[RE-wrenches] Low output

Rick Brown rick at solshineenergyalternatives.com
Tue Jun 26 19:48:31 EDT 2018


Bill,

Thanks for updating us on this issue. 

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergyAlternatives.com
Check, Virginia 24072
540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21

> On Jun 26, 2018, at 7:06 PM, Bill Battagin <frenergy at psln.com> wrote:
> 
> OK Campers, this long  and short of the "low output" with this CC...... installer error.  The battery and PV negatives were separate in the wiring section of the Kid, but were tied together at a bus bar in the DC enclosure.  I pulled the PV neg off the common neg bus, spliced it to the separate neg to the PV neg landing in the CC and there it was, full output.
> 
>             I've managed to find egg on my face for other issues on the list, I really appreciate the help.
> 
> Bill
> 
> Feather River Solar Electric
> 
> 
>> On 6/19/2018 9:52 PM, frenergy wrote:
>> Off-gridders,
>> 
>>             Small 24 volt off-grid install.....new installation, 3, 285 watt PVs in series, 4, L-16's in series, Midnight "Kid" CC.  Problem: I cannot get more than about 200 watts (8-9 amps battery side) out of the Kid display in full noon sun, clean PVs. Should be 700 watts plus and about 28 amps.  Bulk/Absorb set at 29V, battery voltage at ~25 V (pulled down with a heat gun).  I changed that Kid out for another new one> Same issue!  I disconnected the PV wires where they land in the Kid and got 9.3 amps short circuit, 105 volts oc  Called Midnight tech support but we couldn't come up with a good solution.  Ideas?
>> 
>> Thx,
>> 
>> Bill
>> 
>> Feather River Solar Electric
>> Bill Battagin, Owner
>> 4291 Nelson St.
>> Taylorsville, CA 95983
>> 530.284.7849
>> CA Lic 874049
>> www.frenergy.net
>> 
>> 
>> ---
>> This email has been checked for viruses by Avast antivirus software.
>> https://www.avast.com/antivirus
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180626/98f59706/attachment.htm>


More information about the RE-Wrenches mailing list