[RE-wrenches] 100ms for Locked Rotor Amps?
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Fri Jul 26 09:20:05 EDT 2019
The CSW is for a small cabin. Anyone living offgrid with normal loads
should use an XW and they will not have to deal with any of this. It has
been that way since 2006.
On Thu, 25 Jul 2019 22:17:13 -0700, Jerry
Shafer wrote: Wrenches Some time back, (years) l did a off grid system
for a customer that was building his home, he was milli g lumber from the
home site, l quoted a Outback PS-4 3648, the customer already had a very
large battery bank 2000 amp hrs. at 48 DC nominal. Anyway he had a well on
a 5 hp. freq drive and a very big tall 6" bandsaw, trace/Schneider said no
way could there stack do the job and it was larger. Outback on the other
had said no problem and for years after that PS-4 ran the well, the saws
and now the finished home. It is interesting that Schneider was not willing
to do what Outback could, they must have something in there root
programming preventing the stacked surge. Some like Chevrolet, some like
Ford, l have done rows of Radians and lm sure some out there have the same
with other manufacturers. It's all good data for all of us. Jerry
On
Thu, Jul 25, 2019, 4:15 PM Jeff Clearwater wrote: Hey There Wrenches,
So be advised that after a little research the SW dual stack will NOT
double the surge ratings of a single SW.
But that brings me to my second
question:
What inverter surge rating should one refer to when looking at
maximum Inrush or LRA - 1ms? 100ms? 1 sec?
Your engineering wisdom
welcomed!
Thanks,
Jeff
Jeff Clearwater wrote on 7/23/19 8:27 PM:
Thanks for the tip! I'll check the firmware.
Dave Angelini Offgrid Solar
wrote on 7/22/19 9:11 AM:
Hi Jeff,
I am not going to guess if this will
work, it should. I use XW's because they start anything I have come across.
If you do this, make sure but SW's have the latest and same firmware.
There were problems with stacked SW's early on in their development.
Dave
Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [2]
e-mail offgridsolar at sti.net
[3]
text 209 813 0060
On Mon, 22 Jul 2019 07:26:07 -0700, Jeff Clearwater
[4] wrote: Hey Esteemed Wrenches,
So I recently built a power trailer
with a single 4 KW (4048) Schneider SW for a client with a moderate cabin
lifestyle.
But he lives on a high hill and even though his 2 HP Macerator
is only rated at 15 amps continuous that baby starts up with a whopping
kick - probably close to or at it's 53 Amps Locked Rotor rating.
The SW
has the following surge capability:
SW 4048 Rated @ 240 Volts:
Continuous - 15.2 Amps 3700 Watts
30 Minutes - 18.3 Amps 4400 Watts
5
Secs - 29.2 Amps 7000 Watts
Max (100ms?) - 41 Amps - 9840 Watts
Can I be
confidant that 2 stacked SWs will start this baby?
Any experience with
similar macerators - or simply educated guesses?
Thanks!
Jeff
--
Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [5]
e-mail offgridsolar at sti.net
[6]
text 209 813 0060
_______________________________________________
List
sponsored by Redwood Alliance
List Address:
RE-wrenches at lists.re-wrenches.org [7]
Change listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[8]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[9]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [10]
Check
out or update participant bios:
www.members.re-wrenches.org [11]
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [12]
Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [13]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[14]
List rules ">Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [17]
e-mail
offgridsolar at sti.net [18]
text 209 813 0060
Links:
------
[1]
mailto:jeffc at villagepowerdesign.com
[2]
http://members.sti.net/offgridsolar/
[3] mailto:offgridsolar at sti.net
[4]
mailto:jeffc at villagepowerdesign.com
[5]
http://members.sti.net/offgridsolar/
[6] mailto:offgridsolar at sti.net
[7]
mailto:RE-wrenches at lists.re-wrenches.org
[8]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[9]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[10]
http://www.re-wrenches.org/etiquette.htm
[11]
http://www.members.re-wrenches.org
[12]
mailto:RE-wrenches at lists.re-wrenches.org
[13]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[14]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[15]
http://www.re-wrenches.org/etiquette.htm
[16]
http://www.members.re-wrenches.org
[17]
http://members.sti.net/offgridsolar/
[18] mailto:offgridsolar at sti.net
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190726/bd3d9476/attachment.htm>
More information about the RE-Wrenches
mailing list