[RE-wrenches] Solectria TL woes
Jerry Shafer
jerrysgarage01 at gmail.com
Tue Feb 25 15:16:15 EST 2020
Andrew
What is the AC Voltage when this occurs, to much VAC will shut down the
inverter. It also looks like you are clipping all the inverters during the
mid day, is due to low temps or does this always happen. What is the DC
MPPT voltage, is it at the upper limit.
Jerry
NABCEP PV inspector
On Tue, Feb 25, 2020, 12:02 PM Andrew Truitt <atruitt at gmail.com> wrote:
>
> Wrenches,
>
> I have a couple of Solectria 36TLs at a small community solar site in CO
> that shut themselves down occasionally for what appears to be no reason.
>
> [image: image.png]
>
> Voltages and frequency are normal, firmware is updated, IR scan shows
> nothing irregular, and the other 2 inverters at the site (50TLs) are fine.
> It can happen under sunny or cloudy conditions. Solectria will RMA the
> inverters but before I go out and replace I'm curious if anyone has seen
> this behavior?
>
>
> Regards,
>
> Andrew Truitt
>
> www.dr.ventures
> d: 202.486.7507
>
> NABCEP Certified PV Installation Professional ID: 032407-66
> Colorado Journeyman Electrician License No.: 600132
>
> <https://www.linkedin.com/in/andrewtruitt/>
>
> [image: Logo]
>
> The content of this email is confidential and intended for the recipient
> specified in this message only. It is strictly forbidden to share any part
> of this message with any third party, without written consent of the
> sender. If you received this message by mistake, please reply to this
> message and follow with its deletion, so that we can ensure such a mistake
> does not occur in the future.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200225/514e8e89/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 71945 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200225/514e8e89/attachment.png>
More information about the RE-Wrenches
mailing list