[RE-wrenches] Low voltage DC v. higher voltage DC

Harry Mahon Michael.Mahon at sma-america.com
Fri Sep 21 12:07:13 EDT 2018


Drake – you are completely correct on the lost sales and two x SI not being price competitive until the size gets pretty large.  It is simply a corporate decision on how much work would need to be done to completely redesign a very good product and make sure it meets the same performance and reliability standards as the original.  Is that cost likely to be re-couped in a reasonable amount of time, based on an estimate of increased sales.  And again, that is just the -US model, the MOW model is two generations ahead already, with no need for unbalanced output in a single unit.

Best –
Mike

SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/facebook.jpg]<http://www.facebook.com/pages/SMA-America/140290312717395> [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/twitter.jpg] <http://twitter.com/SMA_America>  [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wordpress.jpg] <http://www.smainverted.com/>  [Linkedin Logo] <http://www.linkedin.com/company/364675>  [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/youtube.jpg] <http://www.youtube.com/playlist?list=PL840A5336CAC32332>  [SMAAFORUM_ICON] <http://smaadvance.com/signup/>
[cid:image008.jpg at 01D43B9E.70803930]


This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Drake
Sent: Friday, September 21, 2018 6:53 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC

That being said, SMA is loosing a lot of sales by not having a split phase Sunny Island on the market. It would be my unit of choice for many application that I have gone with other brands. The price of a pair of SIs is often just not competitive.

 At 12:25 AM 9/21/2018, you wrote:

Content-Language: en-US
Content-Type: multipart/related;
         boundary="_010_DB7PR04MB4506FEAEB9C7C3E0387F51EFBB120DB7PR04MB4506eurp_";
         type="multipart/alternative"

Tump - You are right about the large number of times that has been asked, and I wish I had a happy answer.

However, with all the work on Sunny Boy Storage and Sunny Central Storage (and even a Tripower storage), resources to develop and test a split phase Sunny Island are not available.  There is active work on updating the communications to support SMA’s Ethernet based communications.  Still, this may be months out.

With the Smartformer being discontinued, the MidNite MNX-240 is the recommended part to create 240 split phase from one Sunny Island.

Best regards –
Mike


SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/fa]<http://www.facebook.com/pages/SMA-America/140290312717395>  [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/tw] <http://twitter.com/SMA_America> [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wo] <http://www.smainverted.com/> [Linkedin Logo] <http://www.linkedin.com/company/364675> [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/yo] <http://www.youtube.com/playlist?list=PL840A5336CAC32332> [SMAAFORUM_ICON] <http://smaadvance.com/signup/>
[cid:image008.jpg at 01D43B9E.70803930]


This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org>> On Behalf Of Tump
Sent: Thursday, September 20, 2018 4:01 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC

I bet Mike could retire from the industry if he had a nickel for every time he was asked for/about that. I’ve asked Santa for years…… €¦ still waiting. T
On Sep 20, 2018, at 5:21 PM, Chris Schaefer <chris at solarandwindfx.com<mailto:chris at solarandwindfx.com> > wrote:

Hey Michael from SMA, any chance we can finally get an 240vac SI here in the states?

Christopher

On Tue, Sep 18, 2018 at 12:11 PM, Harry Mahon < Michael.Mahon at sma-america.com<mailto:Michael.Mahon at sma-america.com>> wrote:
Marco – <

I will need to ask for information about the BYD availability.  Once those units have all required listings/certifications and are available in US, they should be ready to use with SBS.  The CANBUS comms to the BMS has already been vetted, and they are on the SMA Approved battery list already.  But I will get confirmation on the immediate usability.

Best regards –
<Mike




SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


<image001.jpg><http://www.facebook.com/pages/SMA-America/140290312717395> <image002.jpg><http://twitter.com/SMA_America> <image003.jpg><http://www.smainverted.com/> <image004.jpg><http://www.linkedin.com/company/364675> <image005.jpg><http://www.youtube.com/playlist?list=PL840A5336CAC32332> <image006.png><http://smaadvance.com/signup/>
<image007.jpg>


This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

From: RE-wrenches < re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org>> On Behalf Of Marco Mangelsdorf
Sent: Monday, September 17, 2018 10:20 PM
To: RE-wrenches < re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC


Mahalo Mike.

Can you tell us please when the SS will actually be able to integrate the BYD battery platform in the north American market?

marco
On Monday, September 17, 2018, Harry Mahon < Michael.Mahon at sma-america.com<mailto:Michael.Mahon at sma-america.com>> wrote:
Marco and all – yes that is the correct spec ssheet for the BYD batteries that will work with Sunny Boy Storage.

SMA strongly would recommend the Sunny Island for off-grid in general and certainly whole home backup.  See the attached from Home Power April/May 2011; quad stack of SIs acting as UPS for the home – just charging batteries when grid is prresent, powering home with batteries/PV when grid is gone.  A dual split phase cluster is almost 24,000 W continuous (!) capability and can handle crazy power factor loads with no issues.  Built in generator functions and two relay positions per Sunny Island allow for lots of redundancy and fail-safe load shedding to be built in.

The Sunny Boy Storage (SBS) is designed to be a grid-tied inverter to allow higher self consumption of local PV power.  Even with the ABU to allow off grid operation (grid forming on its AC outputs rather than just on the dedicated 120VAC Secure Power Supply outlet), there can be a several second delay in the switch from grid power to microgrid as the ABU must signal the Sunny Boy Storage that it has disconnected from the grid and that it is safe for the SBS to form a grid on its output terminals.  Also be aware that there is no master-slave configuration ability with the SBS – they will always assume they are acting independently on their energy meter input information.

