[RE-wrenches] How to find Ground fault on ungrounded system.
Jerry Shafer
jerrysgarage01 at gmail.com
Sat Aug 18 14:55:53 EDT 2018
Darrel
I have the same issue with the same inverter, my issue is intermittant and
it does appear to be in the array, l have done the test to earth, megger
tester, PVA-600, My issue may not appear for weeks and my thought is
modules leaking when it gets wet enough. I suggest testing with a wet
array, l have had sucess with megger testing and leaking connectors or
splices that way.
Jerry
On Fri, Aug 17, 2018, 10:41 PM Darryl Thayer <darylsolar1 at gmail.com> wrote:
> The system is Fronius Primo, trip on fault code meaning ground fault in
> the array. I disconnect the arrays from the combiner it measures 400+
> corresponding to Voc
> @ temp. My Fluke multimeter the same about 5 volts to ground off both
> ends of the disconnected array. When I connect the inverter and set into
> operation I measure a difference of voltage to ground. The tech support
> at Fronius says it can't be the inverter. Is the problem in the array? Or
> the inverter?
>
> If I meg the array, my procedure is to open circuit the array and connect
> my negative lead to ground and my positive lead of the Megger. to the
> negative lead of the array. please comment on my megging practice.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180818/4375a4ec/attachment.htm>
More information about the RE-Wrenches
mailing list