[RE-wrenches] Fwd: Re: Rapid Shutdown and January 1 2019 option?

cwarfel cwarfel at entech-engineering.com
Sun Jul 8 10:02:32 EDT 2018


Thanks Rebekah, At this time, I feel like we are stranded on one option 
that used to be very popular with my customers.  Unlike most of the 
mainland, 95% of our customers want batteries. Right now, we are only 
going to do ground mounted dc coupled until we have a chance to evaluate 
the Outback system. The combiner box is large and that doesn't excite 
some people. Chris


On 7/6/2018 8:23 PM, Rebekah Hren wrote:
> Hi Ray and Dan and Chris, etc,
>
> I agree with a lot of what you are saying, don't get me wrong...I have 
> an off-grid house too and I've been worrying about how module level 
> shutdown will be implemented and what it means for reliability and 
> cost, especially dc-coupled battery-based systems that really don't 
> have or need MLPE.
>
> I'm working on article for the Sept/Oct Homepower about rapid shutdown 
> and one the things I've been excited to learn about is the new Sunspec 
> alliance power line communication protocol 
> <https://www.solarpowerworldonline.com/2017/10/communicating-get-job-done-inverters-sunspecs-rapid-shutdown-standard/> 
> for receivers and transmitters for RS. As Ray mentioned Midnite is 
> already selling their SOB 
> <http://www.midnitesolar.com/productPhoto.php?product_ID=671&productCatName=Software&productCat_ID=44&sortOrder=1&act=p> 
> (er, haha). And Tigo just got their cheapest RS MLPE option the TSF-F 
> UL <https://www.tigoenergy.com/library/view/TS4-F+-+Fire+Safety.pdf/> 
> listed. What's cool is the devices are inverter-agnostic, and don't 
> need another conductor for data or power running to them. But as Ray 
> also said, they aren't working with charge controllers, yet.
>
> So I do think there is some good news on the horizon! From the way the 
> 2020 NEC first draft is written, I don't perceive any chance of the 
> 690.12 rules really changing drastically. But something else that may 
> change the products we can use to meet the requirements is a new UL 
> standard that is being worked on- UL 3741 PV Hazard control. I don't 
> know much about it, but here is a list of the people 
> <https://csds.ul.com/Include/ViewRoster.aspx?GroupID=1782&stpNumber=3741> who 
> are on the Standards Technical Panel. I think a few of them are on 
> this listserv so maybe one of them will give us an update!
>
> Best,
> Rebekah
>
>
>
> On Fri, Jul 6, 2018 at 4:39 PM Ray <ray at solarray.com 
> <mailto:ray at solarray.com>> wrote:
>
>
>
>
>     -------- Forwarded Message --------
>     Subject: 	Re: [RE-wrenches] Rapid Shutdown and January 1 2019 option?
>     Date: 	Fri, 6 Jul 2018 16:37:47 -0600
>     From: 	Ray <ray at solarray.com> <mailto:ray at solarray.com>
>     To: 	Rebekah Hren <rebekah.hren at gmail.com>
>     <mailto:rebekah.hren at gmail.com>
>
>
>
>     Hi Rebekah;
>
>     I very much appreciated your previous posts on this. Yes, we do
>     not need to disconnect the inverter and battery per previous
>     interpretations.  However, the RS system can and will trip for a
>     variety of reasons, which disconnects the charging system.  It
>     might take a couple of days to discharge the batteries, but the
>     results are the same: rotten meat in the fridge and a dead
>     battery. If no one is home, thousands of dollars of battery could
>     be ruined in a matter of weeks, if its Gel or AGM.
>
>     If we get to a point where all the modules have shut down built
>     in, and the Controllers also have built in disconnect so their
>     capacitors don't back feed, then it won't be so hard to comply
>     with 690.12.  In the mean time though, off grid should be given a
>     clear exemption based on array size and Voc of the array.  We are
>     often only wiring 2 modules in series, so we are already well
>     below 100 v.   Rules designed for 600 v arrays should not
>     unilaterally apply to everyone, just as 600 VAC rules don't all
>     apply to 120 vac residential.  There are numerous exemptions for
>     lower voltage AC situations, we are just asking that the same
>     thinking be applied to PV.
>
>     Ray Walters
>     Remote Solar
>     303 505-8760
>
>     On 7/6/18 2:57 PM, Rebekah Hren wrote:
>>     I believe there was a big improvement for off-grid systems as
>>     relates to RS in the 2017 NEC - the diagrams in 690.1(b) all show
>>     the PV system disconnect clearly now.  If you check out the
>>     diagrams you can see that energy storage/battery circuits,
>>     including the battery-based inverter whether AC or DC coupled,
>>     are outside the PV system boundary, thus not PV system circuits,
>>     thus not subject to RS.
>>
>>     Also, the NEC 2020 1st draft report has been published
>>     <https://downloads.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70&tab=nextedition>,
>>     so get your comments submitted!
>>
>>     Rebekah Hren
>>     Member, NEC CMP-4
>>
>>     On Fri, Jul 6, 2018 at 2:22 PM Dan Fink <danbob88 at gmail.com
>>     <mailto:danbob88 at gmail.com>> wrote:
>>
>>         I agree with you, Ray, as a purely off-grid solar installer
>>         and troubleshooter. I think all that was accomplished in NEC
>>         2017 on this issue is that non-habitable structures, like the
>>         common off-grid 'power shed' don't need 690.12 RS anymore.
>>
>>         Dan Fink
>>         Professor of Solar Energy Technology, Ecotech Institute
>>         IREC Certified Instructor™ for:
>>         ~ PV Installation Professional
>>         ~ Small Wind Installer
>>         Executive Director, Buckville Energy
>>         NABCEP Registered Continuing Education Providers™
>>         NABCEP Associate
>>
>>         970.672.4342
>>
>>
>>         On Fri, Jul 6, 2018 at 11:32 AM, Ray <ray at solarray.com
>>         <mailto:ray at solarray.com>> wrote:
>>
>>             Midnite has some string level and module level 690.12
>>             disconnects that wire in like an optimizer or micro
