[RE-wrenches] OK, so what would happen if I do this...
Kent Osterberg
kent at coveoregon.com
Wed Mar 4 11:59:57 EST 2020
If using an ac battery charger to get power around the inverter to the
batteries it would have to be rated for the full power of the PV array.
Otherwise, you couldn't divert the full power of the array on the dc
side. For a 24-volt battery, it would require a battery charger rated
for over 80 amps. That alone seems risky with a 100Ah battery. To add to
the difficulty of this approach the battery charger would add a delay
time in the control loop that would almost certainly result in an
unstable system.
Kent Osterberg
On 3/3/2020 7:53 PM, Jay wrote:
> Or a charger such as Iota, or power max.
>
> Jay
> Peltz power.
>
>> On Mar 3, 2020, at 7:24 PM, don at energysolarnow.com wrote:
>>
>>
>> You wrote that you would connect the Exeltech to just one of the
>> service phases.
>> But most GT inverters are 240 and require both phases. Is yours
>> different? You did not mention which model it is.
>> Also, as Kent Osterberg mentioned, the Exeltech will not charge its
>> batteries from the AC output.
>> Your scheme with the PLC controlling an SCR leaves unaddressed how
>> any charge current gets directed into the batteries to allegedly
>> raise their voltage. Is there a charger somewhere in this scheme?
>> You still need some way to charge batteries from solar. How about
>> connecting a charge controller to some of the solar panels?
>>
>> Don Barch
>> Energy Solar
>>
>> -------- Original Message --------
>> Subject: RE-wrenches Digest, Vol 13, Issue 59
>> From: re-wrenches-request at lists.re-wrenches.org
>> <mailto:re-wrenches-request at lists.re-wrenches.org>
>> Date: Sun, March 01, 2020 2:19 pm
>> To: re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>
>>
>> Send RE-wrenches mailing list submissions to
>> re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>> or, via email, send a message with subject or body 'help' to
>> re-wrenches-request at lists.re-wrenches.org
>> <mailto:re-wrenches-request at lists.re-wrenches.org>
>>
>> You can reach the person managing the list at
>> re-wrenches-owner at lists.re-wrenches.org
>> <mailto:re-wrenches-owner at lists.re-wrenches.org>
>>
>> When replying, please edit your Subject line so it is more specific
>> than "Re: Contents of RE-wrenches digest..."
>>
>>
>> When responding to posts within the Digest, be sure to restore
>> the Subject: line to the original, and please edit out any
>> extraneous lines from the quoted message.
>>
>>
>> Today's Topics:
>>
>> 1. OK, so what iwould happen if I do this... (Mark Frye)
>> 2. Re: OK, so what iwould happen if I do this... (frenergy)
>> 3. Re: OK, so what iwould happen if I do this... (Kent Osterberg)
>> 4. Re: OK, so what iwould happen if I do this... (Jerry Shafer)
>>
>>
>> ----------------------------------------------------------------------
>>
>> Message: 1
>> Date: Sat, 29 Feb 2020 15:27:32 -0800
>> From: Mark Frye <markf at berkeleysolar.com
>> <mailto:markf at berkeleysolar.com>>
>> To: RE-wrenches <re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>>
>> Subject: [RE-wrenches] OK, so what iwould happen if I do this...
>> Message-ID:
>> <93731c38-40b5-7c63-1d74-a879fbdd9d74 at berkeleysolar.com
>> <mailto:93731c38-40b5-7c63-1d74-a879fbdd9d74 at berkeleysolar.com>>
>> Content-Type: text/plain; charset=utf-8; format=flowed
>>
>> I have 2kw of grid tied PV on my house.
>>
>> Suppose I:
>>
>> - Open the main breaker to disconnect from the grid
>>
>> - I open the PV breaker
>>
>> - I connect a small good quality inverter like an Exeltech XP 500
>> to one
>> of the phases of the service (120 VAC)
>>
>> - I put a small battery pack, 100 AH at 24 VDC on the inverter
>>
>> OK so far, I could run some small loads for a relatively short
>> period of
>> time before the batteries get low
>>
>> -I have a PLC with an AD input and DA output. On the input I
>> measure the
>> battery voltage, on the output I control a SCR. The SCR controls
>> a 2kw
>> immersion heater sitting in a big bucket of water. The PLC has a
>> scan
>> time of 2 mS and I program it to increase the duty cycle of the
>> SCR as
>> voltage of the battery rises above 24 VDC.
>>
>> OK so far nothing has really changed from above.
>>
>> - I close the PV breaker, the GT inverters see the battery inverter,
>> sync and connect after five minutes.
