Hi William
Yes downsizing breaker to meet load is no problem. And getting wire that big into it with 1” KO is a pain.
I’m pretty sure any hub will work, needs 3S mate
Where in the manual did you find the “don’t mix with other 60/80 controllers?
Jay
Peltz power
> On May 15, 2020, at 12:46 AM, William Miller <william at millersolar.com> wrote:
>
>
> Friends:
>
> I have occasion to try the FM100 charge controller. I am wondering of anyone had found any quirks with implementing this device. I have a few specific questions:
>
> 1. I want to avoid AFCI unless mandated. Will this be defeated if I don’t run the leads through the sense coil? (There is an AFCI and non-AFCI version but I can’t seem to find the non-AFCI version anywhere.)
> 2. I noticed the manual indicates you are not supposed to mix the FM100 with the FM80 or 60 in the same battery system. This negates it for one project I had in mind. I am curious as to why this is. Anyone know?
> 3. Will the FM100 work with a standard hub?
> 4. I suppose this unit requires a 125 amp breaker. If the PV array cannot support that full 100 amps I might down-size the OCPD accordingly. Anyone contemplate this question?
>
> Thanks in advance.
>
> William
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200515/6f771b90/attachment.htm>
More information about the RE-Wrenches
mailing list