[RE-wrenches] Stand alone battery charger
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Wed Apr 22 11:06:48 EDT 2020
Also consider that the engineer is calling out xw+6848 which does have
firmware support that stopped on the old graybox xw6048. Make sure you at
least have the latest firmware in your 6048s' and that it is all the same.
It is on the schneider site under discontinued products. Good Luck with
this!
Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridsolar at sti.net
[2]
text 209 813 0060
On Wed, 22 Apr 2020 09:18:26 -0400, Jason Szumlanski
wrote: Interesting. I am going to look into that. We are manually
stopping the generator (the BMS kills the two-wire start signal). I don't
think the AC2 transfer time matters much in terms of solving the clients
complaints, but I will play with that also. Thanks!
On Wed, Apr 22, 2020 at 8:18 AM Tump wrote: KISS.... have you
checked the low voltage setting on AC2? Make sure that is is not set to the
default settings. AC Transfer time? I set to the lowest time, I believe its
1. You also have 4 inverters what IS the charge setting of these units?
"Gen assist" enabled? Info from Schneider engineer below; The AGS will
cause XW+ to disconnect the generator when a stop signal is sent (Auto
Stop) for the generator cool down period (user adjustable-AGS>Advanced
Settings>Cfg Gen). If you are just manually stopping the generator, then it
is possible for the XW+ to stay connected all the way down to 80V unless
you increase that low AC value in XW+>Advanced Settings>AC Settings menu.
_AC2 TRANSFER TIME MAY ALSO BE ADJUSTED (DEFAULT IS 40S) USING COMBOX,
GATEWAY OR CONFIG TOOL. THIS IS THE TIME IT TAKES TO SWITCH FROM GEN TO
INVERTING. _ Hope that helps, Eric On Apr 21, 2020, at 4:27 PM, Jason
Szumlanski wrote:
The issue is during switching only. During inverter
operation everything is silky smooth. During generator operation things are
mostly smooth, but large loads that come on or off during heavy charging
can cause some surging, but that is more a function of a junky generator
(which was just replaced with a better unit). So the natural conclusion
by the client is let's just run on battery/inverter all the time. And it
does make sense. And it's his money.
(239) 410-4985
On Tue, Apr 21, 2020 at 2:29 PM Ray wrote:
Are you sure its just the
transfer switching causing problems? I've seen quite a bit of lights
dimming, flickering, and strangeness with XW inverters ( and many others)
just in normal operation. Certain LEDs are particularly sensitive, just
another appliance coming on can cause noticeable flicker that bothers some
clients. Our solution was to try different brands of LEDs till we found
ones that had less trouble. I recall the Phillips ones being good, but you
would have to test a few to see.
Ray Walters
Remote Solar
303 505-8760
On 4/21/20 12:26 PM, Jason Szumlanski wrote: I have not looked into
that, but the problem also exists transferring from inverter to generator.
The owner wants "clean" power all the time, and just keeping him on
inverter power all the time would be a solution.
On Tue, Apr 21, 2020 at 9:35 AM Tump wrote: Have you shortened the
transfer time from gen to inv, voltage "cut out"acceptance of the gen in
power instead of their 90Vac to say 110V/L ? Raising the output voltage on
the 6848s border-left:#1010ff 2px solid; margin-left:5px; width:100%"> On
Apr 21, 2020, at 8:27 AM, Jason Szumlanski wrote:
I actually need
400Adc at 51V nominal of total charge rate. I was hoping to use 100Adc
chargers for redundancy, or some combination of 2-8 chargers to reach the
needed current, assuming they can be synced up. I don't think the charging
algorithm needs to be complicated. We are basically bulk charging the LiPOs
to 80% with the battery BMS controlling the generator. The concept is to
get to 80% sometime in the night and solar kicks in during the day to reach
100% using 2-stage charging from the XW charge controllers. The problem I
have is the quad XW6048s in the system run at a pretty good load
typically... often over 50%. This is off-grid with generator backup. The
transfer switches in the XW6048 are causing surges and brownouts when the
switched loads are high, especially smart dimmers and televisions. I need
seamless power for this client. My thought is to abandon the internal
chargers in the XW6048s and just run loads off inverter power full-time. I
would charge the batteries with external battery chargers. The tricky part
is how to adjust the charge rate based on load, and also based on solar
input. I need to limit the net charging current. Of course, I still need
400Adc of charging current, which I'm learning might be hard to find. I
don't really want to buy four more XWs - that's a pretty expensive
solution. Jason Szumlanski Florida Solar Design Group
On Fri, Apr
17, 2020 at 4:26 PM Dave Angelini Offgrid Solar wrote:
I use the CSW
4048. It has a 50 amp charger. A good spare for clients. Get 2 of them.
Repurpose an old Radian or XW well over 100A. XW+ is 140adc.
