What about installing a 200 amp breaker in the 400 amp buss box?
We talk a lot about doing it for smaller boxes, is there a reason it won’t work here?
Jay
Peltz power
> On Oct 17, 2019, at 1:30 PM, Glenn Burt <Glenn.burt at glbcc.com> wrote:
>
>
> Hi Jeff,
>
> Seems to me if allowed in your jurisdiction, you might be best served by installing a new 200A fused service disconnect ahead of the existing main service panel. Or even a 400A one to allow for additional work inside (CT’s), then perform a supply side connection in it. Some manufacturers of switchgear have an option for lugs that accept multiple conductors, so no piercing of conductors needs to happen.
>
> Good luck,
> Glenn
>
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Jeff Clearwater
> Sent: Thursday, October 17, 2019 3:20 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] SolarReady Service Panel vs adding Supply Side connection?
>
> Esteemed Wrenches,
>
> I am in need of changing out an existing 200 Amp service entrance in order to accommodate a bus capable of handling a a 200 Amp Solar backfeed (41 KW system) .
>
> PG&E is upgrading the transformer to handle the backfeed but when I proposed a Siemens SolarReady 400 Amp service entrance they couldn't approve it cause since the building is a shop - they classify it as commercial and require a panel that can handle CTs when there is a 400 Amp service involved.
>
> Anyone else faced with this have solutions? What is the cheapest equipment I can provide to satisfy all requirements?
>
> We don't need to upgrade the existing 200 amp service entrance equipment for load purposes - only to meet the bus requirements of backfeed.
>
> Would it be cheaper and easier to use the existing (or new) 200 Amp residential panel - not call it a 400 Amp upgrade but simply add a 200 Amp Supply Side Connection? Suggested equipment to do that in the most economical manner?
>
> Any help well appreciated!
>
> Jeff
>
>
>
>
>
>
>
>
> --
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin
> www.villagepowerdesign.com
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20191017/e0b76962/attachment.htm>
More information about the RE-Wrenches
mailing list