[RE-wrenches] Soft Start Modules for Well and Sewage Pumps?

Jeff Clearwater jeffc at villagepowerdesign.com
Fri Jul 26 10:03:32 EDT 2019


Hey Wrenches,

Anyone have success using soft-start modules on well and sewage pumps to 
lower the surge for off-grid inverters?

The baby we are trying to tame is a 2 HP 15 amp, 53 LRA Omnivore Grinder 
Pump - LSG200 series - single phase 230 Vac.

Thanks!

Jeff


~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~

Jeff Clearwater wrote on 7/26/19 6:32 AM:

> Thanks Ray and Jerry,
>
> Great to hear from you both with your years of combined experience :)
>
> So yes looking at the 5 sec has me switching back to a trusty Radian - 
> even then from what you are saying it may not work.
>
> And you are right Ray -  Outback is careful to rate the "overload 
> capability" in KVA rather than KW due most likely to voltage sag of 
> course.
>
> So this 53 LRA 2 HP motor - if I can only trust the 5 second (50 A) 
> might not start - especially with other loads on the system?
>
> RADIAN SURGE RATINGS:
>
> Maximum Output Current
> 1 ms peak 100 Amps AC at 240 VAC, 200 Amps AC at 120 VAC
> 100 ms RMS 70.7 Amps AC at 240 VAC
>
> Overload Capability
> 100 ms surge 16.97 kVa
> 5 seconds 12 kVa
> 30 minute 9 kVa
>
> Other's experience with 2 HP sewage pump or well pump motors on a Radian?
>
> Thanks!
>
> Jeff
>
>
> Ray wrote on 7/25/19 5:48 PM:
>
>> I only look at the 5 sec and 30 sec surge ratings to get an idea what 
>> an inverter can really do in the real world.  All those millisecond 
>> ratings/ in rush current specs won't get a pump or motor started, and 
>> will basically just get you into trouble.  The reason they have those 
>> ratings in amps and not watts, is that the voltage craters during 
>> that 100mS surge.
>>
>> I can't tell you how many times we tried to start a pump, compressor, 
>> or large table saw, and the inverter just shut off, even though the 
>> "in rush current" was within the theoretical inverter capacity.  
>> Actual Wrench list testimonials are much more valuable than those 
>> arcane specs.
>>
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>> On 7/25/19 5:15 PM, Jeff Clearwater wrote:
>>> Hey There Wrenches,
>>>
>>> So be advised that after a little research the SW dual stack will 
>>> NOT double the surge ratings of a single SW.
>>>
>>> But that brings me to my second question:
>>>
>>> What inverter surge rating should one refer to when looking at 
>>> maximum Inrush or LRA - 1ms?  100ms?  1 sec?
>>>
>>> Yourengineering wisdom welcomed!
>>>
>>> Thanks,
>>>
>>> Jeff
>>>
>>>
>>>
>>> Jeff Clearwater wrote on 7/23/19 8:27 PM:
>>>
>>>> Thanks for the tip!  I'll check the firmware.
>>>>
>>>> Dave Angelini Offgrid Solar wrote on 7/22/19 9:11 AM:
>>>>
>>>>> Hi Jeff,
>>>>>
>>>>> I am not going to guess if this will work, it should.  I use XW's 
>>>>> because they start anything I have come across.
>>>>>
>>>>> If you do this, make sure but SW's have the latest and same 
>>>>> firmware. There were problems with stacked SW's early on in their 
>>>>> development.
>>>>>
>>>>> *Dave Angelini Offgrid Solar "we go where powerlines don't" 
>>>>> http://members.sti.net/offgridsolar/ e-mail offgridsolar at sti.net 
>>>>> <mailto:offgridsolar at sti.net> text 209 813 0060*
>>>>>
>>>>> On Mon, 22 Jul 2019 07:26:07 -0700, Jeff Clearwater 
>>>>> <jeffc at villagepowerdesign.com> wrote:
>>>>>
>>>>>> Hey Esteemed Wrenches,
>>>>>>
>>>>>> So I recently built a power trailer with a single 4 KW (4048) 
>>>>>> Schneider SW for a client with a moderate cabin lifestyle.
>>>>>>
>>>>>> But he lives on a high hill and even though his 2 HP Macerator is 
>>>>>> only rated at 15 amps continuous that baby starts up with a 
>>>>>> whopping kick - probably close to or at it's 53 Amps Locked Rotor 
>>>>>> rating.
>>>>>>
>>>>>> The SW has the following surge capability:
>>>>>>
>>>>>> SW 4048 Rated@ 240 Volts:
>>>>>> Continuous - 15.2 Amps 3700 Watts
>>>>>> 30 Minutes - 18.3 Amps 4400 Watts
>>>>>> 5 Secs - 29.2 Amps 7000 Watts
>>>>>> Max (100ms?) - 41 Amps - 9840 Watts
>>>>>>
>>>>>> Can I be confidant that 2 stacked SWs will start this baby?
>>>>>>
>>>>>> Any experience with similar macerators - or simply educated guesses?
>>>>>>
>>>>>> Thanks!
>>>>>>
>>>>>> Jeff
>>>>>>
>>>>> -- 
>>>>>   
>>>>> *Dave Angelini Offgrid Solar "we go where powerlines don't" 
>>>>> http://members.sti.net/offgridsolar/ e-mail offgridsolar at sti.net 
>>>>> <mailto:offgridsolar at sti.net> text 209 813 0060*
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>


-- 
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
-------------- next part --------------