggest that you start with the spec sheet (of whichever
          brand lithium battery is on your radar), &amp; see what the
          manufacturer says about &quot;allowable rate of recharge&quot;. You may
          find that C/2 is an acceptable rate with several
          manufacturers, Mark--much faster than what we&#39;re accustomed to
          with typical lead-acid batteries. Let&#39;s assume:</div>
        <div><br>
        </div>
        <div>* ...that your AC coupled PV array crests around 1800 watts
          to the battery when there are no loads</div>
        <div>* ...that the battery is below 100% state of charge, and</div>
        <div>* ...that the solar conditions are optimal. </div>
        <div><br>
        </div>
        <div>Let&#39;s further assume that those conditions represent your
          battery&#39;s highest energy rate in either direction. </div>
        <div><br>
        </div>
        <div>1800w X two hours = 3,600 watt-hours dividing by 48v
          nominal = 75 amp-hours in the above hypothetical situation. </div>
        <div><br>
        </div>
        <div>++++++++++++++++++++++++++++++</div>
        <div><br>
        </div>
        <div>
          The rate at which a battery can receive energy is (usually)
          also the rate at which it can comfortably deplete, so let&#39;s
          briefly look at the flip side: Assuming the battery mfr. wants
          the watt-hours to be no less than two times the maximum
          wattage, a 3600 watt-hour (C/2) battery should not be depleted
          faster than 1800 watts. Your 4kW Radian, Mark, could exceed
          that if the loads demand it--&amp; maybe your loads don&#39;t.
          Motor starting surges should probably be part of the thinking
          &amp; it wouldn&#39;t hurt to ask the mfr.&#39;s opinion about short
          term surges which briefly deplete the battery faster than the
          hypothetical two hour rate.</div>
        <div><br>
        </div>
        <div>By approaching this question based on the battery
          manufacturer do&#39;s &amp; don&#39;ts, one improves the chance of
          getting warranty coverage should it later be needed. &quot;What the
          large print giveth, the fine print taketh away.&quot; </div>
        <div><br>
        </div>
        <div>The Wrench List is the Bomb!  </div>
        <div><br clear="all">
          <div>
            <div dir="ltr" data-smartmail="gmail_signature">
              <div dir="ltr">
                <div>Mick Abraham, Proprietor<br>
                  <a href="http://www.abrahamsolar.com/" rel="noreferrer noreferrer noreferrer" target="_blank">www.abrahamsolar.com</a><br>
                  <br>
                  Landline: 970-731-4675</div>
                <div>Cell phone or for text messaging: 970-946-6584</div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <div hspace="streak-pt-mark" style="max-height:1px"><img alt="" style="width:0px;max-height:0px;overflow:hidden" src="https://mailfoogae.appspot.com/t?sender=abWlja0BhYnJhaGFtc29sYXIuY29t&amp;type=zerocontent&amp;guid=74c54196-b300-4b9d-8f4a-9fa513751306"><font size="1" color="#ffffff">\u1427</font></div>
      <br>
      <fieldset></fieldset>
      <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  

<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check out or update participant bios:</span><br><span><a href="http://www.members.re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a></span><br><span></span><br></div></blockquote></div>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org/" rel="noreferrer noreferrer noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
_______________________________________________<br>List sponsored by Redwood Alliance<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noreferrer">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br><br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">www.re-wrenches.org/etiquette.htm</a><br><br>Check out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">www.members.re-wrenches.org</a><br><br></div></blockquote></div><br></div></div>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>