Ray, I spent a bit of time today with a person who inspects for several
state renewable energy programs and to summarize, this person said the
opposite of what you said, and finish saying "seems pretty clear cut".
We did review three sections of 690, and one from 705. I pointed out
that these are not controlled conductors as I interpret them but they
should have been defined. I did not see any earlier posts regarding
this, so I apologize for the redundancy.
On 2/13/2020 3:16 PM, Ray wrote:
>
> This has been discussed to death in previous Wrench strings. Just to
> cut to the chase:
>
> please review NEC 2017, Figure 690.1(b) Note:(2). /The PV system
> disconnect in these diagrams separates the PV system from all other
> systems.//
> /
>
> The inverter, charge controller, batteries etc are no longer part of
> article 690, and are not subject to its requirements. Look at articles
> 705, 706, and 480 for guidance for those _/other systems/_.
>
> /Ray Walters/
> Remote Solar
> 303 505-8760
> On 2/13/20 12:55 PM, Dave Angelini Offgrid Solar wrote:
>> Hi Chris,
>>
>> A few times and my back-up with a schneider system is their rapid
>> shutdown. In the end the inspector comes around and realizes there is
>> little gain for an offgrid ground mounted array for fireman. You do have to
>> educate them and if they are insistent on being a bonehead, install the RS
>> for the inspection and then use the box for the next one or sell it.
>>
>> After almost 30 years offgrid the last thing I want is something that can
>> fault out the solar or worse when I am away. Networks can be the enemy at
>> times. Less is more offgrid in my opinion.
>>
>>
>> Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>> http://members.sti.net/offgridsolar/
>> e-mailoffgridsolar at sti.net
>> text 209 813 0060
>>
>> On Thu, 13 Feb 2020 13:07:53 -0500, Christopher Warfel
>> <cwarfel at entech-engineering.com> wrote:
>>> I got involved in a long discussion on Rapid Shutdown compliance for
>>> battery multimode, grid interconnect inverters that have a ground
>>> mounted array. At one point, ground mounted array was not supposed to
>>> be subject to Rapid Shutdown unless there were dc conductors on the
>>> building. NEC 2017 seems to say it is if conductors are 3' in or on
>>> buildings. The intent of Rapid Shutdown was supposed to protect fire
>>> fighters from exposure to high dc voltage when the array was on a roof.
>>> Every code cycle it morphs into something a little different. Has
>>> anyone had to confront this situation, and was this type of project
>>> subject to Rapid Shutdown? Thanks in advance for any clarity on this.
>>> Chris
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>>
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200213/9107943c/attachment.htm>
More information about the RE-Wrenches
mailing list