<div dir="ltr"><div>Drake</div><div>I have performed test for manufactures and you must keep the test voltage under the max rated voltage of the module, we have a bunch of tests we do but in short, you need to see the modules up close, look at the edges and back sheets look for green, brown or black spots, you need to do testing both dry first then wet if it is a ground fault concern. Most of the time the visual will find the issues but you still want to verify what you think you see. Make sure you look at the wiring to and from, the combiner box(s) or even the inverter(s).<br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Apr 10, 2019 at 8:31 AM Drake &lt;<a href="mailto:drake.chamberlin@redwoodalliance.org">drake.chamberlin@redwoodalliance.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
<div>
Hello Wrenches, <br><br>
We are troubleshooting an array of Orion modules, either 230s or 250s.
The array is showing a ground fault. <br><br>
We would like to test these modules with an insulation tester? <br><br>
We would like to apply 500 V or 1000 V to each the + and \u2013 and test
resistance to ground. <br>
 <br>
Is this practice safe for individual PV modules? Is there anything I
should be aware of before attempting this?<br><br>
Thanks,<br><br>
Drake<br><br>
<a name="m_5862061877422196794__MailAutoSig"></a>Drake Chamberlin<br>
<i>Athens Electric LLC<br>
OH License 44810<br>
CO License 3773<br>
NABCEP Certified Solar PV <br>
740-448-7328<br>
</i><a href="http://athens-electric.com/" target="_blank">http://athens-electric.com/</a>
<br><br>
<br>
</div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>