On the FM100 landing page
<http://outbackpower.com/products/charge-controllers/flexmax-100>. The
warning is pasted below.
*Due to the different voltage ratings, OutBack Power does not recommend
mixing the FM100-300VDC with the FM60 or FM80-150VDC controllers on the
same battery bank.*
Interestingly the warning is not seen on the FM100 AFCI landing page
<http://outbackpower.com/products/charge-controllers/flexmax-100-afci>.
I thought I saw this also in one of the Owner’s manuals but I looked today
and can’t find it there. Interesting…
I have a client that wants to add a fourth PV array to a system with three
FM80s. This will require a fourth charge controller. Being able to run
smaller wire in the existing conduits is an attractive proposition, making
the FM100 a desirable approach. I now have to figure out if I can add the
FM100-AFCI (which is apparently the only version available) to a system
with three FM80s, and if I do, what do I do with the existing GFDI breaker
and how do I arrange the DC bond? There is a lot to consider here.
BTW, I was told by a tech support person for an on-line sales firm that the
original FM100 did not have the AFCI but those units have been
discontinued. Now all FM100s have the AFCI capability. I am weighing if I
want AFCI if it is not required. My territory includes central California
wild lands so I suppose I should take advantage of any fire safety means at
my disposal…
William
*From:* Jay [mailto:jay.peltz at gmail.com]
*Sent:* Friday, May 15, 2020 7:34 AM
*To:* william at millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Outback FM100
Hi William
Yes downsizing breaker to meet load is no problem. And getting wire that
big into it with 1” KO is a pain.
I’m pretty sure any hub will work, needs 3S mate
Where in the manual did you find the “don’t mix with other 60/80
controllers?
Jay
Peltz power
On May 15, 2020, at 12:46 AM, William Miller <william at millersolar.com>
wrote:
Friends:
I have occasion to try the FM100 charge controller. I am wondering of
anyone had found any quirks with implementing this device. I have a few
specific questions:
1. I want to avoid AFCI unless mandated. Will this be defeated if I
don’t run the leads through the sense coil? (There is an AFCI and non-AFCI
version but I can’t seem to find the non-AFCI version anywhere.)
2. I noticed the manual indicates you are not supposed to mix the
FM100 with the FM80 or 60 in the same battery system. This negates it for
one project I had in mind. I am curious as to why this is. Anyone know?
3. Will the FM100 work with a standard hub?
4. I suppose this unit requires a 125 amp breaker. If the PV array
cannot support that full 100 amps I might down-size the OCPD accordingly.
Anyone contemplate this question?
Thanks in advance.
William
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200515/cd53dccd/attachment.htm>
More information about the RE-Wrenches
mailing list