[RE-wrenches] Cost of service upgrade vs Solar credits
frenergy
frenergy at psln.com
Wed Jan 16 20:24:54 EST 2019
William,
I recently did a GT with PG&E where they allowed me to
backfeed 18KW into their 208 /single/ phase (L-L-N). So even though just
2 hots and a neutral were pulled unto this service panel, no doubt the
PG&E source (transformer across the street) had 3 phase available....yet
I was backfeeding just two of those 3 legs when my backfeed got back
over to their transformer. This is a PTO'ed, operating system. Years
ago I was told they only wanted to see 6KW max out of balance,
apparently it depends.
Jerry made a pretty good point about about biting the $20K
bullet now and get help from the ITC.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
On 1/16/2019 1:11 PM, Jerry Shafer wrote:
> William, Wrenches,
> can we assume the utility voltage is 120/208 of so Fronius has some
> inverters that do that, if it is 277/480 then SMA can do that but
> neither of them are less then 10k, Enphase does not have a 3 leg
> inverter just 1/2,2/3/,3/1 leg balance but you can do that with most
> any single phase inverter.
> We have had several customers that got hit with Xformer upgrade
> charges at time of PTO which is a real problem. I agree that is you go
> solar that the bill would be close to zero now that would trigger the
> 20 k bill to your customer, better off paying it now and getting FTC
> while you can.
> Jerry
>
> On Wed, Jan 16, 2019 at 12:30 PM William Miller
> <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>
> Friends:
>
> I am engaged in a rather complicated decision process regarding an
> AG customer in PG&E territory. The customer spends a lot of money
> pumping water and wishes to offset that cost with installation of
> a grid-tied system. His two services are decrepit and have to be
> upgraded. There was some question if he will be required to
> upgrade from single phase to three phase given the size of his
> motor loads. We received a waiver to allow us to continue with
> single phase although I am not sure that is the right decision.
>
> We were also informed that the $20,000 cost to upgrade the single
> phase feeder to allow bigger services would be waived because of
> the potential revenue PG&E would earn over time. There is a
> review three years out and if the revenue meets projections based
> on existing loads, the construction credit would remain. If,
> however, after three years revenue decreased, the credit would be
> rescinded, requiring the customer to fork over the 20 grand.
>
> I was told that if we install solar and zero out the annual bill,
> that reduction in billing would trigger the rescinding of the
> credit. I want to check that the utility is interpreting this
> correctly. Do any of you esteemed wrenches have any experience in
> this area?
>
> Another question: If we go three phase and I wish to use
> inverters with two hot leads, I know they will work on three
> phase, but the back-feed will be imbalanced. I know we are
> allowed some amount of imbalance, but I am not sure how much.
> Anyone know this answer?
>
> I am searching for true three phase inverters in the less than
> 10kW range. This would require a connection to all three phases.
> I believe Enphase can do this. Are there any other units you know of?
>
> Thanks,
>
> William
>
>
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus