Thanks for all of the comments.  My big question is *do these batteries
operate at lower voltages than a standard lead battery*.  From what I'm
gathering from this list, they do not.  I am fairly certain its a battery
problem, in fact, I think that there may be a bad cell as Alan suggests.

As far as Flexnet DC calibration, I do think this system is calibrated.  We
get to charge voltage and end amps daily and it corresponds to 100% SOC.
The solar keeps up with load easily esp with this generator run-time.  We
are making about 130% of what is being used.

The AGS start is done the "standard" way through the Aux relay on the
master, not via FNDC relay.  I haven't used that relay because calibration
issues are so prevalent.

I think its back to the basics with cell testing.

All of the comments are very much appreciated.



On Fri, Apr 19, 2019 at 9:49 PM Darryl Thayer <darylsolar1 at gmail.com> wrote:

> Jay has a real strong point.  If you are near low voltage low state of
> charge. Two or 4 hrs from a 4kw array is only 8 to 16 kwh nowhere near 46
> kwh.  Given the recomended max charge rate is C/5 you would have to be
> charging for days
>
> On Fri, Apr 19, 2019, 10:20 PM John Blittersdorf <
> john.blittersdorf at gmail.com> wrote:
>
>> Mac,
>>    If there is a TriMetric or charge controllers, you can get min/max
>> voltages each day or since last reset.   I have found that is very useful
>> info when large, short duration loads hit.  ie well pump.  I would find on
>> one of my 24 v systems that an 18 or 19 v min would indicate that the well
>> pump went on when the batteries were quite low and pulled the voltage down
>> to low battery cutoff.  If the system does not shut down, you might see a
>> voltage lower than the 2 minute setpoint.  I think the FlexNet DC also
>> records minimum voltage.  And be sure that the gen start trigger is not the
>> flexnet as that is big trouble.
>>
>> John Blittersdorf.
>>
>> On Fri, Apr 19, 2019 at 8:06 PM Glenn Burt <glenn.burt at glbcc.com> wrote:
>>
>>> Hi Larry,
>>>
>>>
>>>
>>> I am curious why you would use the 100Hr rate for this approximation and
>>> not the 20 or 24Hr one, since that is the period in which Mac is reporting
>>> the anomaly. Happy to learn the details!
>>>
>>>
>>>
>>> Thanks,
>>>
>>> Glenn
>>>
>>>
>>>
>>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
>>> Behalf Of *Starlight Solar Power Systems
>>> *Sent:* Friday, April 19, 2019 3:10 PM
>>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>>> *Subject:* Re: [RE-wrenches] Operating Voltages Outback RE High
>>> Capacity Battery
>>>
>>>
>>>
>>> Mac,
>>>
>>>
>>>
>>> Only removing 6kWh from 46kWh of storage should not be able to produce
>>> the voltage sag to trigger AGS. That’s only about 13% at a 100Hr rate.
>>> Voltage should be no where near that point. Have you verified actual
>>> voltage when the AGS is triggered? Loose wiring or terminal corrosion can
>>> cause voltage drop but I would think that an easy find/repair you would
>>> have checked.
>>>
>>>
>>>
>>> Saying the battery easily charges to 100% worries me as sulfated
>>> batteries do that. Healthy LA batteries take many hours to reach full
>>> saturation. Has cell voltage been compared for non-uniformity? Has the
>>> equalization charge been performed?
>>>
>>>
>>>
>>> I am not a fan of the unusual low voltages that Outback prescribes for
>>> EnergyCells and seriously wonder how these voltages can properly maintain
>>> these cells. CV is below the point where balanced O2 and H2 evolution takes
>>> place. But, thats off point.
>>>
>>>
>>>
>>>
>>> Larry Crutcher
>>> Starlight Solar Power Systems
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> On Apr 19, 2019, at 10:27 AM, Mac Lewis <maclewis1 at gmail.com> wrote:
>>>
>>>
>>>
>>> Hello Wrenches,
>>>
>>>
>>>
>>> We recently inherited an Outback system that I've been keeping an eye on
>>> via Optics.  Its a dual stack 3648 VFXR, with about 4kW of PV with a single
>>> string of EnergyCell 1100RE battery bank (reported to be ~6 months old)
>>> ~.46 kWh at C20.
>>>
>>>
>>>
>>> I have been observing how the system functions and how the voltage
>>> behaves.  We keep getting 2 minute voltage starts on the generator in the
>>> middle of the night that don't seem necessary judging from how much energy
>>> has been used from the battery bank.  I am hesitant to tweak anything
>>> because these battery set-points are a bit different than I'm used to.
>>>
>>>
>>>
>>> As per Outback:
>>>
>>> Absorb Voltage is 55.6V for 2 hours
>>>
>>> Float Voltage is 54.0V
>>>
>>>
>>>
>>> I've slowly been dropping the 2 minute start voltage to see if there is
>>> a bottom, but I'm hesitant to take it much lower (maybe I should).
>>>
>>> 2 minute start voltage: 44.8 V.
>>>
>>>
>>>
>>>
>>>
>>> The system easily charges the battery bank to 100% (and easily reached
>>> the 2 hr absorb time) every day.  The flexnet DC is correctly set up and
>>> calibrated.
>>>
>>>
>>>
>>> The load on the system is pretty consistent.  They use between 400 and
>>> 600W throughout the night.
>>>
>>>
>>>
>>> An average night, they may use about 6 kWh before the voltage sags below
>>> the 2 minute start voltage and it starts the generator.
>>>
>>>
>>>
>>> Just curious if our 2 minute voltage needs to be dropped or if these
>>> batteries are degraded.  What corrective changes can I make to get better
>>> performance?
>>>
>>>
>>>
>>> I have and will call Outback about this, but I'd like other perspectives
>>> as well.
>>>
>>>
>>>
>>> Thanks as always for your expertise
>>>
>>>
>>>
>>> --
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> Mac Lewis
>>>
>>>
>>> "Yo solo sé que no sé nada." *-Sócrates*
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190420/b991d658/attachment.htm>


More information about the RE-Wrenches mailing list