Your case is interesting because everything was operating and in place but
the range is tighter and only has 3 modules connected per string.
In Hawaii we recorded close to 3000 watts m2, during a commissioning of a
100 k Satcon inverter had 3 equal conbiners, with only one combiner on we
clipped the inverter at just over 100 KWAC on the display. Iradiance meter
went out of range. In northern California had over 2000 watts m2 and poped
the inverters with over volts. Edge of cloud, cold temps, higher elevations
can really be an issue for so called safe zone.
Jerry
On Nov 21, 2018 10:11 PM, <bruce at willpowerelect.com> wrote:
Compadres,
I have 4 identical arrays of 3 strings of 3 Solarworld SW 245 mono (2010
model) to FM80s. When designing, not exceeding 150 voc was critical. No
record temp data available. Location ~ 4,000' Pacific Northwest. Recently
replaced an FM80 with 6 blown FETs showing max power at 3075 watts! This
from a 2205 watt array into a 24 volt battery. Max historical voc is ~120.
My guess at record low temp is -10F. tc%/ÂșC MPP doesn't get anywhere close.
What would the WM2 need to be in order to achieve 3075 watts on a 2205 watt
array? BTW, 2 of the four original chargers are still working fine and one
of them also shows 3075 watts max power. Edge of cloud effect against snow
field at bottom of array?
Cheers,
Bruce Fiero-RMI
*"**Energizing the Rogue Valley"*
4115 S Pacific Hwy
*Medford, OR 97501*
*P:* 541.535.3965
*F:* 541.512.0061
*E:* bruce at willpowerelect.com
*W:* Willpower Electric, LLC <http://www.willpower-electric.com>
*CCB **191852*
*Oregon Electrical Contractor **C681*
*NABCEP Certified Solar (PV) Installer 031409-38*
*DUNS* *191470363*
*Energy Trust of Oregon Trade Ally **Solar (PV) Installation & Energy
Efficient Commercial Lighting Programs *
***This email may contain information that is privileged, confidential, or
otherwise exempt from disclosure under applicable law. If you are not the
addressee, or if it appears that you have received this email in error,
please advise me immediately by reply email, keep the contents
confidential, and immediately delete the message and any attachments from
your system. *
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181122/36546c76/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: sigimg0
Type: image/jpeg
Size: 4536 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181122/36546c76/attachment.jpe>
More information about the RE-Wrenches
mailing list