[RE-wrenches] How much Li battery?

Dave Angelini Offgrid Solar offgridsolar at sti.net
Sun May 24 11:41:55 EDT 2020



My experience is that is really is about the cycles and the design life
of the battery. Both will give you an idea of how long it should last at
the amount of power you need. 

It is a poor design to over cycle and just
as poor to use so little power that the system life is exceeded without
using the power you paid for. The HALT testing gives an idea of life and
many battery makers do not tell you about accelerated testing.  

So, the
good part is they are fine with partial Soc, but the float it forever in
grid tie may not be good. I think they need to be exercised if they are to
be depended on. I have not seen anyone saying that. A good question Jay


Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridsolar at sti.net
[2]
text 209 813 0060

On Sun, 24 May 2020 07:15:53 -0700, Jay  wrote:  One
question I have for those more versed than me in lithium is, I'm under the
impression that having a lithium battery in float for years isn't good for
it. Or at the very least it has to be cycled with some regularity.    I'd
like to hear data on that   Thx Jay   Peltz power.          
 On May 23,
2020, at 10:08 PM, Ray  wrote:

I suggest starting with a very simple look
at the continuous output rating of the battery and match that to the
inverter continuous rating. This ends up with quite a bit more battery than
you might think at first. However, if the customer paid the big bucks for a
battery backup system, they should at least get enough battery to operate
the inverter at its rated power. Anything less, I would consider poor
design. The same goes for lead acid batteries, they just don't work well,
even on grid, when the battery is undersized. Even lead acid batteries have
maximum current output ratings that should at least be matched to the
inverter rating.  

If you WERE going to under size the battery, then you
should keep it safe by reducing the size of the inverter battery breaker as
well. I know this "micro battery for GTB" is becoming a trend, but it
doesn't mean its right.  
Ray Walters
Remote Solar
303 505-8760
 On 5/23/20
5:48 PM, Mick Abraham wrote:  Greetings, All~ Mark Frye had asked: "...with
a 4000w Outback Radian, AC coupled with 2000w of PV, what is the smallest
Li battery I would want for stable operation?"   Mick's reply: In the
lithium arena, one often finds the ratings in kilowatt-hours rather than in
amp-hours. This is an easy conversion for us energy nerds to make, so below
I'm mainly using watts & watt-hours with occasional conversions to
amp-hours.   I suggest that you start with the spec sheet (of whichever
brand lithium battery is on your radar), & see what the manufacturer says
about "allowable rate of recharge". You may find that C/2 is an acceptable
rate with several manufacturers, Mark--much faster than what we're
accustomed to with typical lead-acid batteries. Let's assume:   * ...that
your AC coupled PV array crests around 1800 watts to the battery when there
are no loads * ...that the battery is below 100% state of charge, and *
...that the solar conditions are optimal.    Let's further assume that
those conditions represent your battery's highest energy rate in either
direction.    1800w X two hours = 3,600 watt-hours dividing by 48v nominal
= 75 amp-hours in the above hypothetical situation.   
++++++++++++++++++++++++++++++   The rate at which a battery can receive
energy is (usually) also the rate at which it can comfortably deplete, so
let's briefly look at the flip side: Assuming the battery mfr. wants the
watt-hours to be no less than two times the maximum wattage, a 3600
watt-hour (C/2) battery should not be depleted faster than 1800 watts. Your
4kW Radian, Mark, could exceed that if the loads demand it--& maybe your
loads don't. Motor starting surges should probably be part of the thinking
& it wouldn't hurt to ask the mfr.'s opinion about short term surges which
briefly deplete the battery faster than the hypothetical two hour rate.  
By approaching this question based on the battery manufacturer do's ">ᐧ


_______________________________________________
List sponsored by Redwood
Alliance

List Address: RE-wrenches at lists.re-wrenches.org [4]

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[5]

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[6]

List rules & etiquette:
www.re-wrenches.org/etiquette.htm [7]

Check
out or update participant bios:
www.members.re-wrenches.org [8]

 
_______________________________________________
List sponsored by Redwood
Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List
rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update
participant bios:
www.members.re-wrenches.org
  

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridsolar at sti.net
[3]
http://www.abrahamsolar.com
[4]
mailto:RE-wrenches at lists.re-wrenches.org
[5]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[6]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[7]
http://www.re-wrenches.org/etiquette.htm
[8]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200524/ca69da5e/attachment.htm>


More information about the RE-Wrenches mailing list