[RE-wrenches] Rapid Shutdown Again?

cwarfel cwarfel at entech-engineering.com
Thu Aug 30 09:01:43 EDT 2018


In submitting my comments, I only could access 2017, and that's where I 
made my comments.  Does anyone have more information, or is it too late?


On 8/29/2018 10:05 PM, Ray wrote:
>
> The link to review the first draft of the 2020 code is not working.  
> Do you have just the changes for 690?  I'd really like to submit some 
> comments.
>
> Thanks,
>
> Ray Walters
> Remote Solar
> 303 505-8760
> On 8/28/18 7:59 AM, Rebekah Hren wrote:
>> Hi all,
>> What you need to do now - to get your voices heard about rapid 
>> shutdown requirements-  is to make public comments on the first draft 
>> of the 2020 NEC. *_Comments are due AUGUST 30 at midnight!!! _*
>>
>> Here is the link to a press release 
>> <https://www.necanet.org/about-us/news/news-release-archive/news/2018/07/02/nfpa-releases-2020-nec-first-draft-for-public-review> with 
>> links to read the draft and input your comments:
>> https://www.necanet.org/about-us/news/news-release-archive/news/2018/07/02/nfpa-releases-2020-nec-first-draft-for-public-review
>>
>> The process for changing the NEC is standardized by the NFPA and 
>> while it may not be perfect, it's what we've got!
>>
>> Best,
>> Rebekah Hren
>>
>> On Tue, Aug 28, 2018 at 6:50 AM cwarfel 
>> <cwarfel at entech-engineering.com 
>> <mailto:cwarfel at entech-engineering.com>> wrote:
>>
>>     I like your solutions to this. Just sticking to rapid shutdown
>>     and not the fire code, I think a lot of the problems with 690.12
>>     could be reduced if the maximum string voltage was 150 or even
>>     250.  It reduces the ampacity on a roof for a given power and I
>>     feel that is more of a danger than array voltage that the
>>     Firefighters are highly likely to avoid.
>>
>>     I still cannot get Outback Power to provide a corrected
>>     installation manual or a start up procedure on the RSI/ICS
>>     equipment. Two plus months and all I get are repeated vague or
>>     incorrect information. One expert at OB said that they really
>>     didn't deal much with Rapid Shutdown............
>>
>>     I cannot install any more Outback on roofs at this time.
>>
>>     I'll see if it is ok to provide a link to an online petition to
>>     change 690.12.
>>
>>
>>     Chris
>>
>>
>>
>>     On 8/27/2018 2:13 PM, Ray wrote:
>>>
>>>     HI Chris;
>>>
>>>     As with all things bureaucratic,  good intentions can go awry
>>>     when actually implemented.  Years ago, I was one of the wrenches
>>>     pushing for some form of disconnect closer to the power source,
>>>     or the PV array.  I had no idea it would come back to bite us
>>>     small off grid folks so hard, though.  I'm not quite for
>>>     scrapping all of 690.12, but I do think it needs some serious
>>>     work. /In or on the building/ needs to be defined more clearly
>>>     as 'on the roof'. Ground mounts need a clearer exemption. The PV
>>>     disconnect needs to be clearly defined and also clearly stated
>>>     that the Rapid disconnect system stops there.  The time limit
>>>     needs to be bumped up to 90 seconds: no one is going to throw
>>>     the switch and be hacking on the roof that fast.  The array
>>>     voltage should be 150 vdc, so that lower voltage off grid
>>>     systems could be exempt, and I really think 690.12 should only
>>>     apply to larger arrays (over 10kW) that have long exposed runs
>>>     of conduit (over 10 yards) or that cover more than a certain
>>>     percentage of the total roof area.  If an array covers one face
>>>     of the garage it should be exempt, and if it covers half the
>>>     total roof, then it should have Rapid disconnect, for instance. 
>>>     We need to be sensible, do the fire fighters have a good spot to
>>>     cut and vent the roof without electrical hazards or not?
>>>
>>>     Its interesting how article 690 has morphed from being almost
>>>     entirely oriented towards off grid in 99 and 02, to now off grid
>>>     is barely even considered.  Just look at the lack of thought
>>>     when they wrote the definitions for /DC to DC Converters/.  The
>>>     solar industry has been ready and willing to be thrown under the
>>>     bus at every turn.  I think its about time we started advocating