Best regards –
Mike

SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


<image001.jpg><http://www.facebook.com/pages/SMA-America/140290312717395> <image002.jpg><http://twitter.com/SMA_America> <image003.jpg><http://www.smainverted.com/> <image004.jpg><http://www.linkedin.com/company/364675> <image005.jpg><http://www.youtube.com/playlist?list=PL840A5336CAC32332> <image006.png><http://smaadvance.com/signup/>
<image007.jpg>


This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

From: RE-wrenches < re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org>> On Behalf Of Marco Mangelsdorf
Sent: Saturday, September 15, 2018 10:08 PM
To: 'RE-wrenches' < re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC

Sabaidee from Vientiane, Lao PDR.

Attached is the spec sheet on the BYD battery in question.

I’ve confirmed with SMA directly that there’s no capability for the Sunny Storage design (S.S., ABU and battery) to use a generator input.  My apologies for mis-stating earlier that it could accommodate a generator.

As far as grid-tie with batteries, the Holy Grail as far as I’m concerned is being able to provide whole house back-up and not have to do the old fashioned and pain in the arse critical load sub-panel.  The more choices that we’re provided, the more better.  So I’m pleased that companies like SMA, Ensync, SolarEdge and others are bringing new equipment and designs to market to allow for whole house back-up.

marco

From: RE-wrenches [ mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay
Sent: Saturday, September 15, 2018 5:00 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC

HI Harry,

The battery is charged from the AC side correct?
And is the charging algorithm inside the ABU.

If so why couldn’t you use a generator to charge the battery?

jay

peltz power



On Sep 13, 2018, at 7:10 AM, Harry Mahon < Michael.Mahon at sma-america.com<mailto:Michael.Mahon at sma-america.com>> wrote:

Marco –

The Sunny Boy Storage “Advanced Backup Unit” accessory or ABU will be discussed at SPI in a couple weeks – first units are being stockeed now at our warehouses in US.  The ABU will allow the SBS to be a grid former in case of utility outage, however there are no plans to have any generator inputs/controls to allow for battery charging from generat
And yes, BYD BBox HV 5.12/7.68/10.24 devices will be supported when available in US (will be this year I understand)

Mike

-----


The SMA Sunny Storage looks

promising.





It will be able to work with the LGC RESU10 HV battery and,

sooner rather


than later I hope, BYD package as

well.





And it will allow for a backup generator tie

in.





Ta-dah!





marco





On Thursday, September 13, 2018, Bruce Erickson

<<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>

bruce at<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>

mendocinosolar.com<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>>


wrote:





> Hi

Marco,


>


> I partially agree with you. I recently bid Outback,

StorEdge, and

Pika


> options for a GTBB customer, partly to understand pricing

for myself, and


> found OB to be so much more expensive. The customer really

wanted a system


> that would be to be able to charge the batteries off a

generator in an


> outage, understandably. But the extra thousands in cost for

OB ended up


> being prohibitive. Add-on rapid shutdown is a killer. So

he’s opting for

a


> nice modern high voltage DC system, with optimizers and

built-in RSD, but


> when there’s an extended outage, he’ll have to hope the

sun comes out

right


> after the storm to recharge the batteries, or he’ll end

up in the dark


> again, until the grid comes back. Maybe there’s a high

voltage inverter


> that allows generator charging, or a third-party battery

charger, that

I’m


> not aware of. Otherwise high voltage systems are very

limited for

backup,


> at least in winter storm

scenarios.


>


> *Bruce

Erickson*


> Mendocino Solar

Service


> PO Box

1252


> Mendocino, CA

95460


>

707-937-1701


> 707-937-1741

fax


>

<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>

bruce at<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>

mendocinosolar.com<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>


>


> *Connecting Mendocino County to Solar Since*

*1994*


>


>

_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>


_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>


--
Chris Schaefer’s
[[]]<http://www.solarandwindfx.com/>
Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com<http://www.solarandwindfx.com/> ~ E-mail: chris at solarandwindfx.com<mailto:chris at solarandwindfx.com>
[[]]
Thomas Jefferson, the author of our great Constitution, once said, "democracy" will cease to exist when you take away from those who are willing to work and give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

Tump at swnl.net<blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>                www.SWNL.net<blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
                Solarwinds Northernlights
       Serving Mid Coast Maine & Northern California
                         207-832-7574   Cl. 610-517-8401
                              Blair "TUMP" May
               ********  MAINE'S CHARTER ********
                      NABCEP    "Certified PV Installer"

              ********  MAINE'S CHARTER ********
                  Trace Xantrex "Certified" Dealer / Installer"





_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180921/f6d2efcf/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 428 bytes
Desc: image001.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180921/f6d2efcf/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 428 bytes
Desc: image002.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180921/f6d2efcf/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 717 bytes
Desc: image003.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180921/f6d2efcf/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 731 bytes
Desc: image004.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180921/f6d2efcf/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 480 bytes
Desc: image005.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180921/f6d2efcf/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 808 bytes
Desc: image006.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180921/f6d2efcf/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 18895 bytes
Desc: image007.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180921/f6d2efcf/attachment-0005.jpg>


More information about the RE-Wrenches mailing list