[RE-wrenches] Schneider SW 4048 error

Mac Lewis maclewis1 at gmail.com
Thu Feb 28 18:54:23 EST 2019


Hi Laura,

First thing I would try is to update the firmware.  Eeprom is a type of
memory so maybe you have a bad board but I have remedied this error with a
firmware update.

Here is what works with Schneider tech support last I checked:
(833)391-8640 option 8

Good luck

On Thu, Feb 28, 2019 at 4:28 PM Laura Conchelos <lauraconchelos at gmail.com>
wrote:

> Howdy,
> I have a Schneider 4048 being used off-grid and it keeps turning off. It
> shows errors 52-56, all of which are EEPROM ERROR. There is no fault
> light and the inverter can be turned on again and runs for a couple of
> hours before it seems to happen again. In the manual it says: "Clear the
> fault and check the latest configuration made or any recent
> configurations. If fault detection reoccurs or occurs frequently, service
> is required." I can't think of anything I configured that would cause
> this. And Schneider has you fill out a web form rather than answer a phone
> call apparently. Does anyone have a good tech support number for Schneider?
>
> Thanks!
> Laura
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190228/21090205/attachment.htm>


More information about the RE-Wrenches mailing list