Hello Larry is always a good source. I have used Morningstar MPPT 60 s on
my few LiFe po4 systems 4 years now, no controller problems or equipment
problems yet.  I imagine when the BMS disconnects battery voltage high,
controller output goes high for a short period i will put an Egauge on the
output to messure voltage on one system to see if i catch an event.   Very
good point

On Tue, Jan 8, 2019, 11:03 AM Starlight Solar Power Systems <
larry at starlightsolar.com wrote:

> There was some off board chatter about this subject but I think it is
> useful to some to copy my comments on the board.
>
> If a Li battery EMS or BMS detects a fault condition, it can cause an open
> circuit to the battery. As the battery owner gets familiar with their new
> energy storage system, this will likely happen. If high current is flowing,
> connected devices need to be able to handle that condition without harm.
>
> Morningstar notified us (about 4 year ago) that this event could cause
> damage to their controller. That’s puzzling to me because OCV also happens
> if your battery circuit protection opens.
>
> We mostly sell Midnite and Blue Sky Energy controllers with some Outback
> in the mix. No failures have been reported to us.
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
>
>
> On Jan 7, 2019, at 7:46 AM, Dan at FoxFire-Energy.com
> <Dan at foxfire-energy.com> wrote:
>
> I've been asked to trouble shoot a problem with a new set of LiFePO4
> batteries on an older OB system.. The customer complained the system would
> go dark within a few min. of the batt indicator light going yellow.. From
> what I've gathered so far the BMS of the batteries is shutting down.. The
> distributor sent out one of their techs, but it looks like they missed a
> few adjustments.. The biggie is their CC (OB FM60) went into snooze mode
> within a day of being connected to these guys, and now OB tells me the CC
> lost it's FETs and that's pretty common with NiFePO4 BMS.. also when the
> tech came out to commission the bank, one of the terminals on a battery
> melted and another distorted.. the customer has a few more days to accept
> the bank, I'm thinking send them back.. Comments?
>
>
> Dan Brown
> Foxfire Energy Corp.
> Renewable Energy Systems
> (802)-483-2564
> www.Foxfire-Energy.com <http://www.foxfire-energy.com/>
> ______________________________________________
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190108/c1dace2d/attachment.htm>


More information about the RE-Wrenches mailing list