Hi Nick, so if I understand you correctly then I can find some older Enphase units (I know where I can get some 250’s) and they will integrate with a couple of new 265w Hanwah Q Cells, no problem. I could just plug them in then add them to the existing array. The existing Envoy and 210 Enphase units will not have any issues etc.?

Thanks!

Ron
earthRight Solar - Solareagle.com

> On Jul 7, 2018, at 10:35 AM, Nick Soleil <nsoleil at enphaseenergy.com> wrote:
> 
> Hi wrenches,
> 
> The older generation micros (M190s, M210s, M215s, M250s, S280s) all communicated at 144kHz, line to neutral and communicated with the old EMUs, the oval Envoys, and the Envoy-S system monitors.
> 
> The new IQ micros (IQ 6, IQ 6+, IQ 7, IQ 7+, and IQ 7X) no longer have a neutral, so we had to go to a new communication protocol which is 110kHz, line to line.  
> 
> You would need a new IQ Envoy for pairing with the new IQ micros in addition to the existing system monitor.  
> 
> If your customer wants to stick with HIT modules similar to the Sanyo's they had originally, then you can pair the Panasonic HIT modules with our IQ 7X micros.  We have a module compatibility tracker online here:
> https://enphase.com/en-us/support/module-compatibility <https://enphase.com/en-us/support/module-compatibility>
> 
> 
> Cordially,
> Nick Soleil
> Enphase Energy
>  Product Manager
> 
> (707) 763-4784 x7267  // office
> (707) 321-2937  // cell
>  <https://enphase.com/>
> Energy
>  Evolved <http://enphase.com/>™
> Powering What’s Next™ | The Enphase Energy Management System <http://ow.ly/HbVS3>
> 
> NABCEP Certified Solar PV Installer #03262011-300
> California C10 Licensed Electrician #986315
> Texas Master Electrician #284451
> 
> 
> 
> 
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf of Jay <jay.peltz at gmail.com>
> Sent: Saturday, July 7, 2018 8:32 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Enphase question
>  
> Hi Jerry,
> 
> Can the new EMU work with the older units?
> 
> Jay
> Peltz power. 
> 
> 
> On Jul 6, 2018, at 11:59 PM, Jerry Shafer <jerrysgarage01 at gmail.com <mailto:jerrysgarage01 at gmail.com>> wrote:
> 
>> Wrenches, Ron
>> Thats a good thing with enphase, mix and don't need to match, you will need inverters that connect in line or just seperate them with a combiner/subpanel. You will need to stay away from the new Q inverter series as its on a different frequency for comms, 190's 210's 215's and as l recall the 250's all on the older EMU, they are getting harder to find but im sure there are some out there.
>> Jerry
>> 
>> On Fri, Jul 6, 2018, 3:06 PM RM You <solareagle at solareagle.com <mailto:solareagle at solareagle.com>> wrote:
>> I have a legacy system with 12 Sanyo HIT 215N panels and Enphase 210’s. Client wants to re-do roof and add two more panels when the system is re-installed. Are there any concerns with mixing Enphase inverters on a single string, e.g. adding a couple of 265w panels and appropriate inverters? We don’t do a lot of grid tie and this hasn’t come up before.
>> 
>> Ron
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180707/17f04a32/attachment.htm>


More information about the RE-Wrenches mailing list