>>             inverter, so those should be able to meet the 2019
>>             requirements.  However beware:  they as of yet still
>>             don't have a reasonable disconnect system to disconnect
>>             the charge controller which has capacitors that back feed
>>             the PV line for up to 90 seconds. They have a DC GFI
>>             breaker with remote trip capability but it takes 4
>>             spaces, so with multiple charge controllers it turns into
>>             a wiring mess really fast.
>>
>>             I actually wired in some 60 amp rated diodes on one
>>             system to get it to pass inspection; what a joke, going
>>             back to 1980s equipment to pass 2017 code. 690.12 is an
>>             absolute nightmare for small off grid.  There really
>>             should be some exemptions for small arrays (under 3 kW)
>>             and under 100 vdc.  Fire fighters are not going to get
>>             there till the structure is down anyway,  Response times
>>             are up to an hour for remote locations with volunteer
>>             fire departments.  Its not like in town at all;  no one
>>             is going to go on the roof on an off grid fire.
>>
>>             On the flip side, there are real dangers created by
>>             nuisance tripping of 690.12 equipment.  Again, on grid
>>             it's a mere inconvenience, but off grid it could mean
>>             spoiled food, frozen water lines, shut down heating
>>             systems in subzero temperatures, and for the elderly:
>>             loss of their breathing machines.  I've already had a 74
>>             year old customer climbing on their roof multiple times
>>             to reset the Rapid shutdown equipment after nuisance
>>             trips.  Are we going to wait until we get someone killed
>>             in the name of "Safety" before we fix this?
>>
>>             Ray Walters
>>             Remote Solar
>>             303 505-8760
>>
>>             On 7/6/18 9:55 AM, cwarfel wrote:
>>>
>>>             I am wondering about the experience installers have with
>>>             a DC coupled multimode system design that will comply
>>>             after January 1 with what I feel is the biggest
>>>             mistake/poorly guided part of NEC 2017 690, and that is
>>>             690.12. We are installing two Outback systems with the
>>>             remote controlled combiner and even that won't comply
>>>             after January 1 unless we parallel more subarrays
>>>             (There's safety for you, lower voltage-higher
>>>             amperage!). Thanks for any insight.
>>>
>>>             Chris
>>>
>>>
>>>
>>>
>>>             -- 
>>>
>>>             Christopher Warfel, PE
>>>                    ENTECH Engineering, Inc.
>>>             PO Box 871, Block Island, RI 02807
>>>             (401)466-8978
>>>
>>>             EEI logo <http://entech-engineering.com>
>>>
>>>
>>>             _______________________________________________
>>>             List sponsored by Redwood Alliance
>>>
>>>             List Address:RE-wrenches at lists.re-wrenches.org
>>>             <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>             Change listserver email address & settings:
>>>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>             List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>             List rules & etiquette:
>>>             www.re-wrenches.org/etiquette.htm
>>>             <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>             Check out or update participant bios:
>>>             www.members.re-wrenches.org
>>>             <http://www.members.re-wrenches.org>
>>>
>>
>>
>>             _______________________________________________
>>             List sponsored by Redwood Alliance
>>
>>             List Address: RE-wrenches at lists.re-wrenches.org
>>             <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>             Change listserver email address & settings:
>>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>             List-Archive:
>>             http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>             List rules & etiquette:
>>             www.re-wrenches.org/etiquette.htm
>>             <http://www.re-wrenches.org/etiquette.htm>
>>
>>             Check out or update participant bios:
>>             www.members.re-wrenches.org
>>             <http://www.members.re-wrenches.org>
>>
>>
>>
>>         _______________________________________________
>>         List sponsored by Redwood Alliance
>>
>>         List Address: RE-wrenches at lists.re-wrenches.org
>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>         Change listserver email address & settings:
>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>         List-Archive:
>>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>         List rules & etiquette:
>>         www.re-wrenches.org/etiquette.htm
>>         <http://www.re-wrenches.org/etiquette.htm>
>>
>>         Check out or update participant bios:
>>         www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>>
>>
>>     -- 
>>     Tel: 336.266.8800
>>     NABCEP Certified Solar PV Installation Professional™ 091209-85
>>     NC Licensed Electrical Contractor
>>
>>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     List Address:RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out or update participant bios:
>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> -- 
> Tel: 336.266.8800
> NABCEP Certified Solar PV Installation Professional™ 091209-85
> NC Licensed Electrical Contractor
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-- 

          Christopher Warfel, PE
        ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                (401)466-8978

EEI logo <http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180708/0705f309/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180708/0705f309/attachment.jpg>


More information about the RE-Wrenches mailing list