[RE-wrenches] Trojan L16RE-2V set-points
William Miller
william at millersolar.com
Wed Sep 12 14:31:01 EDT 2018
Friends:
I used to buy Trojans. My vendor told me about 3 years ago that Trojan had been acquired and the chemistry in the plates had changed. Later they denied making that statement.
I had a set of L16s vastly underperform. Trojan suggest a bulk/absorption voltage higher than any other manufacturer, a value hard to achieve and maintain in a small off grid system. I replaced them with US Battery and system performance improved.
Due to the decline in quality I stopped using Trojan. Due to the varying stories, I stopped using Battery Systems. We prefer the MK/Deka brand.
William
> On Sep 12, 2018, at 11:33 AM, Ray <ray at solarray.com> wrote:
>
> Unfortunately I'm seeing premature failures of the 2 v models even more. You have paralleled cells in each battery, and it can be difficult to even identify the failures. I found the infared camera to be invaluable, as you can see the shorted cell clearly in a thermal image.
> Ray Walters
> Remote Solar
> 303 505-8760
>> On 9/12/18 9:53 AM, Drake wrote:
>> I agree with the comments that followed on this thread, and would also like to add that Trojan L-16 batteries have a high rate of premature failure. Possibly the 2 V cells are better, but the 6 V cells seem very prone to dying early. Trojan batteries were robust in past decades, but seem exceedingly fragile now.
>>
>> At 08:44 PM 9/11/2018, you wrote:
>>> Hello wrenches,
>>>
>>> I inspected a system that another company had installed. It had single string of 12 x Trojan L16RE-2V batteries about 2 years old. They had experienced a battery melt-down. It looks as though the meltdown had occurred internally, not from a bad connection.
>>>
>>> The system was dual stack Outback VFXR-3524A inverters (to be precise one was a sealed unit). The set-points were as follows:
>>> Absorb Voltage was 29.8V
>>> Absorb Time was 6.0 hours
>>> Float Voltage was 27.0V
>>> Rebulk Voltage was 27.0V
>>> End Amps was 0A
>>>
>>> These settings extended similarly to 2 x FM80 charge controllers.
>>>
>>> I was able to jumper the melted battery and get her power in 15 minutes. Her installer had left her without power for 2 weeks. My clients will kill me if that happened!
>>>
>>> Anyway, I believe these set-points are way out of whack and too aggressive. The voltage is OK (Trojan recommends ~29.6V for this) but the Absorb time seems way too long, Rebulk is too high and end amps isn't helping. However, Im not finding a definitive article from Trojan that describes typical Absorb times or even how to adjust towards a good Absorb Time, based on specific gravity measurements or amperage absorption. Â
>>>
>>> My diagnosis is that these batteries have been cooked over the past 2 years. In the electrolyte, there is noticeable "floaties". The client said that the original installer had accused her of not using distilled water, but I don't believe that would cause her symptoms. I believe the floaties are plate material.
>>>
>>> I'd be interested in wrenches opinions familiar with these batteries if these are appropriate settings for a low energy user. I will attempt to get through to Trojan as well.
>>>
>>> Thanks in advance
>>>
>>>
>>>
>>> --
>>>
>>>
>>>
>>> Mac Lewis
>>>
>>> "Yo solo sé que no sé nada." -Sócrates
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180912/a2fc53af/attachment.htm>
More information about the RE-Wrenches
mailing list