[RE-wrenches] Schneider ac coupling time.
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Wed Jun 5 14:28:08 EDT 2019
Jay,
XW+ and XWpro have so many adjustments for AC coupling that I wish they
would just make an offgrid firmware version that would get rid of all the
grid requirements. I tested this on XW pro and it took about 8 seconds.
However, as Kienan remarked it would also depend on charge rate from both
solar and/or grid/gen. It also would depend on the capacity/Soc of the
bank. I used a 400AH 48v bank.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
On Wed, 5 Jun 2019 17:11:24 +0000, Kienan Maxfield
<maxfieldsolar at hotmail.com> wrote:
> Jay,
>
> It waits 50 seconds to even start to try to shift the frequency. I don’t
> know how long it takes to get up to get to 64 HZ. I heard somebody say
that
> they thought that the 50 second delay should be adjustable, but I could
not
> find a way to adjust it. I have not had a chance to talk to Schneider
> tech-support about it since then.
>
> I had a problem with this on a job, by the time the Schneider would
change
> its frequency, the voltage would be way over an acceptable voltage. I
had
> to adjust the voltage setpoint down in order to try to shorten the
delay.
> That was not really a good workaround because how quickly the voltage
rises
> depends on the charge rate.
>
> I know that all of the delays and ramp up speeds and ramp down speeds
are
> fully user adjustable on outback equipment, I hope that Schneider has
added
> this adjustability by now... but last time I checked, I don’t think you
> could.
>
> Thanks,
> Kienan
>
>
>
>> On Jun 5, 2019, at 10:46 AM, jay <jay.peltz at gmail.com> wrote:
>>
>>
>> HI All,
>>
>> I’ve got a project using lithium batteries and a big hydro.
>>
>> 4kw hydro
>> 6.8kw schneider
>> off grid
>> AC coupled hydro
>>
>> The plan is to use a combination of ways to keep from overcharging the
>> batteries.
>>
>> 1. PWM diversion control load. If this doesn’t keep up then we go to #2
>> 2. AC couple HZ control and if that fails we go to #3
>> 3. SS relay control on GT inverter output via inverter control
>>
>>
>> My question is this: Does anyone know the time between when the XW+
>> sees the voltage and then gets to the 64hz for regulation?
>>
>> thanks
>>
>> jay
>>
>> peltz power
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>>
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
>
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
--
More information about the RE-Wrenches
mailing list