[RE-wrenches] Aquion - Mix and Matching Layers
Tom Duffy
Tom at solar-biz.com
Fri May 10 13:06:08 EDT 2019
Hi All
We have had similar disasters with the Aquions going bad… same problems, some installers have loosened the nut with ruinous results but, bad trays in the stack are common as well.
Kind regards
Tom Duffy
Senior Solar Design Engineer
[TSBLOGODPIx500x200]
tom at solar-biz.com<mailto:tom at solar-biz.com>
MAIN TOLL FREE: 888-826-0939
DIRECT: 888-503-6772
International: 001-575-539-2111
PANAMA: 507-836-5588 X 122
FAX: 520-844-8442
www.thesolarbiz.com
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Bradley Bassett
Sent: Thursday, May 9, 2019 2:36 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Aquion - Mix and Matching Layers
As Aquion said, loosening the main nut will destroy the battery. I can vouch for that as well, not my doing, but I could not recover the batteries where that had been done. I tightened the nuts and got just about one cycle before they were gone.
I suspect that the temperature cycling of the batteries enhanced creep of the case and active materials to the point where there was no longer adequate compression, and so they are failing. It could be that if they had mfg them with steel cases and permanent layer level compression they might have been longer lived.
One thing about being able to take the layers apart is that they are much easier to move around that way. Each layer is only about 30 lbs. Then you can find creative uses for the aluminum bases and high strength threaded rod from them.
If you need an MSDS to show to the disposal site, contact me at AEE Solar. At our Hazo House locally here, they took a brief look at the MSDS and said, sure bring them in, no problem. Worth a try.
Brad
On Thu, May 9, 2019 at 10:38 AM Glenn Burt <Glenn.burt at glbcc.com<mailto:Glenn.burt at glbcc.com>> wrote:
We got such a black eye from the Aquions we installed that we had to replace entire banks to regain customer confidence and prevent bad word of mouth talk about the company.
They were a big loss both to our reputation and financial health.
I recommend discussing the issues and replacing the entire bank.
Sent from my Verizon LG Smartphone
------ Original message------
From: Lou Russo
Date: Thu, May 9, 2019 11:53 AM
To: RE-wrenches;
Cc:
Subject:[RE-wrenches] Aquion - Mix and Matching Layers
Wrenches,
I am getting more and more call about orphaned Aquion systems that have gone bad. Many of the systems have one or two "layers" that have gone bad. Voltage spikes up to the 14-15V range while charging and cratering to zero if even the tiniest load is put on it (e.g. turning on a charge controller, like I said...tiny). So I do not believe charging that particular "layer" with 6V charger would fix the problem.
Has anybody out there swapped out a bad "layer" with a good one and reassembled the stack? Is it even possible?
As always thanks for the help.
Aloha,
Lou Russo
lou at spreesolarsystems.com<mailto:lou at spreesolarsystems.com>
808 345 6762<tel:808%20345%0D%20%206762>
Spree Solar Systems LLC
CT-34322
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190510/dde86d46/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6229 bytes
Desc: image001.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190510/dde86d46/attachment.jpg>
More information about the RE-Wrenches
mailing list