Not too long ago we finished a large off-grid residential power system
installation.  It has a three-stack Radian 8048A with three FM80s and about
3,000 AH of battery.  The home has all the bells and whistles including VFD
drive pool pumps and home automation.



We have been experiencing some GFI tripping on various AC branch circuits.
I checked the bonding scenario and it appears to be correct:  One bond only
at the AC Combiner output of the inverters.



We have checked N-G voltages and they seem minimal.  We did find some high
THD when the generator is charging the batteries, as high as 19%.  I am not
sure if this is voltage or current waveform distortion but I ordered a
Fluke power quality meter and will be testing again as soon as it arrives.
An Outback engineer told me distortion of a generator AC waveform under
charging loads is normal.



Unlike the recent case reviewed on this forum--where a specific appliance
seemed to be causing problems in the PV GFI circuit, I have no indication
that one appliance is the culprit and the problem is on the AC side.



As an aside, I have always been interested in the design of PV GFI
technology.  It seems counterintuitive to me to deliberately un-bond any
ground-referenced system and run that bond through a breaker pole.
Nonetheless, the PV GFI circuit has not opened in this scenario.  This does
not mean there is no ground fault current, it means there is not a ground
fault current in excess of 1 amps.



I have reviewed all of the recent and historic posts about GFI tripping and
I don’t see anything that might help.  I suspect we have plumbed the depths
of Wrenches current knowledge on this subject, but I am laying out the
scenario in case any part of this description elicits a recollection.  When
we get this figured out, I will report back.



Sincerely,



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200120/a9e21caf/attachment.htm>


More information about the RE-Wrenches mailing list