[RE-wrenches] Backfeed in PG&E territory
Jerry Shafer
jerrysgarage01 at gmail.com
Tue Aug 27 14:31:48 EDT 2019
Bill
The meter main is an UL approved product, any alterations may effect that
in the eyes of the inspector or PG&E. I have done a breakout panel where l
was exceeding the 20% rule but a 128 amp still may be an issue. The break
out panel is a connection where there are breakers all around to protect
all the connections. You need to confirm that PG&E will require a disco,
you might to eliminate a breaker though. The breakout panel is not always
approved either. Can you upgrade the panel with dual 200 amp outputs, one
goes to a breaker bus and the other just taps out. This would be less of a
liability issue l would think also. These panels do what you want and are
UL Approved.
Jerry
On Tue, Aug 27, 2019, 10:40 AM frenergy <frenergy at psln.com> wrote:
> Wrenches,
>
> Is the only a way to back feed 128 amps (240v, split PH)
> onto a 200 amp panel is to tap the conductors between the meter and the
> main CB, assuming I can pull it off in the "customer section" of the
> panel. Of course with the requisite AC disco within 10 feet. Or, has
> anybody ever gotten a written approval from a panel manu to thread a
> 1/4" hole in a bus between the meter and the main CB to install a lug
> for accepting a backfeed source?
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
>
> ---
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190827/cf192ec8/attachment.htm>
More information about the RE-Wrenches
mailing list