[RE-wrenches] Step-up/Step-down Transformer question
Darryl Thayer
darylsolar1 at gmail.com
Tue Sep 18 12:37:38 EDT 2018
DRakes suggestion has the advantage of the DC side is not a voltage
sensitive as the AC side and voltage drop is not as critical. allowing
perhaps a 3%
On Mon, Sep 17, 2018 at 12:50 PM <drake.chamberlin at redwoodalliance.org>
wrote:
> Another option would be to locate the inverters near the grid and run the
> DC at as high a voltage as possible. Have a separate run of wire for each
> of the 5 inverters. If you ran the DC at 500 V, an 11.4 kW inverter would
> only draw 22.8. A. Use 2/0 AL for a little over 1% VD at full power.
>
>
>
> ----- Original Message -----
> From:
> "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>
> To:
> "RE-wrenches" <RE-wrenches at lists.re-wrenches.org>
> Cc:
>
> Sent:
> Mon, 17 Sep 2018 09:42:01 -0700
> Subject:
> [RE-wrenches] Step-up/Step-down Transformer question
>
>
> Wrenches,
>
> We have a PV array situated about 900' from the POI (240V 1PH). We
> initially spec'd (5) 11.4kW inverters and the combined output would be
> 238A. The wire size required for this current over that distance is cost
> prohibitive.
>
> A solution was to use a single 50kW 3 phase inverter at the array and then
> convert it to 240V... somehow? Is anyone familiar with how to go about
> doing this? My thought was to have a step down transformer at the POI and
> pull off two legs to get 240V. Is this even a thing?
>
> The other, more expensive option is to use a step up transformer at the
> array and a step down at the POI to get us a smaller wire size.
>
> Thanks for any input.
>
>
> --
> Loren Ortiz Commercial PV Designer
>
> loren at cal-solar.com <lorenzo at cal-solar.com>* (530) 274-3671*
>
>
>
> <http://californiasolarco.com/referral-program/>
> *Showroom located at: 149 E Main St. Grass Valley, CA 95945*
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180918/0f0fae93/attachment.htm>
More information about the RE-Wrenches
mailing list