DAVE
ANGELINI OFFGRID SOLAR
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [15]
e-mail
offgridsolar at sti.net [16]
text 209 813 0060
On Fri, 17 Apr 2020 14:21:14
-0400, Jason Szumlanski wrote: I'm looking for a standalone 51V nominal
battery charger suitable for a LiPO battery with 2-stage charging and
adjustable setpoints for max current and battery voltage. It would require
dual chargers with 100A capacity (I want dual chargers for redundancy so I
have at least 50% capacity if one goes bad). Ideally they would sync up so
they change stages simultaneously, but I'm not sure if that's really
important. Who makes something like that? Jason Szumlanski
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [18]
Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [19]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[20]
List rules " alt="" width="0" height="0" />
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [23]
Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [24]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[25]
List rules border-left:#1010ff 2px solid; margin-left:5px;
width:100%"> TUMP at SWNL.NET WWW.SWNL.NET Solarwinds Northernlights _
_ _ SERVING MID COAST MAINE ">
_ 207-832-7574 CL. 610-517-8401 _ _ __BLAIR
"TUMP" MAY_
******** MAINE'S CHARTER ********
_ __ NABCEP "CERTIFIED PV
INSTALLER"_
******** MAINE'S CHARTER ********
_ TRACE XANTREX
"CERTIFIED" DEALER / INSTALLER"_
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [28]
Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [29]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[30]
List rules " alt="" width="0" height="0" />
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [33]
Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[34]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[35]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [36]
Check
out or update participant bios:
www.members.re-wrenches.org [37]
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [38]
Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [39]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[40]
List rules "
src="data:image/gif;base64,R0lGODlhAQABAIAAAAAAAP///yH5BAEAAAAALAAAAAABAAEAAAIBRAA7"
alt="" width="0" height="0" />
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [43]
Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[44]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[45]
List rules border-left:#1010ff 2px solid; margin-left:5px;
width:100%"> TUMP at SWNL.NET WWW.SWNL.NET Solarwinds Northernlights _
_ _ SERVING MID COAST MAINE ">
_ 207-832-7574 CL. 610-517-8401 _ _ __BLAIR
"TUMP" MAY_
******** MAINE'S CHARTER ********
_ __ NABCEP "CERTIFIED PV
INSTALLER"_
******** MAINE'S CHARTER ********
_ TRACE XANTREX
"CERTIFIED" DEALER / INSTALLER"_
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [48]
Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [49]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[50]
List rules "
src="https://webmail.sti.net/tuxedo/?_task=mail&_action=display-attachment&_file=rcmfile11587567780091358700"
alt="" width="0" height="0" />
Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridsolar at sti.net
[3]
mailto:tump at swnl.net
[4] mailto:jason at floridasolardesigngroup.com
[5]
https://mailtrack.io/trace/link/66033386a2a45137f2b120abb405cca4e927d183?url=http%3A%2F%2Fwww.floridasolardesigngroup.com%2F&userId=1613865&signature=4f411814c62fe532
[6]
http://webmail.sti.net/tel:(239)+491-8010
[7]
https://mailtrack.io/trace/link/820314f28a259bd71c900c3d37295758887d5c04?url=http%3A%2F%2Fwww.FloridaSolarDesignGroup.com&userId=1613865&signature=a8e03312019dcafc
[8]
https://mailtrack.io/trace/link/07e1e531a45de497a46be66e6fd5ef0d301cb2b6?url=https%3A%2F%2Fwww.facebook.com%2Ffloridasolardesigngroup&userId=1613865&signature=8fc87785daeb6626
[9]
https://mailtrack.io/trace/link/650dd5b2dbef8e11b3a7fe576865160d8faa8e0a?url=https%3A%2F%2Ftwitter.com%2FFloridaSolarDG&userId=1613865&signature=8a8fc1a336f4dfb7
[10]
https://mailtrack.io/trace/link/05be406956337ef2c9e2a768972030fdda96636b?url=https%3A%2F%2Fwww.youtube.com%2Fchannel%2FUCjnsYt5r7DNJD3ZnqI10j8g&userId=1613865&signature=238dfb7609b42168
[11]
mailto:ray at solarray.com
[12] mailto:tump at swnl.net
[13]
mailto:jason at floridasolardesigngroup.com
[14]
mailto:offgridsolar at sti.net
[15]
https://mailtrack.io/trace/link/290c2833767afa7e7c0b639ab4d233b97fddd564?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=e52be68029129b4f
[16]
mailto:offgridsolar at sti.net
[17]
mailto:jason at floridasolardesigngroup.com
[18]
mailto:RE-wrenches at lists.re-wrenches.org
[19]
