[RE-wrenches] Solar Ready Service Panel vs adding Supply Side connection?

Chris Schaefer chris at solarandwindfx.com
Wed Oct 23 19:14:42 EDT 2019


Jeff,
While this is a big thread but if I understand correctly, especially with
your last comment "combiner cost is to high". I use a fiberglass 14 x12
junction box with a hinged cover along with  a power distribution block.
Total cost is just a bit over $200 bucks. Attached is a picture. If you
want specific p/n contact me off list and I'd be happy to share.

Christopher

On Wed, Oct 23, 2019 at 6:04 PM Jeff Clearwater <
jeffc at villagepowerdesign.com> wrote:

> Hey William,
>
> That exact unit is actually where I started this journey but PG&E will not
> accept that Solarready residential unit because it’s a commercial account
> and anything over 200 A in a commercial account requires a CT cabinet. So
> to avoid CTs we need to separate out the 200 amp meter socket.
>
> I could feed that unit with 200 Amos after a 200 A Meter\Main but the
> combined cost would be high.
> Best,
>
> Jeff
>
> Sent from my iPhone
>
> On Oct 23, 2019, at 10:59 AM, William Miller <william at millersolar.com>
> wrote:
>
> Jeff:
>
>
>
> Would a class 320, solar-ready, meter/main combo be approved for this
> commercial application?  Here is a link
> <https://www.downloads.siemens.com/download-center/download?BTLV_44465>
> to a product we have used in residential applications.  It offers
> through-the-jaws metering at 400 amps peak, 320 amps continuous.
>
>
>
> William
>
>
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Jeff Clearwater
> *Sent:* Wednesday, October 23, 2019 9:11 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] SolarReady Service Panel vs adding Supply
> Side connection?
>
>
>
> Hey Jay,
>
> Yes so you were on to it - but with the addition of having that downstream
> of a separate 200 AMP meter box and 200 A Main that works :)  Otherwise
> PG&E would call it a 400 Amp service which for commercial accounts means
> having to have CTs for the metering.
>
> Thanks!,
>
> Jeff
>
> Jay wrote on 10/17/19 3:38 PM:
>
>
> What about installing a 200 amp breaker in the 400 amp buss box?
>
>
>
> We talk a lot about doing it for smaller boxes, is there a reason it won’t
> work here?
>
>
>
> Jay
>
> Peltz power
>
>
>
> On Oct 17, 2019, at 1:30 PM, Glenn Burt <Glenn.burt at glbcc.com>
> <Glenn.burt at glbcc.com> wrote:
>
> 
>
> Hi Jeff,
>
>
>
> Seems to me if allowed in your jurisdiction, you might be best served by
> installing a new 200A fused service disconnect ahead of the existing main
> service panel. Or even a 400A one to allow for additional work inside
> (CT’s), then perform a supply side connection in it. Some manufacturers of
> switchgear have an option for lugs that accept multiple conductors, so no
> piercing of conductors needs to happen.
>
>
>
> Good luck,
>
> Glenn
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org>
> <re-wrenches-bounces at lists.re-wrenches.org> *On Behalf Of *Jeff Clearwater
> *Sent:* Thursday, October 17, 2019 3:20 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> <re-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] SolarReady Service Panel vs adding Supply Side
> connection?
>
>
>
> Esteemed Wrenches,
>
> I am in need of changing out an existing 200 Amp service entrance in order
> to accommodate a bus capable of handling a a 200 Amp Solar backfeed (41 KW
> system) .
>
> PG&E is upgrading the transformer to handle the backfeed but when I
> proposed a Siemens SolarReady 400 Amp service entrance they couldn't
> approve it cause since the building is a shop - they classify it as
> commercial and require a panel that can handle CTs when there is a 400 Amp
> service involved.
>
> Anyone else faced with this have solutions?  What is the cheapest
> equipment I can provide to satisfy all requirements?
>
> We don't need to upgrade the existing 200 amp service entrance equipment
> for load purposes - only to meet the bus requirements of backfeed.
>
> Would it be cheaper and easier to use the existing (or new) 200 Amp
> residential panel - not call it a 400 Amp upgrade but simply add a 200 Amp
> Supply Side Connection?  Suggested equipment to do that in the most
> economical manner?
>
> Any help well appreciated!
>
> Jeff
>
>
>
>
>
>
>
>
> --
> ~~~~~~~~~~~
>
> Jeff Clearwater
> Village Power Design
> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
> www.villagepowerdesign.com
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
> _______________________________________________
>
> List sponsored by Redwood Alliance
>
>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
>
>
> Change listserver email address & settings:
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>
>
> List rules & etiquette:
>
> www.re-wrenches.org/etiquette.htm
>
>
>
> Check out or update participant bios:
>
> www.members.re-wrenches.org
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s
<http:www.solarandwindfx.com>

*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
<chris at solarandwindfx.com>*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191023/d608e829/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 20190115_125728.jpg
Type: image/jpeg
Size: 198651 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191023/d608e829/attachment.jpg>


More information about the RE-Wrenches mailing list