[RE-wrenches] More GFI tripping problems
Jerry Shafer
jerrysgarage01 at gmail.com
Tue Jan 21 10:19:02 EST 2020
William
Just so it is clear, the outback on the DC side GFI is .5 amp not a 1. amp
Jerry
On Tue, Jan 21, 2020, 6:41 AM William Miller <william at millersolar.com>
wrote:
> Colleagues:
>
>
>
> Not too long ago we finished a large off-grid residential power system
> installation. It has a three-stack Radian 8048A with three FM80s and about
> 3,000 AH of battery. The home has all the bells and whistles including VFD
> drive pool pumps and home automation.
>
>
>
> We have been experiencing some GFI tripping on various AC branch
> circuits. I checked the bonding scenario and it appears to be correct:
> One bond only at the AC Combiner output of the inverters.
>
>
>
> We have checked N-G voltages and they seem minimal. We did find some high
> THD when the generator is charging the batteries, as high as 19%. I am not
> sure if this is voltage or current waveform distortion but I ordered a
> Fluke power quality meter and will be testing again as soon as it arrives.
> An Outback engineer told me distortion of a generator AC waveform under
> charging loads is normal.
>
>
>
> Unlike the recent case reviewed on this forum--where a specific appliance
> seemed to be causing problems in the PV GFI circuit, I have no indication
> that one appliance is the culprit and the problem is on the AC side.
>
>
>
> As an aside, I have always been interested in the design of PV GFI
> technology. It seems counterintuitive to me to deliberately un-bond any
> ground-referenced system and run that bond through a breaker pole.
> Nonetheless, the PV GFI circuit has not opened in this scenario. This does
> not mean there is no ground fault current, it means there is not a ground
> fault current in excess of 1 amps.
>
>
>
> I have reviewed all of the recent and historic posts about GFI tripping
> and I don’t see anything that might help. I suspect we have plumbed the
> depths of Wrenches current knowledge on this subject, but I am laying out
> the scenario in case any part of this description elicits a recollection.
> When we get this figured out, I will report back.
>
>
>
> Sincerely,
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200121/2d928062/attachment.htm>
More information about the RE-Wrenches
mailing list