https://mailtrack.io/trace/link/2c8383435a52be99ea6f1adaf9dfaa2f1b3fb259?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=59aaebd1c76f9454
[20]
https://mailtrack.io/trace/link/8f98d67ae7b562b5855cb7cc6f1cb42e11a50a99?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=d07f36493c98b97b
[21]
https://mailtrack.io/trace/link/8f81d3140b61586335b7c5ed188783f0342bc2ab?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8dd98de73b717e94
[22]
https://mailtrack.io/trace/link/291c006dfa87eb9a60fdce3f9acfa512e3fc9523?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=05d52193d638afd6
[23]
mailto:RE-wrenches at lists.re-wrenches.org
[24]
https://mailtrack.io/trace/link/2b9c7e98f244f36f6f97acebbb31fa6f52bb083d?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=766fe3dd1e1f938a
[25]
https://mailtrack.io/trace/link/513dffc08f8ebd182e2fc9cd208b1ab5dd5a5329?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=ee7f76ae7d350857
[26]
https://mailtrack.io/trace/link/a51bdf407e4e0bb98e02e71af34330c35f325698?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=c333baa0c0aa0736
[27]
https://mailtrack.io/trace/link/d527bd19df5a7006163ddb66e3409cdda563e359?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f6f4243adaf90546
[28]
mailto:RE-wrenches at lists.re-wrenches.org
[29]
https://mailtrack.io/trace/link/b699f67e4c9e3507bd5c739adc3c5256e8eab61e?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c282925db000f213
[30]
https://mailtrack.io/trace/link/500f7759e1ba4092cf35974752b887ea353397eb?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=18ea22ac66c0e187
[31]
https://mailtrack.io/trace/link/a704281366810bdedf8dca9206732ec881b97237?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=598ebb3877e1425b
[32]
https://mailtrack.io/trace/link/64b50b1f31a2e2ed2c41796cb1e3f872a0c8c3f3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=e853edec7f4e5783
[33]
mailto:RE-wrenches at lists.re-wrenches.org
[34]
https://mailtrack.io/trace/link/10d6d463155f275b52fedff26d22cddd175cf75e?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=fa3e2215a2b180be
[35]
https://mailtrack.io/trace/link/433140c89638905f48058ed76695feb11780fd94?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=4c161acf68a712f7
[36]
https://mailtrack.io/trace/link/ba6694855252cb96f47c5cbb640dacf62ff28590?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f4ab19ce4fb08805
[37]
https://mailtrack.io/trace/link/d0bc581668f9d9edb45e897931a6b7a24264f028?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4f5c75021e62fc91
[38]
mailto:RE-wrenches at lists.re-wrenches.org
[39]
https://mailtrack.io/trace/link/94c6c205af838d5c8a00179dd448b37cd493ca4f?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c79e932e7280e377
[40]
https://mailtrack.io/trace/link/ff405a5330a5bf63ad8e4d1e282d85a2176301cd?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=6ce95c12b87c5665
[41]
https://mailtrack.io/trace/link/b15bf50b7775f752a12dc98f10c84ef31b3f556b?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=c0606f62e56a2961
[42]
https://mailtrack.io/trace/link/831a26af6eb4aa8f26a4affdc946762acbbeab21?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=db3a284220a0f623
[43]
mailto:RE-wrenches at lists.re-wrenches.org
[44]
https://mailtrack.io/trace/link/929c119d764128c429afefbc2b8c6aa79080b589?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c28046f1773b0816
[45]
https://mailtrack.io/trace/link/e4b652c227c1c6d738e58667d5574202b8e6a6a8?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=3a9b447344ddd63c
[46]
https://mailtrack.io/trace/link/87b69231252f231980cd831f20505b27ffefc53a?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=57b721191d4d6e0d
[47]
https://mailtrack.io/trace/link/2d9831d4b94ce6df65cb60a35bc29f23ef3257c1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=a8cc7d3017723263
[48]
mailto:RE-wrenches at lists.re-wrenches.org
[49]
https://mailtrack.io/trace/link/6ce64c74070cebafe3c06b49b8212ff7e140fea8?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=02f70045987b6b59
[50]
https://mailtrack.io/trace/link/e4b652c227c1c6d738e58667d5574202b8e6a6a8?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=3a9b447344ddd63c
[51]
https://mailtrack.io/trace/link/87b69231252f231980cd831f20505b27ffefc53a?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=57b721191d4d6e0d
[52]
https://mailtrack.io/trace/link/2d9831d4b94ce6df65cb60a35bc29f23ef3257c1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=a8cc7d3017723263
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200422/134194af/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200422/134194af/attachment.gif>
More information about the RE-Wrenches
mailing list