>>
>> Voila, I can run house loads from 0 to 2kw with my existing GT PV
>> with
>> the balance of energy dumped as needed to the immersion heater.
>>
>> Right?
>>
>> Mark Frye
>>
>>
>>
>> ------------------------------
>>
>> Message: 2
>> Date: Sun, 1 Mar 2020 06:26:27 -0800
>> From: frenergy <frenergy at psln.com <mailto:frenergy at psln.com>>
>> To: re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>
>> Subject: Re: [RE-wrenches] OK, so what iwould happen if I do this...
>> Message-ID: <c97234cd-4441-34d7-740c-51f07837b081 at psln.com
>> <mailto:c97234cd-4441-34d7-740c-51f07837b081 at psln.com>>
>> Content-Type: text/plain; charset=utf-8; format=flowed
>>
>> Mark,
>>
>> ??? ??? ??? OR, you change-out your inverter to an SMA with Secure
>> Power Supply and during grid power outage, while there is some
>> sun on
>> the panels, you would have up to 2KW of 120VAC power on the SPS
>> circuit
>> by just flipping a switch. We usually install a 4X outdoor box
>> with a
>> 120 VAC outlet ganged with a switch right under the inverter and
>> let the
>> customer run the power to the : frig, lights, battery charger, TV or
>> whatever during an outage, though some romex could be run to
>> close to
>> the frig.
>>
>> Bill
>>
>> Feather River Solar Electric
>> Bill Battagin, Owner
>> 4291 Nelson St.
>> Taylorsville, CA 95983
>> 530.284.7849
>> CA Lic 874049
>> www.frenergy.net <http://www.frenergy.net>
>>
>> On 2/29/2020 3:27 PM, Mark Frye wrote:
>> > I have 2kw of grid tied PV on my house.
>> >
>> > Suppose I:
>> >
>> > - Open the main breaker to disconnect from the grid
>> >
>> > - I open the PV breaker
>> >
>> > - I connect a small good quality inverter like an Exeltech XP
>> 500 to
>> > one of the phases of the service (120 VAC)
>> >
>> > - I put a small battery pack, 100 AH at 24 VDC on the inverter
>> >
>> > OK so far, I could run some small loads for a relatively short
>> period
>> > of time before the batteries get low
>> >
>> > -I have a PLC with an AD input and DA output. On the input I
>> measure
>> > the battery voltage, on the output I control a SCR. The SCR
>> controls a
>> > 2kw immersion heater sitting in a big bucket of water. The PLC
>> has a
>> > scan time of 2 mS and I program it to increase the duty cycle
>> of the
>> > SCR as voltage of the battery rises above 24 VDC.
>> >
>> > OK so far nothing has really changed from above.
>> >
>> > - I close the PV breaker, the GT inverters see the battery
>> inverter,
>> > sync and connect after five minutes.
>> >
>> > Voila, I can run house loads from 0 to 2kw with my existing GT
>> PV with
>> > the balance of energy dumped as needed to the immersion heater.
>> >
>> > Right?
>> >
>> > Mark Frye
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>> >
>> > Change listserver email address & settings:
>> >
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> >
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>> >
>> >
>> --
>>
>>
>> --
>> This email has been checked for viruses by Avast antivirus software.
>> https://www.avast.com/antivirus
>>
>>
>>
>>
>> ------------------------------
>>
>> Message: 3
>> Date: Sun, 1 Mar 2020 08:58:45 -0800
>> From: Kent Osterberg <kent at coveoregon.com
>> <mailto:kent at coveoregon.com>>
>> To: re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>
>> Subject: Re: [RE-wrenches] OK, so what iwould happen if I do this...
>> Message-ID: <9e32901e-c5d4-ff70-9c44-406cc6d48d50 at coveoregon.com
>> <mailto:9e32901e-c5d4-ff70-9c44-406cc6d48d50 at coveoregon.com>>
>> Content-Type: text/plain; charset=utf-8; format=flowed
>>
>> Mark,
>>
>> I believe that your plan would fail because you are forcing power to
>> flow through the XP inverter backwards to charge the batteries. I
>> don't
>> believe the XP inverter can do that. The grid tied inverter would
>> probably connect then immediately shut down, or connect and
>> immediately
>> ruin the XP inverter. It would work if you had a inverter with a
>> bidirectional architecture like a Magnum, Outback, or Schneider
>> inverter. But even then you'd have a hazardous situation because the
>> cooling water is going to evaporate.
>>
>> Kent Osterberg
>> Blue Mountain Solar
>>
>>
>> On 2/29/2020 3:27 PM, Mark Frye wrote:
>> > I have 2kw of grid tied PV on my house.
