[RE-wrenches] Enphase question
Nick Soleil
nsoleil at enphaseenergy.com
Sat Jul 7 13:35:23 EDT 2018
Hi wrenches,
The older generation micros (M190s, M210s, M215s, M250s, S280s) all communicated at 144kHz, line to neutral and communicated with the old EMUs, the oval Envoys, and the Envoy-S system monitors.
The new IQ micros (IQ 6, IQ 6+, IQ 7, IQ 7+, and IQ 7X) no longer have a neutral, so we had to go to a new communication protocol which is 110kHz, line to line.
You would need a new IQ Envoy for pairing with the new IQ micros in addition to the existing system monitor.
If your customer wants to stick with HIT modules similar to the Sanyo's they had originally, then you can pair the Panasonic HIT modules with our IQ 7X micros. We have a module compatibility tracker online here:
https://enphase.com/en-us/support/module-compatibility
Cordially,
Nick Soleil
Enphase Energy Product Manager
(707) 763-4784 x7267 // office
(707) 321-2937 // cell
[Enphase_esig_logo6.jpg]<https://enphase.com/>
Energy Evolved<http://enphase.com>™
Powering What’s Next™ | The Enphase Energy Management System<http://ow.ly/HbVS3>
NABCEP Certified Solar PV Installer #03262011-300
California C10 Licensed Electrician #986315
Texas Master Electrician #284451
________________________________
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf of Jay <jay.peltz at gmail.com>
Sent: Saturday, July 7, 2018 8:32 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase question
Hi Jerry,
Can the new EMU work with the older units?
Jay
Peltz power.
On Jul 6, 2018, at 11:59 PM, Jerry Shafer <jerrysgarage01 at gmail.com<mailto:jerrysgarage01 at gmail.com>> wrote:
Wrenches, Ron
Thats a good thing with enphase, mix and don't need to match, you will need inverters that connect in line or just seperate them with a combiner/subpanel. You will need to stay away from the new Q inverter series as its on a different frequency for comms, 190's 210's 215's and as l recall the 250's all on the older EMU, they are getting harder to find but im sure there are some out there.
Jerry
On Fri, Jul 6, 2018, 3:06 PM RM You <solareagle at solareagle.com<mailto:solareagle at solareagle.com>> wrote:
I have a legacy system with 12 Sanyo HIT 215N panels and Enphase 210’s. Client wants to re-do roof and add two more panels when the system is re-installed. Are there any concerns with mixing Enphase inverters on a single string, e.g. adding a couple of 265w panels and appropriate inverters? We don’t do a lot of grid tie and this hasn’t come up before.
Ron
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180707/6724e14e/attachment.htm>
More information about the RE-Wrenches
mailing list