[RE-wrenches] need for outdoor DC disconnect
Kirk Herander
vtsolar at icloud.com
Wed Jun 12 17:34:49 EDT 2019
I am not required to meet 2017 code. In Florida, they are only up to the
2011 code. I want to bring it up to NEC2017 regardless. So for my questions,
assume the 2017 code is relevant. And it is a flat carport roof, the rack is
mounted at a fixed tilt of about 20 degrees. Understood?
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of
Ray
Sent: Wednesday, June 12, 2019 4:24 PM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] need for outdoor DC disconnect
Are you required to meet the latest code? In many retrofit/ replacement
situations, you are only required to meet the code requirements of the date
the original system was installed. Metal vs PVC is dependent on the code
version you are meeting. Was metal a NEC 2008 requirement? I don't have my
old code versions here. When metal is required, its only from the point of
entry into the building to the inverter, so if you mount the inverter
outdoors, it doesn't have to change either. I've got lots of legacy systems
that have PVC on the inside, and never had an issue. Seems like more
trouble to change out than its worth, but if the AHJ requires it, then yes.
Also, you didn't mention if the array was roof or ground mounted, which
would effect the 690.12 interpretation.
Ray Walters
Remote Solar
303 505-8760
On 6/12/19 12:49 PM, Kirk Herander wrote:
All,
I am retrofitting an existing PV system with Storedge / LG Chem / optimizers
and updating some code issues. I am replacing the PVC conduit carrying the
array conductors into the building with metallic raceway to the point of DC
disconnect(i.e. the inverter). The array is presently connected to an
Outback inverter / FM60 controller / AGM batteries (grid tied with backup).
If I am interpreting NEC 690.12 etc. correctly, a DC disconnect outdoors is
generally not required because of new rapid shutdown capability, amongst
other reasons. Would this be the case regardless of metal or plastic conduit
penetrating the building? The system at present has no outdoor DC disco, and
to me that's a violation in addition to lack of metallic raceway entering
the building. Thanks.
Kirk Herander
Owner|Principal, VT Solar, LLC
Celebrating our 28th Anniversary 1991-2019
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com
&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aa
aaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B
%2BqtvcALkdDghvk4%3D&reserved=0> www.vermontsolarnow.com
dba Vermont Solar Engineering
NABCEPTM 2003 Inaugural Certificant
VT RE Incentive Program Partner
802.863.1202
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190612/940561f2/attachment.htm>
More information about the RE-Wrenches
mailing list