[RE-wrenches] Solectria TL woes
Jeff Irish, PE
jeff.irish at suncommon.com
Tue Feb 25 15:55:53 EST 2020
Andrew, I've seen this in multiple inverter systems when the AC voltage
gets pushed outside the upper limit by the inverter output currents. One
or two inverters will cycle on-off, those with the lowest setting or
tolerance. Cause can be (1) high AC voltage from the utility to start
with, and/or (2) high impedance looking into the grid from the inverters,
usually from an undersized or loose service conductor.
Jeff
On Tue, Feb 25, 2020 at 3:16 PM Jerry Shafer <jerrysgarage01 at gmail.com>
wrote:
> Andrew
> What is the AC Voltage when this occurs, to much VAC will shut down the
> inverter. It also looks like you are clipping all the inverters during the
> mid day, is due to low temps or does this always happen. What is the DC
> MPPT voltage, is it at the upper limit.
> Jerry
> NABCEP PV inspector
>
> On Tue, Feb 25, 2020, 12:02 PM Andrew Truitt <atruitt at gmail.com> wrote:
>
>>
>> Wrenches,
>>
>> I have a couple of Solectria 36TLs at a small community solar site in CO
>> that shut themselves down occasionally for what appears to be no reason.
>>
>> [image: image.png]
>>
>> Voltages and frequency are normal, firmware is updated, IR scan shows
>> nothing irregular, and the other 2 inverters at the site (50TLs) are fine.
>> It can happen under sunny or cloudy conditions. Solectria will RMA the
>> inverters but before I go out and replace I'm curious if anyone has seen
>> this behavior?
>>
>>
>> Regards,
>>
>> Andrew Truitt
>>
>> www.dr.ventures
>> d: 202.486.7507
>>
>> NABCEP Certified PV Installation Professional ID: 032407-66
>> Colorado Journeyman Electrician License No.: 600132
>>
>> <https://www.linkedin.com/in/andrewtruitt/>
>>
>> [image: Logo]
>>
>> The content of this email is confidential and intended for the recipient
>> specified in this message only. It is strictly forbidden to share any part
>> of this message with any third party, without written consent of the
>> sender. If you received this message by mistake, please reply to this
>> message and follow with its deletion, so that we can ensure such a mistake
>> does not occur in the future.
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
Jeff Irish, PE
<https://medium.com/gender-inclusivit/why-i-put-pronouns-on-my-email-signature-and-linkedin-profile-and-you-should-too-d3dc942c8743>
| Vice President
SunCommon.com | Main: 845-876-3767
13 Hook Road, Rhinebeck, NY 12572
<https://suncommon.com/solar-winter-discount-2020/>
SunCommon believes that everyone has the right to a healthy
environment and brighter
future—and renewable energy is where it starts. Energy from the sun can power
our lives and build vibrant communities. Our mission is to tear down
barriers to clean energy and use our business as a force for good.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200225/9e8d72c3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 71945 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200225/9e8d72c3/attachment.png>
More information about the RE-Wrenches
mailing list