I agree with you, Ray, as a purely off-grid solar installer and
troubleshooter. I think all that was accomplished in NEC 2017 on this issue
is that non-habitable structures, like the common off-grid 'power shed'
don't need 690.12 RS anymore.
Dan Fink
Professor of Solar Energy Technology, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Registered Continuing Education Providers™
NABCEP Associate
970.672.4342
On Fri, Jul 6, 2018 at 11:32 AM, Ray <ray at solarray.com> wrote:
> Midnite has some string level and module level 690.12 disconnects that
> wire in like an optimizer or micro inverter, so those should be able to
> meet the 2019 requirements. However beware: they as of yet still don't
> have a reasonable disconnect system to disconnect the charge controller
> which has capacitors that back feed the PV line for up to 90 seconds. They
> have a DC GFI breaker with remote trip capability but it takes 4 spaces, so
> with multiple charge controllers it turns into a wiring mess really fast.
>
> I actually wired in some 60 amp rated diodes on one system to get it to
> pass inspection; what a joke, going back to 1980s equipment to pass 2017
> code. 690.12 is an absolute nightmare for small off grid. There really
> should be some exemptions for small arrays (under 3 kW) and under 100 vdc.
> Fire fighters are not going to get there till the structure is down
> anyway, Response times are up to an hour for remote locations with
> volunteer fire departments. Its not like in town at all; no one is going
> to go on the roof on an off grid fire.
>
> On the flip side, there are real dangers created by nuisance tripping of
> 690.12 equipment. Again, on grid it's a mere inconvenience, but off grid
> it could mean spoiled food, frozen water lines, shut down heating systems
> in subzero temperatures, and for the elderly: loss of their breathing
> machines. I've already had a 74 year old customer climbing on their roof
> multiple times to reset the Rapid shutdown equipment after nuisance trips.
> Are we going to wait until we get someone killed in the name of "Safety"
> before we fix this?
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 7/6/18 9:55 AM, cwarfel wrote:
>
> I am wondering about the experience installers have with a DC coupled
> multimode system design that will comply after January 1 with what I feel
> is the biggest mistake/poorly guided part of NEC 2017 690, and that is
> 690.12. We are installing two Outback systems with the remote controlled
> combiner and even that won't comply after January 1 unless we parallel
> more subarrays (There's safety for you, lower voltage-higher amperage!).
> Thanks for any insight.
>
> Chris
>
>
>
>
> --
>
> Christopher Warfel, PE
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> (401)466-8978
>
> [image: EEI logo] <http://entech-engineering.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180706/efa05028/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180706/efa05028/attachment.jpg>
More information about the RE-Wrenches
mailing list