Drake
I have performed test for manufactures and you must keep the test voltage
under the max rated voltage of the module, we have a bunch of tests we do
but in short, you need to see the modules up close, look at the edges and
back sheets look for green, brown or black spots, you need to do testing
both dry first then wet if it is a ground fault concern. Most of the time
the visual will find the issues but you still want to verify what you think
you see. Make sure you look at the wiring to and from, the combiner box(s)
or even the inverter(s).
On Wed, Apr 10, 2019 at 8:31 AM Drake <drake.chamberlin at redwoodalliance.org>
wrote:
> Hello Wrenches,
>
> We are troubleshooting an array of Orion modules, either 230s or 250s. The
> array is showing a ground fault.
>
> We would like to test these modules with an insulation tester?
>
> We would like to apply 500 V or 1000 V to each the + and – and test
> resistance to ground.
>
> Is this practice safe for individual PV modules? Is there anything I
> should be aware of before attempting this?
>
> Thanks,
>
> Drake
>
> Drake Chamberlin
>
>
>
>
>
> *Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified
> Solar PV 740-448-7328 *http://athens-electric.com/
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190410/2b727f34/attachment.htm>
More information about the RE-Wrenches
mailing list