>>>     for our own self interests like all the other parties involved. 
>>>     This also means that us off grid folks need to be properly
>>>     represented, and off grid considered with all code changes.  I
>>>     think DC coupled PV should have its own section and be separated
>>>     from AC coupled PV.  The systems are so different that it
>>>     doesn't make sense to throw them into the same section.  The
>>>     emergence of article 706 is a step in the right direction.
>>>
>>>     Ray Walters
>>>     Remote Solar
>>>     303 505-8760
>>>     On 8/23/18 5:31 PM, cwarfel at entech-engineering.com
>>>     <mailto:cwarfel at entech-engineering.com> wrote:
>>>>
>>>>     I think Rapid Shutdown should be scrapped professionally and
>>>>     personally.  It was ill conceived and ill written.  Anyone
>>>>     willing to join me in a petition to CMP 44 and the like,
>>>>     contact me off list.
>>>>
>>>>     To your question directly, you have a ground mounted system and
>>>>     you are not subject to 690.12 unless your conductors are "in or
>>>>     on building" which i cannot seem to find what that actually
>>>>     means. Exempted are buildings that are isolated only for the PV
>>>>     system This is a big win for installers as almost everyone
>>>>     installs systems like this.......   Right.    They used to have
>>>>     a dimension to this, but I guess that gave installers too much
>>>>     information. This is a stupid Code addition for roof mounted pv
>>>>     systems, disguised as protecting Firefighters, but not doing so
>>>>     in reality. The NEC looks politically compromised by
>>>>     consultants and manufacturers who too advantage of this fear
>>>>     mongering. No other country with a pv industry has historically
>>>>     done this. Why are installers not up in arms about this?
>>>>
>>>>     This is the NEC reference.
>>>>
>>>>     690.12 Rapid Shutdown of PV Systems on Buildings. PV system
>>>>     circuits installed on or in buildings shall include a rapid
>>>>     shutdown function to reduce shock hazard for emergency
>>>>     responders in accordance with 690.12(A) through (D).
>>>>
>>>>     If your system is ground mounted, you are outside the
>>>>     "altruistic" intent of 690.12 of protecting Firefighters. Put a
>>>>     initiation device disconnect switch at the array.  Any
>>>>     supporters of RS should chime in with the support of 690.12 and
>>>>     add clarity and guidance to those of us who actually install
>>>>     systems and have to deal with this baloney.  690.12 has caused
>>>>     more problems for multimode systems than any tariffs, which are
>>>>     bad enough. I don' think the industry needs any more "safe
>>>>     design and installation" assistance from the CMPs involved with
>>>>     this issue.
>>>>
>>>>     Chris Warfel
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>     On 2018-08-23 00:31, Ray wrote:
>>>>
>>>>>     Greetings fellow wrenches;
>>>>>
>>>>>     I know we have beat this many times but I once again have not
>>>>>     been able to resolve the contradictory information in 690 in
>>>>>     regards to implementing 690.12.  As Rebekah Hren pointed out
>>>>>     before, the diagrams shown in Figure 690.1(b) show that the
>>>>>     /PV System DC Circuit/ stops at the /PV Disconnect/.  Note 2
>>>>>     says specifically the '/PV Disconnect separates the PV system
>>>>>     from all other systems/'. But then in the definitions in 690.2
>>>>>     on the next page, the new definition of a /P//V System DC
>>>>>     Circuit/ says that it includes DC to DC converter output
>>>>>     circuits.  (which are Solar Edge module level controls, but
>>>>>     could be interpreted as a MPPT battery charge Controller?)
>>>>>
>>>>>     Then 690.12 which only applies to '/PV System circuits in or
>>>>>     on buildings/', says we have to control conductors more than 3
>>>>>     ft after penetrating the building.
>>>>>
>>>>>     So in my case, I'm looking at a ground mount, and installing
>>>>>     an external lockable disconnect on the wall before it goes
>>>>>     into the building. This will officially be the PV Disconnect. 
>>>>>     In my interpretation, I should not need to do any Rapid
