[RE-wrenches] SolarReady Service Panel vs adding Supply Side connection?
August Goers
august at luminalt.com
Wed Oct 23 10:35:49 EDT 2019
Replying on list, I had mistakenly only replied to Jeff off list. -August
On Wed, Oct 23, 2019 at 6:26 AM August Goers <august at luminalt.com> wrote:
> Hi Jeff - I think technically you can try a supply side connection per NEC
> 705.12(A) if you can find equipment with provisions to both feed your
> existing service and then the solar. Sometimes a splice box is required.
>
> Without knowing the configuration of the existing equipment, it's hard to
> understand if that will be easier overall compared to just going the route
> where you supply a 200 A rated meter socket (maybe you already have this?)
> and 200 A main breaker panel (with no loads) and then a 400 A bused panel
> to connect both your loads and the PV system.
>
> August
>
>
>
>
> On Mon, Oct 21, 2019 at 11:52 AM Jeff Clearwater <
> jeffc at villagepowerdesign.com> wrote:
>
>> Hey August, Jay, and Burt and all,
>>
>> Thanks for the great input! and I'm sorry if I wasn't clearer.
>>
>> They are not asking for 400 Amps - I suggested it as that was the rating
>> of the solar ready panel I specified.
>>
>> They are just saying IF it's 400 Amps then they need room for CTs cause
>> it's a shop and hence residential equipment is not approved.
>>
>> So as August and Glenn indicate below - perhaps the easiest is a 200 AMP
>> meter can with a Supply side line. That does throw it back to my AJH to
>> approve but that is pretty standardI would hope. It also requires the
>> variance letter from PG&E.
>>
>> I'm running 5 SB7.7s at 32 Amps each - so 160 AMPS of solar input.
>>
>> So If I supply a 200 A meter can with supply side lugs that I can feed
>> into a 200 A fused disconnect and solar distribution panel and keep the
>> existing 200 Amp panel box fed by the 200 Amp main breaker - any reason
>> that won't work?
>>
>> OR does anyone know of a commercial 400 AMP solar ready meter base with 2
>> 200 Amp feeds - one for solar and one for loads that does allow room for
>> CTs?
>>
>> Thanks,
>>
>> Jeff
>>
>> August Goers wrote on 10/17/19 4:35 PM:
>>
>> Hi Jeff -
>>
>> PG&E defines the service rating amperage based on the enclosure rating of
>> the first piece of equipment the service hits. See section 1.14 in the
>> Greenbook:
>>
>>
>> https://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/startstop/newconstruction/greenbook/servicerequirements/greenbook_manual_full.pdf
>>
>>
>> This might be why they insist that you need a 400 A service just because
>> you want a 400 A rated bus. The easy way around it is to supply a 200 A
>> rated meter socket and main disconnect, then feed a 400 A sub panel.
>>
>> A meter/main like the Eaton MBEB200BTS might also work for you:
>> https://www.homedepot.com/p/Eaton-200-Amp-BR-Type-Main-Breaker-Meter-Breaker-without-Distribution-EUSERC-MBEB200BTS/100555147
>>
>>
>> August
>> Luminalt
>>
>>
>> Hi Jeff,
>>
>>
>>
>> Seems to me if allowed in your jurisdiction, you might be best served by
>> installing a new 200A fused service disconnect ahead of the existing main
>> service panel. Or even a 400A one to allow for additional work inside
>> (CT’s), then perform a supply side connection in it. Some manufacturers of
>> switchgear have an option for lugs that accept multiple conductors, so no
>> piercing of conductors needs to happen.
>>
>>
>>
>> Good luck,
>> Glenn
>>
>> On Thu, Oct 17, 2019 at 12:19 PM Jeff Clearwater <
>> jeffc at villagepowerdesign.com> wrote:
>>
>>> Esteemed Wrenches,
>>>
>>> I am in need of changing out an existing 200 Amp service entrance in
>>> order to accommodate a bus capable of handling a a 200 Amp Solar backfeed
>>> (41 KW system) .
>>>
>>> PG&E is upgrading the transformer to handle the backfeed but when I
>>> proposed a Siemens SolarReady 400 Amp service entrance they couldn't
>>> approve it cause since the building is a shop - they classify it as
>>> commercial and require a panel that can handle CTs when there is a 400 Amp
>>> service involved.
>>>
>>> Anyone else faced with this have solutions? What is the cheapest
>>> equipment I can provide to satisfy all requirements?
>>>
>>> We don't need to upgrade the existing 200 amp service entrance equipment
>>> for load purposes - only to meet the bus requirements of backfeed.
>>>
>>> Would it be cheaper and easier to use the existing (or new) 200 Amp
>>> residential panel - not call it a 400 Amp upgrade but simply add a 200 Amp
>>> Supply Side Connection? Suggested equipment to do that in the most
>>> economical manner?
>>>
>>> Any help well appreciated!
>>>
>>> Jeff
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> --
>>> ~~~~~~~~~~~
>>> Jeff Clearwater
>>> Village Power Design
>>> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>>> www.villagepowerdesign.com
>>> cell - 413-559-9763
>>> ~~~~~~~~~~~~~~~~~~~~~~~
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette: