Typically a fused disconnect can only handle 80% of it's nominal current on
a continuous basis. Unfused disconnects are often 100% rated. For
example, see attached Square D bulletin #3110DB0401R0410.
So, a 100% rated (unfused) 30A disconnect (at least, from Square D) should
be fine here, as long as your OCPD is provided elsewhere (eg, the breaker
you mentioned).
NEC 690.8(B)(1)(Exception) explicitly allows a 100%-rated device to be used
without multiplying the inverter output current by 125%.
On Wed, Aug 21, 2019 at 3:22 PM Greg <greg at remotepowerinc.com> wrote:
> Fellow Wrenches, I'm having a discussion with a utility engineer
> regarding the following situation:
>
> Installing a 6kW inverter that has a full rated output of 25 amps. 80% of
> 30 is 24. That means to me I need to go up to a 40 amp breaker. I'm
> running #8 (continuous load 25 x 1.25 etc.)
> The engineer believes I should use a 60 amp disco since it's on a 40 amp
> breaker. My thinking is I can use a 30 amp disco since it can not produce
> more than 25 amps ever.
>
> Do any of you have a reference that shows what I'm doing is okay? Not
> okay?
>
> Thanks again,
> Greg Egan
> Remote Power Inc.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
*Blake Gleason, PE* | Employee-Owner |
*Director of Innovation & Technical Excellence*
510.845.2997 x128
Follow us on Facebook
<https://www.facebook.com/pages/Sun-Light-Power/119675658118322?ref=hl>,
LinkedIn <https://www.linkedin.com/company/sun-light-and-power> or our
website <https://sunlightandpower.com/>.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190821/2d64e41d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Square-D-Switch-PV-Bulletin_06-10_100percent_rated.pdf
Type: application/pdf
Size: 114256 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190821/2d64e41d/attachment.pdf>
More information about the RE-Wrenches
mailing list