>>>>>     Shutdown, because I've essentially prevented the /PV system/
>>>>>     from ever entering the building at all ( based on the 5th
>>>>>     diagram and Note 2)  However, I could see an AHJ claiming I
>>>>>     had to do RS all the way to the output side of the charge
>>>>>     controller.
>>>>>
>>>>>     If this were true, could I simply apply RS equipment from the
>>>>>     PV disconnect to the output of the charge controller, or am I
>>>>>     back to module level shutdown for my ground mounted array, or
>>>>>     could I build a tiny building that just housed the PV
>>>>>     Disconnect and take the exemption for '/buildings with the
>>>>>     sole purpose of housing PV system equipment/'?
>>>>>
>>>>>     Essentially the definitions in 690.2 are too broad, and are at
>>>>>     odds with the Figure and Notes of 690.1.  They really didn't
>>>>>     fix this in the 2017 code for us lowly off gridders. Charge
>>>>>     controllers are covered by article 706.23___/Charge Control/_,
>>>>>     and NOT by 690.12 at all. IMHO, the charge controller needs to
>>>>>     be clearly defined and differentiated from DC to DC converters
>>>>>     like Solar Edge's module level DC equipment.
>>>>>
>>>>>     I just want to go back to doing solar designs and
>>>>>     installations, and quit acting like an attorney parsing every
>>>>>     word of this confusing code language.
>>>>>
>>>>>     -- 
>>>>>     Ray Walters
>>>>>     Remote Solar
>>>>>     303 505-8760
>>>>>
>>>>>     _______________________________________________
>>>>>     List sponsored by Redwood Alliance
>>>>>
>>>>>     List Address: RE-wrenches at lists.re-wrenches.org
>>>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>
>>>>>     Change listserver email address & settings:
>>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>>     List-Archive:
>>>>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>
>>>>>     List rules & etiquette:
>>>>>     www.re-wrenches.org/etiquette.htm
>>>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>>>
>>>>>     Check out or update participant bios:
>>>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>>
>>>>
>>>>
>>>>     _______________________________________________
>>>>     List sponsored by Redwood Alliance
>>>>
>>>>     List Address:RE-wrenches at lists.re-wrenches.org
>>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>>     Change listserver email address & settings:
>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>
>>>>     List rules & etiquette:
>>>>     www.re-wrenches.org/etiquette.htm
>>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>>     Check out or update participant bios:
>>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>
>>>
>>>
>>>
>>>     _______________________________________________
>>>     List sponsored by Redwood Alliance
>>>
>>>     List Address:RE-wrenches at lists.re-wrenches.org
>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>     Change listserver email address & settings:
>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>     List rules & etiquette:
>>>     www.re-wrenches.org/etiquette.htm
>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>     Check out or update participant bios:
>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>
>>     -- 
>>
>>              Christopher Warfel, PE
>>            ENTECH Engineering, Inc.
>>     PO Box 871, Block Island, RI 02807
>>                    (401)466-8978
>>
>>     EEI logo <http://entech-engineering.com>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     List Address: RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     List-Archive:
>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out or update participant bios:
>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>>
>>
>> -- 
>> Tel: 336.266.8800
>> NABCEP Certified Solar PV Installation Professional™ 091209-85
>> NC Licensed Electrical Contractor
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-- 

          Christopher Warfel, PE
        ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                (401)466-8978

EEI logo <http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180830/b133573c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180830/b133573c/attachment.jpg>


More information about the RE-Wrenches mailing list