Fri Aug 24 12:52:46 EDT 2018


Jeremy

It's calculated as follows...

5mv is equal to .005.

.005 X Number of Cells

So a 24 Volt system has 12 cells.

.005 X 12 = .060

So the Temp compensation is -/+ 60mv.

As expressed in the Schneider equipment  it's labeled as -60mv...


<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020  m +1.206.790.5840
f +1.902.597.8447  e steve at surrette.com
<javascript:void(0);> <http://www.facebook.com/RollsBattery>
<http://www.facebook.com/RollsBattery> <http://www.twitter.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------


On Fri, Aug 24, 2018 at 9:22 AM Jeremy Rodriguez <allsolarjeremy at msn.com>
wrote:

>
> Hello,
>   Can someone tell me the default BTS value for the Schneider MPPT60-150
> CC?
> It’s currently set for -54mv/C
> I was going to use -5MV/C for the lead acid batteries, but wasn’t sure if
> the -54 equaled -5.4 due to a fractional conversion, so I left it.
>   The controller did seem to go to float stage quickly, BTW.
>
> Jeremy Rodriguez
> Solar Installation / Design Expert
> All Solar, Inc.
> 1463 M St
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180824/c4c685a7/attachment.htm>


More information about the RE-Wrenches mailing list