I still recommend using a relay triggered from the Aux for AC coupling, it
works reliably and quickly.

Brad
AEE Solar

On Wed, Jun 5, 2019 at 10:11 AM Kienan Maxfield <maxfieldsolar at hotmail.com>
wrote:

> Jay,
>
> It waits 50 seconds to even start to try to shift the frequency. I don’t
> know how long it takes to get up to get to 64 HZ. I heard somebody say that
> they thought that the 50 second delay should be adjustable, but I could not
> find a way to adjust it. I have not had a chance to talk to Schneider
> tech-support about it since then.
>
> I had a problem with this on a job, by the time the Schneider would change
> its frequency, the voltage would be way over an acceptable voltage. I had
> to adjust the voltage setpoint down in order to try to shorten the delay.
> That was not really a good workaround because how quickly the voltage rises
> depends on the charge rate.
>
> I know that all of the delays and ramp up speeds and ramp down speeds are
> fully user adjustable on outback equipment, I hope that Schneider has added
> this adjustability by now... but last time I checked, I don’t think you
> could.
>
> Thanks,
> Kienan
>
>
>
> > On Jun 5, 2019, at 10:46 AM, jay <jay.peltz at gmail.com> wrote:
> >
> >
> > HI All,
> >
> > I’ve got a project using lithium batteries and a big hydro.
> >
> > 4kw hydro
> > 6.8kw schneider
> > off grid
> > AC coupled hydro
> >
> > The plan is to use a combination of ways to keep from overcharging the
> batteries.
> >
> > 1. PWM diversion control load. If this doesn’t keep up then we go to #2
> > 2. AC couple HZ control and if that fails we go to #3
> > 3. SS relay control on GT inverter output via inverter control
> >
> >
> > My question is this:  Does anyone know the time between when the XW+
> sees the voltage and then gets to the 64hz for regulation?
> >
> > thanks
> >
> > jay
> >
> > peltz power
> >
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190605/408f5cbc/attachment.htm>


More information about the RE-Wrenches mailing list