Jerry:



Thanks for the reply.  If we go three phase I believe we get to pick our
voltage.  I understand the options are 120/208, 120/240 (open delta) or
277/480.  277/480 won’t work for us because of existing equipment operating
at 240 VAC.  We have very few 120 loads so a stinger won’t hurt my
feelings—I would pick the 120/240.



I can do an AB/AC/BC installation with many residential inverters, but at
the less than 10K this become problematic:  We actually need to split the
10K system size into a 4K and a 6K to offset annual kWh on two meters.  By
the time you divide these smaller systems into 3 inverters, you don’t have
enough panels to meet the MPPT lower threshold.  This is where Enphase
actually makes some sense.  Furthermore,  too many string inverters makes
the job expensive.  It looks like there are real three phase inverter
options and I will keep looking.



I won’t touch a Fronius.  The new equipment may be improved, but I am still
burnt by a 500% failure rate of IG inverters and some serious character
assassination by Fronius management in dealing with clients.



I misquoted the $20K cost to upgrade.  This number came from an earlier
hypothetical scenario.  I need to get real numbers for this project to
perform an accurate budget analysis.



Thanks for the great input, both online and offline.  I feel like we are
family.  While the complexities of these projects can be a headache, they
make the job interesting.



William



*From:* Jerry Shafer [mailto:jerrysgarage01 at gmail.com]
*Sent:* Wednesday, January 16, 2019 1:12 PM
*To:* William Miller; RE-wrenches
*Subject:* Re: [RE-wrenches] Cost of service upgrade vs Solar credits



William, Wrenches,

can we assume the utility voltage is 120/208 of so Fronius has some
inverters that do that, if it is 277/480 then SMA can do that but neither
of them are less then 10k, Enphase does not have a 3 leg inverter just
1/2,2/3/,3/1 leg balance but you can do that with most any single phase
inverter.

We have had several customers that got hit with Xformer upgrade charges at
time of PTO which is a real problem. I agree that is you go solar that the
bill would be close to zero now that would trigger the 20 k bill to your
customer, better off paying it now and getting FTC while you can.

Jerry



On Wed, Jan 16, 2019 at 12:30 PM William Miller <william at millersolar.com>
wrote:

Friends:



I am engaged in a rather complicated decision process regarding an AG
customer in PG&E territory.  The customer spends a lot of money pumping
water and wishes to offset that cost with installation of a grid-tied
system.  His two services are decrepit and have to be upgraded.  There was
some question if he will be required to upgrade from single phase to three
phase given the size of his motor loads.  We received a waiver to allow us
to continue with single phase although I am not sure that is the right
decision.



We were also informed that the $20,000 cost to upgrade the single phase
feeder to allow bigger services would be waived because of the potential
revenue PG&E would earn over time.  There is a review three years out and
if the revenue meets projections based on existing loads, the construction
credit would remain.  If, however, after three years revenue decreased, the
credit would be rescinded, requiring the customer to fork over the 20 grand.



I was told that if we install solar and zero out the annual bill, that
reduction in billing would trigger the rescinding of the credit.  I want to
check that the utility is interpreting this correctly.  Do any of you
esteemed wrenches have any experience in this area?



Another question:  If we go three phase and I wish to use inverters with
two hot leads, I know they will work on three phase, but the back-feed will
be imbalanced.  I know we are allowed some amount of imbalance, but I am
not sure how much.  Anyone know this answer?



I am searching for true three phase inverters in the less than 10kW range.
This would require a connection to all three phases.  I believe Enphase can
do this.  Are there any other units you know of?



Thanks,



William



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190116/7bded3da/attachment.htm>


More information about the RE-Wrenches mailing list