>> >
>> > Suppose I:
>> >
>> > - Open the main breaker to disconnect from the grid
>> >
>> > - I open the PV breaker
>> >
>> > - I connect a small good quality inverter like an Exeltech XP
>> 500 to
>> > one of the phases of the service (120 VAC)
>> >
>> > - I put a small battery pack, 100 AH at 24 VDC on the inverter
>> >
>> > OK so far, I could run some small loads for a relatively short
>> period
>> > of time before the batteries get low
>> >
>> > -I have a PLC with an AD input and DA output. On the input I
>> measure
>> > the battery voltage, on the output I control a SCR. The SCR
>> controls a
>> > 2kw immersion heater sitting in a big bucket of water. The PLC
>> has a
>> > scan time of 2 mS and I program it to increase the duty cycle
>> of the
>> > SCR as voltage of the battery rises above 24 VDC.
>> >
>> > OK so far nothing has really changed from above.
>> >
>> > - I close the PV breaker, the GT inverters see the battery
>> inverter,
>> > sync and connect after five minutes.
>> >
>> > Voila, I can run house loads from 0 to 2kw with my existing GT
>> PV with
>> > the balance of energy dumped as needed to the immersion heater.
>> >
>> > Right?
>> >
>> > Mark Frye
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>> >
>> > Change listserver email address & settings:
>> >
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> >
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>> >
>> >
>>
>>
>>
>> ------------------------------
>>
>> Message: 4
>> Date: Sun, 1 Mar 2020 07:31:36 -1000
>> From: Jerry Shafer <jerrysgarage01 at gmail.com
>> <mailto:jerrysgarage01 at gmail.com>>
>> To: RE-wrenches <re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>>
>> Subject: Re: [RE-wrenches] OK, so what iwould happen if I do this...
>> Message-ID:
>> <CAMUFgmVYBnMmzgE__tjDS9xpFsOU59jdf3wwSkFhjw291VGH0g at mail.gmail.com
>> <mailto:CAMUFgmVYBnMmzgE__tjDS9xpFsOU59jdf3wwSkFhjw291VGH0g at mail.gmail.com>>
>> Content-Type: text/plain; charset="utf-8"
>>
>> Mark
>> What you are saying is to AC couple but most likely this would
>> fail as your
>> battery fills not enough loads HBCO or to much loads and your
>> battery does
>> a LBCO, either way you would be better off spending the money in
>> a maybe a
>> Outback Skybox easy install and is high voltage PV input and even
>> a small
>> 48 volt bank but think about storage
>> Jerry
>>
>> On Sat, Feb 29, 2020 at 1:27 PM Mark Frye
>> <markf at berkeleysolar.com <mailto:markf at berkeleysolar.com>> wrote:
>>
>> > I have 2kw of grid tied PV on my house.
>> >
>> > Suppose I:
>> >
>> > - Open the main breaker to disconnect from the grid
>> >
>> > - I open the PV breaker
>> >
>> > - I connect a small good quality inverter like an Exeltech XP
>> 500 to one
>> > of the phases of the service (120 VAC)
>> >
>> > - I put a small battery pack, 100 AH at 24 VDC on the inverter
>> >
>> > OK so far, I could run some small loads for a relatively short
>> period of
>> > time before the batteries get low
>> >
>> > -I have a PLC with an AD input and DA output. On the input I
>> measure the
>> > battery voltage, on the output I control a SCR. The SCR
>> controls a 2kw
>> > immersion heater sitting in a big bucket of water. The PLC has
>> a scan
>> > time of 2 mS and I program it to increase the duty cycle of the
>> SCR as
>> > voltage of the battery rises above 24 VDC.
>> >
>> > OK so far nothing has really changed from above.
>> >
>> > - I close the PV breaker, the GT inverters see the battery
>> inverter,
>> > sync and connect after five minutes.
>> >
>> > Voila, I can run house loads from 0 to 2kw with my existing GT
>> PV with
>> > the balance of energy dumped as needed to the immersion heater.
>> >
>> > Right?
>> >
>> > Mark Frye
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>> >
>> > Change listserver email address & settings:
>> >
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> >
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>> >
>> >
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL:
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20200301/a993182d/attachment-0001.html>
>>
>> ------------------------------
>>
>> Subject: Digest Footer
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>>
>> ------------------------------
>>
>> End of RE-wrenches Digest, Vol 13, Issue 59
>> *******************************************
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200304/599f8d05/attachment.htm>
More information about the RE-Wrenches
mailing list