[RE-wrenches] Soft Start Modules for Well and Sewage Pumps?
chris at OasisMontana.com
chris at OasisMontana.com
Fri Jul 26 12:27:34 EDT 2019
Here at the Oasis home/office, we have a Goulds 3 hp 240VAC soft start pump (#18GS30, w/ Franklin motor HS09970 and #3AS30 Aquavar Solo controller); it’s been running off of my 2011 Radian GS8048 since 2016, when I had to drill a new well (the water table is dropping) and pump from about 300 ft. depth. I have 3500 ft. of drip irrigation, a big garden and the usual domestic water loads. It’s worked flawlessly since its inception, and I cannot speak more highly of Goulds pumps. My first one lasted 23 years (it was a 1.5HP model).
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
<http://www.oasismontana.com> www.oasismontana.com
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Dana
Sent: Friday, July 26, 2019 9:34 AM
To: 'Jeff Clearwater' <jeffc at villagepowerdesign.com>; 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Soft Start Modules for Well and Sewage Pumps?
Yes I have used soft starts offgrid with SW & VFX for 15+ years, in spite of doing load evaluations & others installing what ever they normally used. It has been a great rescue device. Well pump, 2 dish washers, booster pump, etc.
Dana Orzel Great Solar Works, Inc.
C - 208.721.7003 dana at solarwork.com <mailto:dana at solarwork.com>
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136 www.solarwork.com <http://www.solarwork.com>
"Responsible Technologies for Responsible People since 1988"
P Please consider the environment before printing this email.
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org> > On Behalf Of Jeff Clearwater
Sent: Friday, July 26, 2019 8:04 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org> >
Subject: [RE-wrenches] Soft Start Modules for Well and Sewage Pumps?
Hey Wrenches,
Anyone have success using soft-start modules on well and sewage pumps to lower the surge for off-grid inverters?
The baby we are trying to tame is a 2 HP 15 amp, 53 LRA Omnivore Grinder Pump - LSG200 series - single phase 230 Vac.
Thanks!
Jeff
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
Jeff Clearwater wrote on 7/26/19 6:32 AM:
Thanks Ray and Jerry,
Great to hear from you both with your years of combined experience :)
So yes looking at the 5 sec has me switching back to a trusty Radian - even then from what you are saying it may not work.
And you are right Ray - Outback is careful to rate the "overload capability" in KVA rather than KW due most likely to voltage sag of course.
So this 53 LRA 2 HP motor - if I can only trust the 5 second (50 A) might not start - especially with other loads on the system?
RADIAN SURGE RATINGS:
Maximum Output Current
1 ms peak 100 Amps AC at 240 VAC, 200 Amps AC at 120 VAC
100 ms RMS 70.7 Amps AC at 240 VAC
Overload Capability
100 ms surge 16.97 kVa
5 seconds 12 kVa
30 minute 9 kVa
Other's experience with 2 HP sewage pump or well pump motors on a Radian?
Thanks!
Jeff
Ray wrote on 7/25/19 5:48 PM:
I only look at the 5 sec and 30 sec surge ratings to get an idea what an inverter can really do in the real world. All those millisecond ratings/ in rush current specs won't get a pump or motor started, and will basically just get you into trouble. The reason they have those ratings in amps and not watts, is that the voltage craters during that 100mS surge.
I can't tell you how many times we tried to start a pump, compressor, or large table saw, and the inverter just shut off, even though the "in rush current" was within the theoretical inverter capacity. Actual Wrench list testimonials are much more valuable than those arcane specs.
Ray Walters
Remote Solar
303 505-8760
On 7/25/19 5:15 PM, Jeff Clearwater wrote:
Hey There Wrenches,
So be advised that after a little research the SW dual stack will NOT double the surge ratings of a single SW.
But that brings me to my second question:
What inverter surge rating should one refer to when looking at maximum Inrush or LRA - 1ms? 100ms? 1 sec?
Your engineering wisdom welcomed!
Thanks,
Jeff
Jeff Clearwater wrote on 7/23/19 8:27 PM:
Thanks for the tip! I'll check the firmware.
Dave Angelini Offgrid Solar wrote on 7/22/19 9:11 AM:
Hi Jeff,
I am not going to guess if this will work, it should. I use XW's because they start anything I have come across.
If you do this, make sure but SW's have the latest and same firmware. There were problems with stacked SW's early on in their development.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net <mailto:offgridsolar at sti.net>
text 209 813 0060
On Mon, 22 Jul 2019 07:26:07 -0700, Jeff Clearwater <mailto:jeffc at villagepowerdesign.com> <jeffc at villagepowerdesign.com> wrote:
Hey Esteemed Wrenches,
So I recently built a power trailer with a single 4 KW (4048) Schneider SW for a client with a moderate cabin lifestyle.
But he lives on a high hill and even though his 2 HP Macerator is only rated at 15 amps continuous that baby starts up with a whopping kick - probably close to or at it's 53 Amps Locked Rotor rating.
The SW has the following surge capability:
SW 4048 Rated @ 240 Volts:
Continuous - 15.2 Amps 3700 Watts
30 Minutes - 18.3 Amps 4400 Watts
5 Secs - 29.2 Amps 7000 Watts
Max (100ms?) - 41 Amps - 9840 Watts
Can I be confidant that 2 stacked SWs will start this baby?
Any experience with similar macerators - or simply educated guesses?
Thanks!
Jeff
--
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net <mailto:offgridsolar at sti.net>
text 209 813 0060
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190726/4de93d08/attachment.htm>
More information about the RE-Wrenches
mailing list