Also check that the voltage reference is correct for each CT. If the CT on
L1 has a voltage reference of L2,
then it looks as if the CT's are backwards, but really it is the voltage
reference that is backwards. Some
panels are not intuitive as to which Line corresponds to which side of the
bus bar (i.e. the line on the left
of the top of the main breaker actually connects to the bus bar on the
right). Ringing it out is not a good
way to determine if you have the correct line, you need to check for
voltage. If you get 0V, then you are
looking at the same line. If you get 240V, then you have the wrong voltage
reference.
Cheers,
Dave
*Dave Tedeyan*
Senior Engineer | Taitem Engineering, PC
10 Verizon Lane | Lansing, NY 14882
o. *607.930.3481* x6 f. 607.277.2119
www.taitem.com
Solar • Sustainability • Energy • Design
B-Corporation Best for the World 2018 Honoree
On Thu, Aug 16, 2018 at 12:08 AM, frenergy <frenergy at psln.com> wrote:
> Jason,
>
> I'm so glad you brought this up, I'm having a very similar
> issue backfeeding a utility (PG&E) meter that we recently started
> backfeeding on a small commercial job. Somewhat unique in that its
> 208/120 SINGLE phase (L-L-N). The inverters are pushing about 3,000
> KWhrs/month to the grid, way more than typical July consumption at this
> site but their billing shows modest consumption.
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049www.frenergy.net
>
> On 8/15/2018 4:01 PM, Jason Szumlanski wrote:
>
> Is it possible for a utility meter to be programmed/wired backward? I have
> a client on an Enphase system with production and consumption monitoring,
> and the Enphase monitoring is showing solar production exceeded consumption
> by 400 kWh for a billing period. However, the meter is reading almost
> exactly the opposite. It seems too coincidental.
>
> I'm going to go out to the site tomorrow to shut down all of the loads and
> see what happens when solar is only backfeeding the meter, but I'm curious
> how the meters are "programmed" or set up to work.
>
> Note that the meter was zeroed to start and the initial billing period
> readings show DEL exceeded REC by 400 kWh, which matches what was billed
> (net usage of positive 400 kWh).
>
> Jason Szumlanski
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> --
>
>
>
> ------------------------------
> [image: Avast logo] <https://www.avast.com/antivirus>
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com <https://www.avast.com/antivirus>
>
> <#m_511908107291212340_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180816/f76aa213/attachment.htm>
More information about the RE-Wrenches
mailing list