[RE-wrenches] 5 battery strings
Matt Partymiller
matt at solar-energy-solutions.com
Wed Jul 25 14:44:00 EDT 2018
Most systems will operate down 2 volts without a problem. Warrants
reconfiguring but often the homeowner won't even notice for a few days.
In the past month I have had Outback and Sunny Island customers running
down a cell. Sunny Island is reconfigurable to manage the situation
better.
Removing a single cell is losing less stored capacity than removing an
entire string.
Matt
On Wed, July 25, 2018 2:32 pm, tom at wagonmaker.com wrote:
> So you're willing to risk total system shutdown if a single cell fails?
> It just seems like a big risk even if the batteries are considered
> highly reliable. I always planned to minimize the risk of failure causing
> a power outage. A buss bar arrangement with more strings provides
> redundancy and reduced downtime while still being very stable, more stable
> than an interconnected series/parallel arrangement.
>
> Tom
>
>
> On 2018-07-25 00:39, Tump wrote:
>
>> Perhaps suggesting the correct amp Hr battery bank would eliminate the
>> _need_ for buss bar. 2 volt EX1400 1K amp hour batteries work very
>> well good warrantee. all the fusing & interconnects would be eliminated.
>> MORE AHs = less interconnects, always the correct way to
>> go!
>>
>>> On Jul 24, 2018, at 9:40 AM, Dave Tedeyan <dtedeyan at taitem.com>
>>> wrote:
>>>
>>>
>>> Thank you all for the ideas and suggestions. This person in
>>> particular had #4 wire for the battery connections, so they are all
>>> getting replaced with anyway. So it seems like rewiring to a busbar
>>> with fuses will be the way to go. And although not ideal to have so
>>> many strings, this will be more cost effective than just getting a
>>> whole new battery bank right off the bat when they have 10 batteries
>>> that have essentially never been used.
>>>
>>> Cheers,
>>> Dave
>>>
>>>
>>> --
>>>
>>>
>>> Dave Tedeyan
>>>
>>>
>>> SENIOR ENGINEER
>>>
>>>
>>> TAITEM ENGINEERING, PC
>>> 10 Verizon Lane, Lansing, NY 14882
>>> Voice: (607) 930-3481 x6
>>> www.taitem.com [1] On Mon, Jul 23, 2018 at 8:50 PM, Glenn Burt
>>> <glenn.burt at glbcc.com>
>>> wrote:
>>>
>>>
>>> Hi Christopher,
>>>
>>>
>>> I buy my copper buss material from McMaster Carr in appropriate
>>> dimensions for the current I am expecting.
>>>
>>> I then cut it to the lengths I need, drill for appropriate size
>>> fasteners and use 2 layers of heat-shrink tubing to protect the exposed
>>> bar.
>>>
>>> Hope this helps.
>>>
>>>
>>> -Glenn
>>>
>>>
>>> FROM: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> ON
>>> BEHALF OF Chris Schaefer
>>> SENT: Monday, July 23, 2018 2:28 PM
>>> TO: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>>> SUBJECT: Re: [RE-wrenches] 5 battery strings
>>>
>>>
>>> What source are you all using for buss bars for these multiple
>>> battery string set ups?
>>>
>>> Christopher
>>>
>>>
>>> On Mon, Jul 23, 2018 at 2:16 PM, <tom at wagonmaker.com> wrote:
>>>
>>>
>>> Separate out the individual series strings and run each string to a
>>> buss bar setup. Remember it isn't just resistance differences between
>>> batteries but resistance difference between cells as well. In a setup
>>> like the existing one the resistance differences can really add up and
>>> if one battery fails the entire system will be offline. Running each
>>> string to a positive and negative common buss bar means you can remove
>>> individual strings without disrupting the entire storage and the
>>> system can continue operating. Also, it means the only resistance
>>> issues of substance are within individual series pairs not the entire
>>> interconnected bank.
>>>
>>> I ran 10 series pairs of 12v AGM batteries, each pair to a common
>>> buss and it was the longest lasting, most stable battery bank I had.
>>> That was years ago and now it would require fusing each string but
>>> for longevity and stability it is the best bet.
>>>
>>> Tom
>>>
>>>
>>> On 2018-07-23 03:56, Dave Tedeyan wrote:
>>>
>>>
>>> Since we are on the topic of bad battery practices...
>>>
>>>
>>> I may be fixing up a system that was both designed and installed
>>> very poorly. They have a 24V Outback VFXR inverter, and ten 12V AGM
>>> batteries wired into 5 parallel strings. I know that is a bad idea, but
>>> since they already have the equipment, are there any safety issues by
>>> re-using this equipment? It
>>> is for a grid tie battery backup system that will remain in float most
>>> of the time. I assume that the batteries will not last particularly
>>> long, but is there any harm in using them and then just getting new
>>> batteries once they fail?
>>>
>>> Stringing is shown in the attached picture.
>>> Cheers,
>>> Dave
>>>
>>>
>>> --
>>>
>>>
>>> Dave Tedeyan
>>>
>>>
>>> SENIOR ENGINEER
>>>
>>>
>>> TAITEM ENGINEERING, PC
>>> 10 Verizon Lane, Lansing, NY 14882
>>> Voice: (607) 930-3481 x6
>>> www.taitem.com [1] [1]
>>>
>>> Links:
>>> ------
>>> [1] http://www.taitem.com/
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> [2]
>>>
>>>
>>> List-Archive:
>>>
>>>
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.
>> html
>>> [3]
>>>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm [4]
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org [5]
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> [2]
>>>
>>>
>>> List-Archive:
>>>
>>>
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.
>> html
>>> [3]
>>>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm [4]
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org [5]
>>
>> --
>>
>>
>> Chris Schaefer’s
>> [8]
>> Tel/Fax 585-229-2083 or Cell 585-748-1870
>> 5115 South Hill Road ~ Canandaigua New York 14424
>> www.solarandwindfx.com [8] ~ E-mail: _chris at solarandwindfx.com_
>>
>> __
>>
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> [2]
>>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.h
>> tml [3]
>>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm [4]
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org [5]
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.h
>> tml
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>> TUMP at SWNL.NET [6] WWW.SWNL.NET [7]
>>>
>>>
>>> Solarwinds Northernlights _ _
>>> _ SERVING MID COAST MAINE & NORTHERN CALIFORNIA_
>>> _ 207-832-7574 CL. 610-517-8401
>>> _
>>> _ __BLAIR "TUMP" MAY_
>>>
>>>
>>> ******** MAINE'S CHARTER ********
>>> _ __ NABCEP "CERTIFIED PV INSTALLER"_
>>>
>>>
>>> ******** MAINE'S CHARTER ********
>>> _ TRACE XANTREX "CERTIFIED" DEALER / INSTALLER"_
>>>
>>
>>
>>
>> Links:
>> ------
>> [1] http://www.taitem.com/
>> [2]
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> [3]
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.h
>> tml [4] http://www.re-wrenches.org/etiquette.htm
>> [5] http://www.members.re-wrenches.org/
>> [6]
>> blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.n
>> et [7]
>> blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.ne
>> t/ [8] http://www.solarandwindfx.com/
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.h
>> tml
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht
> ml
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
Matthew Partymiller
Solar Energy Solutions LLC
(877) 312-7456
matt at solar-energy-solutions.com
More information about the RE-Wrenches
mailing list