<div dir="ltr"><div>Replying on list, I had mistakenly only replied to Jeff off list. -August</div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Oct 23, 2019 at 6:26 AM August Goers <<a href="mailto:august@luminalt.com">august@luminalt.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr">Hi Jeff - I think technically you can try a supply side connection per NEC 705.12(A) if you can find equipment with provisions to both feed your existing service and then the solar. Sometimes a splice box is required. <div><br></div><div>Without knowing the configuration of the existing equipment, it's hard to understand if that will be easier overall compared to just going the route where you supply a 200 A rated meter socket (maybe you already have this?) and 200 A main breaker panel (with no loads) and then a 400 A bused panel to connect both your loads and the PV system. <div><br></div><div>August<div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr">
<p> </p></div></div></div></div></div><br></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Mon, Oct 21, 2019 at 11:52 AM Jeff Clearwater <<a href="mailto:jeffc@villagepowerdesign.com" target="_blank">jeffc@villagepowerdesign.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
<div style="color:rgb(0,0,0);background-color:rgb(255,255,255)" bgcolor="#FFFFFF"><span>Hey August, Jay, and
Burt and all,<br>
<br>
Thanks for the great input! and I'm sorry if I wasn't clearer.<br>
<br>
They are not asking for 400 Amps - I suggested it as that was the rating
of the solar ready panel I specified.<br>
<br>
They are just saying IF it's 400 Amps then they need room for CTs cause
it's a shop and hence residential equipment is not approved.<br>
<br>
So as August and Glenn indicate below - perhaps the easiest is a 200 AMP
meter can with a Supply side line. That does throw it back to my AJH
to approve but that is pretty standardI would hope. It also requires
the variance letter from PG&E.<br>
<br>
I'm running 5 SB7.7s at 32 Amps each - so 160 AMPS of solar input.<br>
<br>
So If I supply a 200 A meter can with supply side lugs that I can feed
into a 200 A fused disconnect and solar distribution panel and keep the
existing 200 Amp panel box fed by the 200 Amp main breaker - any reason
that won't work?<br>
<br>
OR does anyone know of a commercial 400 AMP solar ready meter base with 2
200 Amp feeds - one for solar and one for loads that does allow room
for CTs?<br>
<br>
Thanks,<br>
<br>
Jeff<br>
<br>
August Goers wrote on 10/17/19 4:35 PM:</span><br>
<br>
<blockquote type="cite">
<div dir="ltr">Hi Jeff - <div><br></div><div>PG&E defines the
service rating amperage based on the enclosure rating of the first piece
of equipment the service hits. See section 1.14 in the Greenbook:</div><div><br></div><div><a href="https://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/startstop/newconstruction/greenbook/servicerequirements/greenbook_manual_full.pdf" target="_blank">https://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/startstop/newconstruction/greenbook/servicerequirements/greenbook_manual_full.pdf</a> </div><div><br></div><div>This
might be why they insist that you need a 400 A service just because you
want a 400 A rated bus. The easy way around it is to supply a 200 A
rated meter socket and main disconnect, then feed a 400 A sub panel. </div><div><br></div><div>A
meter/main like the Eaton MBEB200BTS might also work for you:
<a href="https://www.homedepot.com/p/Eaton-200-Amp-BR-Type-Main-Breaker-Meter-Breaker-without-Distribution-EUSERC-MBEB200BTS/100555147" target="_blank">https://www.homedepot.com/p/Eaton-200-Amp-BR-Type-Main-Breaker-Meter-Breaker-without-Distribution-EUSERC-MBEB200BTS/100555147</a> </div><div><br></div><div>August </div><div>Luminalt<br><br></div></div>
<br></blockquote>
<blockquote type="cite"><p class="MsoNormal"><span style="color:windowtext">Hi Jeff,</span></p>
<p class="MsoNormal"><span style="color:windowtext"> </span></p>
<p class="MsoNormal"><span style="color:windowtext">Seems
to me if allowed in your jurisdiction, you might be best served by
installing a new 200A fused service disconnect ahead of the existing
main service panel. Or even a 400A one to allow for additional work
inside (CT\u2019s), then perform a supply side connection in it. Some
manufacturers of switchgear have an option for lugs that accept multiple
conductors, so no piercing of conductors needs to happen.</span></p>
<p class="MsoNormal"><span style="color:windowtext"> </span></p>
<p class="MsoNormal"><span style="color:windowtext">Good luck,</span></p>
<span style="color:windowtext">Glenn</span></blockquote>
<blockquote type="cite"><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Thu, Oct
17, 2019 at 12:19 PM Jeff Clearwater <<a href="mailto:jeffc@villagepowerdesign.com" target="_blank">jeffc@villagepowerdesign.com</a>>
wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div bgcolor="#FFFFFF"><span></span>Esteemed
Wrenches,<br>
<br>
I am in need of changing out an existing 200 Amp service entrance in
order to accommodate a bus capable of handling a a 200 Amp Solar
backfeed (41 KW system) . <br>
<br>
PG&E is upgrading the transformer to handle the backfeed but when I
proposed a Siemens SolarReady 400 Amp service entrance they couldn't
approve it cause since the building is a shop - they classify it as
commercial and require a panel that can handle CTs when there is a 400
Amp service involved.<br>
<br>
Anyone else faced with this have solutions? What is the cheapest
equipment I can provide to satisfy all requirements?<br>
<br>
We don't need to upgrade the existing 200 amp service entrance equipment
for load purposes - only to meet the bus requirements of backfeed.<br>
<br>
Would it be cheaper and easier to use the existing (or new) 200 Amp
residential panel - not call it a 400 Amp upgrade but simply add a 200
Amp Supply Side Connection? Suggested equipment to do that in the most
economical manner?<br>
<br>
Any help well appreciated!<br>
<br>
Jeff <br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<br>
<div>-- <br><span>~~~~~~~~~~~<br>
</span>
<div>
<span>Jeff Clearwater</span><span><span><br>
</span>Village Power Design<br>
</span><span><span><span><a href="https://www.linkedin.com/in/jeff-clearwater-0622a312/" target="_blank">linkedin</a>
</span></span></span><br>
<span><span><a href="http://www.villagepowerdesign.com" target="_blank">www.villagepowerdesign.com</a></span><br>
cell - <span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)">413-559-9763<br>
~~~~~~~~~~~~~~~~~~~~~~~</span></span></div>
<span><span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)"></span></span></div>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br></blockquote></div></blockquote>
<br>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
</blockquote></div></div>