[RE-wrenches] How much Li battery?

Dave Angelini Offgrid Solar offgridsolar at sti.net
Sun May 24 12:07:15 EDT 2020



When I mix a lead acid system and a lithium it often is done to use up
the life of the lead acid system. In this case, the lithium is just left
off and hopefully gets used and tested monthly or so. In winter offgrid,
the LFP gets used in bad weather and increases the days you can run in bad
weather without a generator. 

Doing this is a challenge as both batteries
have different set-points and I have never been able to use the same DC
buss for my clients. This DC bus is where the solar is. What I do is use a
seperate inverter for the lithium and charge it from the AC bus of the lead
acid inverter. 

It sounds complicated but it is just a flick of the AC
bypass in the power distribution panel of an XW or Radian. Another breaker
turns on the charger in the lithium inv/chg. Eventually the old lead acid
will go away. The clients love this as it gets them a completely
independent power system. They can do the same thing later and just have
two LFP banks/inverters.  

Dave Angelini Offgrid Solar
"we go where
powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail
offgridsolar at sti.net [2]
text 209 813 0060

On Sun, 24 May 2020 07:15:53
-0700, Jay  wrote:  One question I have for those more versed than me in
lithium is, I'm under the impression that having a lithium battery in float
for years isn't good for it. Or at the very least it has to be cycled with
some regularity.    I'd like to hear data on that   Thx Jay   Peltz power. 
       
 On May 23, 2020, at 10:08 PM, Ray  wrote:

I suggest starting
with a very simple look at the continuous output rating of the battery and
match that to the inverter continuous rating. This ends up with quite a bit
more battery than you might think at first. However, if the customer paid
the big bucks for a battery backup system, they should at least get enough
battery to operate the inverter at its rated power. Anything less, I would
consider poor design. The same goes for lead acid batteries, they just
don't work well, even on grid, when the battery is undersized. Even lead
acid batteries have maximum current output ratings that should at least be
matched to the inverter rating.  

If you WERE going to under size the
battery, then you should keep it safe by reducing the size of the inverter
battery breaker as well. I know this "micro battery for GTB" is becoming a
trend, but it doesn't mean its right.  
Ray Walters
Remote Solar
303
505-8760
 On 5/23/20 5:48 PM, Mick Abraham wrote:  Greetings, All~ Mark
Frye had asked: "...with a 4000w Outback Radian, AC coupled with 2000w of
PV, what is the smallest Li battery I would want for stable operation?"  
Mick's reply: In the lithium arena, one often finds the ratings in
kilowatt-hours rather than in amp-hours. This is an easy conversion for us
energy nerds to make, so below I'm mainly using watts & watt-hours with
occasional conversions to amp-hours.   I suggest that you start with the
spec sheet (of whichever brand lithium battery is on your radar), & see
what the manufacturer says about "allowable rate of recharge". You may find
that C/2 is an acceptable rate with several manufacturers, Mark--much
faster than what we're accustomed to with typical lead-acid batteries.
Let's assume:   * ...that your AC coupled PV array crests around 1800 watts
to the battery when there are no loads * ...that the battery is below 100%
state of charge, and * ...that the solar conditions are optimal.    Let's
further assume that those conditions represent your battery's highest
energy rate in either direction.    1800w X two hours = 3,600 watt-hours
dividing by 48v nominal = 75 amp-hours in the above hypothetical situation.
  ++++++++++++++++++++++++++++++   The rate at which a battery can receive
energy is (usually) also the rate at which it can comfortably deplete, so
let's briefly look at the flip side: Assuming the battery mfr. wants the
watt-hours to be no less than two times the maximum wattage, a 3600
watt-hour (C/2) battery should not be depleted faster than 1800 watts. Your
4kW Radian, Mark, could exceed that if the loads demand it--& maybe your
loads don't. Motor starting surges should probably be part of the thinking
& it wouldn't hurt to ask the mfr.'s opinion about short term surges which
briefly deplete the battery faster than the hypothetical two hour rate.  
By approaching this question based on the battery manufacturer do's ">ᐧ


_______________________________________________
List sponsored by Redwood
Alliance

List Address: RE-wrenches at lists.re-wrenches.org [4]

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[5]

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[6]

List rules & etiquette:
www.re-wrenches.org/etiquette.htm [7]

Check
out or update participant bios:
www.members.re-wrenches.org [8]

 
_______________________________________________
List sponsored by Redwood
Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List
rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update
participant bios:
www.members.re-wrenches.org
  

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridsolar at sti.net
[3]
http://www.abrahamsolar.com
[4]
mailto:RE-wrenches at lists.re-wrenches.org
[5]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[6]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[7]
http://www.re-wrenches.org/etiquette.htm
[8]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200524/2911e776/attachment.htm>


More information about the RE-Wrenches mailing list